Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by smac999 View Post

so if you take the hot feed wire at the AC panel and short it to the green ground wire what happens?...
If your DC negative and AC ground are bonded as per ABYC, you will send AC into your DC system. This is what causes ESD in fresh water.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 09-05-2021, 15:11   #92
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,743
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by boatpoker View Post
If your DC negative and AC ground are bonded as per ABYC, you will send AC into your DC system. This is what causes ESD in fresh water.

Yes like this... 15a leaking through (salt) water was not enough to blow the 30a main. Elci would have though. But I’m curious what would happen on his boat with a floating ground.
Attached Thumbnails
Click image for larger version

Name:	BC181B0A-339F-4D9C-B8BB-D4CD455CD5E2.jpg
Views:	48
Size:	393.9 KB
ID:	238020  
smac999 is offline   Reply With Quote
Old 09-05-2021, 15:17   #93
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by s/v Jedi View Post
...
So the ground wire (green/yellow, earth, bare copper) on the outlets all go to the ground busbar as shown in my diagram. This is where the ground wires from transformers, inverter/chargers, boat-side of galvanic isolator and isolation transformer etc. go. It is not connected to DC negative and not to AC Neutral. It’s only job is to connect all external metal surfaces of appliances together.
So you are connecting your outlet grounds back to ship/shore ground? You are still connected to shore AC neutral! (if you are plugged into the 50 amp, the 30 amp depends on how you have your isolation transformer configured) Shore ground and shore AC neutral are connected (at the source). You have an isolated supply at your outlets but the outlet ground connection is connected to the water, the shore ground, and the shore neutral. The power at the outlets will not recognize these as a ground. A fault from the outlet power to the ground wire would not cause anything to trip. A second fault from the opposite phased outlet power would cause a trip (of an AC panel breaker), but it would do that only by virtue of the fact that your outlet grounds are wired together (no need to connect them to ship/shore ground). I don't understand why you have the third outlet wire (safety ground) connected back to ship/ shore ground. Why is it not connected to the autotransformer nuetral? Also you are losing out on the safety and corrosion advantage of having a completely isolated system.
Thumbs Up is offline   Reply With Quote
Old 09-05-2021, 15:23   #94
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,335
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by Thumbs Up View Post
Also you are losing out on the safety and corrosion advantage of having a completely isolated system.
AC can cause corrosion on a boat, but at such a slow rate it is unlikely you'll notice it for years or more likely, decades.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 09-05-2021, 15:30   #95
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by boatpoker View Post
AC can cause corrosion on a boat, but at such a slow rate it is unlikely you'll notice it for years or more likely, decades.
He is also grounded to the neighbor boat's DC. Although the galvanic isolator is there, is the isolation transformer passing it's earth connection? (depends on how it is configured)
Thumbs Up is offline   Reply With Quote
Old 09-05-2021, 15:33   #96
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,401
Re: Marine AC - Why Tie Neutral and Earth?

Hahahaha... guys, when the ground becomes active... you may get a vulcanic eruption! The ground in my diagram are just a bunch of wires. You may get a fault in a wind instrument which may make your ground active.. the horror!

About ground to neutral relays: these exist in inverters as well as auto transformers. It is correct that these must not be used. In the Multiplus this is just a configuration setting.

About the genset connected wrong: that’s hilarious it’s actually the only way to get full genset output because it enforces perfect balance over the output windings, which you don’t get when you connect it’s neutral. In fact, only connecting L1 and L2 from genset into an auto transformer which creates a new neutral (like I do) is the recommended way for full genset output.

If you don’t know how a floating power distribution system works then go read up and study it instead of posting that it’s wrong. It’s not wrong, it’s in common use even when your house doesn’t have it!

About my 50A shore power: it should have an isolation transformer but I don’t want a 12kW transformer aboard. I get away with this because my auto transformers don’t ground neutral (I tried what happens: 1.3kW went into shore ground!) and all the regular grounding is in place. Also, I only use this in my own slip where I’m sure the pedestal is in good order (I own the slip).
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-05-2021, 15:48   #97
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Marine AC - Why Tie Neutral and Earth?

Your 50A shore power earth is connecting all of your green wires to shore neutral. Your isolated outlets have their grounds connected to shore power. They should connect to the autotransformer neutrals.
Thumbs Up is offline   Reply With Quote
Old 09-05-2021, 15:50   #98
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,401
Re: Marine AC - Why Tie Neutral and Earth?

For reading up on this, start with section 7.5 on page 60 here: https://www.victronenergy.com/upload...limited-EN.pdf

The section is about mobile installations, where no grounding rods are hammered into the earth.

It amazes me why this is so hard to understand... let’s make it simple: you have a car or motorhome with an inverter: what is your ground? You drive a rod into the soil when you switch on the inverter or start the generator? No you don’t! Yet all ground wiring is in place... it’s called chassis ground instead of earth ground.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-05-2021, 15:53   #99
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,743
Re: Marine AC - Why Tie Neutral and Earth?

so answer this question...

Quote:
Originally Posted by smac999 View Post

so if you take the hot feed wire at the AC panel and short it to the green ground wire what happens?... under inverter, gen , 240v, and 120v shore
smac999 is offline   Reply With Quote
Old 09-05-2021, 16:00   #100
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,401
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by Thumbs Up View Post
Your 50A shore power earth is connecting all of your green wires to shore neutral. Your isolated outlets have their grounds connected to shore power. They should connect to the autotransformer neutrals.
Well... no, they connect to the galvanic isolator. