Lightning -- to ground or not to ground, that is the qn

By providing a thick cable from the mast to the sea, we hope that (most) of any lightning will take that path to the sea, even if it vaporizes the cable in the process (ions are conductive). However, we also provide a path for charge to move from the mast, so the top will be positive and attracting negative strikes.


Alternatively insulate the mast. Let it float, so that it does not attract lightning in the first place.


My boat has the worst of both. Mast is lightly earthed, will attract lightning but not be able to dissipate it.


Many thoughts, any evidence? What do people think?
aberglas is offline   Reply With Quote
Old 08-08-2023, 03:02   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,881
Images: 241
Re: Lightning -- to ground or not to ground, that is the qn

Quote:
Originally Posted by aberglas View Post
... Alternatively insulate the mast. Let it float, so that it does not attract lightning in the first place...
How do you plan to isolate your mast, from ground, against a lightning bolt [> ± 30 kA @ ± 120 kV], that’s traveled across an air gap of many miles?

Grounded masts do not [significantly] attract lightning.

A ‘Custom Search’, of the Forum will return dozens of threads, discussing all aspects of the subject, and including many links to primary sources of information.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 08-08-2023, 03:06   #3
Marine Service Provider

Join Date: Aug 2023
Posts: 76
Re: Lightning -- to ground or not to ground, that is the qn

You are not trying to insulate the mast from a strike. But rather to prevent the streamers reaching up from the masthead to the charge above. To prevent the discharge in the first place.
aberglas is offline   Reply With Quote
Old 08-08-2023, 06:01   #4
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,881
Images: 241
Re: Lightning -- to ground or not to ground, that is the qn

AFIC, there is no lightning [protection] expert that does not insist upon solid grounding of the air terminal [mast], including those who market [discredited] Early Streamer Emission/Dissipation (ESE/ESD), Charge Transfer Systems, Dissipation Array Systems; or whatever your particular magic voodoo salesman calls them.

The International Electrotechnical Commission [IEC] prepares and publishes International Standards, for all electrical, electronic, and related technologies, and is the leading international organization, in its field.
IEC 62305, “Protection against lightning”, published by this body, is the international standard for lightning protection, from which most national standards are derived.
This standard states, in the first line of its introduction that:
“There are no devices or methods capable of modifying the natural weather phenomena to the extent that they can prevent lightning discharges”.
IEC 62305-1 ➥ https://webstore.iec.ch/preview/info...ed2.0%7Den.pdf
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 08-08-2023, 06:14   #5
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,881
Images: 241
Re: Lightning -- to ground or not to ground, that is the qn

Obviously, you’re interested in the subject.
May I suggest a little reading:
“Charge Separation”, & “Field Generation” would be good search terms.

Normally, the ground has a slight negative charge; however, when a thunderstorm is directly overhead, the large negative charge, in the cloud, repels negative charges, on the ground [& upon the sea], underneath the storm.
This causes the ground/sea, and any objects [boats or people] on the ground, directly underneath the storm, to become positively charged. With the cloud polarized into opposites, and with a positive charge induced upon Earth's surface, the stage is set for a lightning strike.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 08-08-2023, 06:27   #6
Registered User

Join Date: Jan 2023
Posts: 1,729
Re: Lightning -- to ground or not to ground, that is the qn

There is no question. Grounding is essential to protection of the vessel from potentially catastrophic damage.
SailingHarmonie is online now   Reply With Quote
Old 08-08-2023, 06:45   #7
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,820
Re: Lightning -- to ground or not to ground, that is the qn

Lighting is a complex subject, but you do not need to be concerned that grounding the mast will increase the chance of a hit. The overwhelming consensus is that grounding the mast, if anything, helps to slightly reduce the chance of strikes. In simple terms this is because the static charge that normally accumulates as the mast rocks from side to side is dissipated when the mast is grounded.

The reduction is strike frequency is only very tiny. The real reason for grounding is to reduce the chance of catastrophic damage and here grounding will produce a significant improvement.
noelex 77 is offline   Reply With Quote
Old 08-08-2023, 07:25   #8
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,253
Re: Lightning -- to ground or not to ground, that is the qn

Grab this PDF, before it disappears!

Not just the mast, also every chainplate must be bonded. Very hard to do on a cat, much easier on a monohull.

This lightning bonding system has nothing to do with strike avoidance; it is purely to cope with a strike, reducing damage as much as possible.

If you use an external under water grounding plate, which should be located below the mast, make sure that it is rated to be used for lightning protection.
Attached Files
File Type: pdf TE-4 Lightning Protection.pdf (252.5 KB, 425 views)
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 08-08-2023, 16:08   #9
Marine Service Provider

Join Date: Aug 2023
Posts: 76
Re: Lightning -- to ground or not to ground, that is the qn

TE-4 makes an interesting note about conductors needing to be mainly vertical. I suppose this combination of current and static electricity is in a hurray to get to ground!


I am grounding my mast with a thick cable connected to a chain in the water. Will only put it out when there is lightning about. may do something more permanent later. Like most glass boats, it has nothing at all now.


Apparently something like 1% of yachts get struck each year in lightning prone areas.
aberglas is offline   Reply With Quote
Old 08-08-2023, 22:30   #10
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,253
Re: Lightning -- to ground or not to ground, that is the qn

Quote:
Originally Posted by aberglas View Post
TE-4 makes an interesting note about conductors needing to be mainly vertical. I suppose this combination of current and static electricity is in a hurray to get to ground!

I am grounding my mast with a thick cable connected to a chain in the water. Will only put it out when there is lightning about. may do something more permanent later. Like most glass boats, it has nothing at all now.

Apparently something like 1% of yachts get struck each year in lightning prone areas.
That won’t work. The main lightning charge comes down the mast because that path has much less resistance than the standing rigging. When it arrives at the base of the mast, you have to guide it into the water… -vertically- ! If you attach a chain to a shroud or chainplate then you only bring a small part of the charge to the water and the main charge will create its own oath from the base of the mast down into the water. Boats without bonding at the mast often show splatter patterns of hundreds of tiny holes in the hull as a result.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 08-08-2023, 22:50   #11
Marine Service Provider

Join Date: Aug 2023
Posts: 76
Re: Lightning -- to ground or not to ground, that is the qn

Thanks, but as I said I am grounding the mast, not the shrouds. Drilling a hole and bolting the thick cable to it.


Normally I would use some anti-corrosion paste between stainless and aluminum. But for this I do not want an insulated connection! There is probably a better way.
aberglas is offline   Reply With Quote
Old 09-08-2023, 06:13   #12
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,253
Re: Lightning -- to ground or not to ground, that is the qn

Quote:
Originally Posted by aberglas View Post
Thanks, but as I said I am grounding the mast, not the shrouds. Drilling a hole and bolting the thick cable to it.

Normally I would use some anti-corrosion paste between stainless and aluminum. But for this I do not want an insulated connection! There is probably a better way.
I’m pretty sure you mentioned using a chain that is hanging in the water. With the requirement to only/mostly use vertical conductors, I can see that only work for a catamaran with a bridge deck suspended over the water, but you don’t have a boat type/model specified in your account so hard to tell.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-08-2023, 08:41   #13
Registered User
 
TeddyDiver's Avatar

Join Date: Aug 2010
Location: Arctic Ocean
Boat: Under construction 35' ketch (and +3 smaller)
Posts: 2,786
Images: 2
Re: Lightning -- to ground or not to ground, that is the qn

Quote:
Originally Posted by s/v Jedi View Post
I’m pretty sure you mentioned using a chain that is hanging in the water. With the requirement to only/mostly use vertical conductors, I can see that only work for a catamaran with a bridge deck suspended over the water, but you don’t have a boat type/model specified in your account so hard to tell.
That's about what I'll do. Grounding stays to water with deployable copper cable. Maybe a rod on the mast top.. Wooden masts thou
TeddyDiver is offline   Reply With Quote
Old 09-08-2023, 08:49   #14
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,253
Re: Lightning -- to ground or not to ground, that is the qn

Quote:
Originally Posted by TeddyDiver View Post
That's about what I'll do. Grounding stays to water with deployable copper cable. Maybe a rod on the mast top.. Wooden masts thou
Wooden masts! They don’t count as a good conductor… I have no experience with this and recommend you search for more info on Google etc. Are your stays stainless steel? Stainless steel isn’t a good conductor either but I think the classic steel stays may be good. If it isn’t a good enough conductor then you may need a copper conductor from a masthead rod all the way down, tied off a stay.

You can also make electrodes just above the waterline. There was a discussion on this recently for a catamaran, you should be able to search for that on the forum.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-08-2023, 08:56   #15
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,881
Images: 241
Re: Lightning -- to ground or not to ground, that is the qn

Quote:
Originally Posted by aberglas View Post
... Normally I would use some anti-corrosion paste between stainless and aluminum. But for this I do not want an insulated connection! There is probably a better way.
Anti-Oxide inhibiting compounds* produce low initial contact resistance, seal out air and moisture, prevent oxidation or corrosion, exhibit superior weathering characteristics, are usable over wide temperature ranges, provide a high conductivity “gas-tight” joint, and reduce galling and seizing.

* Burndy “Penetrox™” compounds contain homogeneously suspended metal particles. The suspended metal particles assist in penetrating thin oxide films, act as electrical “bridges” between conductor strands, aid in gripping the conductor, improve electrical conductivity and enhance the integrity of the connection.
* Ideal “Noalox®” contains suspended zinc particles, which penetrate, and cut aluminum oxide, while carrier material excludes air, to minimize further oxidation, and provide additional inner-strand and inner-conductor current paths for improved conductivity and cooler connections.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Reply

Tags
lightning


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
To ground or not to ground an aluminum arch...that is my question. chrtucke Electrical: Batteries, Generators & Solar 9 06-10-2014 23:17
Attaching lightning ground wire to keel bolt, need workaround. OrangeCrush Electrical: Batteries, Generators & Solar 5 02-04-2013 16:05
Mounting Lightning Ground Strip? Beausoleil Electrical: Batteries, Generators & Solar 2 28-09-2012 12:21
DIY Copper Lightning Ground Plate - How Thick ? sv.Crake Construction, Maintenance & Refit 4 13-07-2011 14:46
No Keel Bolts - How to Ground for Lightning ? sabray Construction, Maintenance & Refit 19 25-08-2010 11:12

Advertise Here


All times are GMT -7. The time now is 08:54.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.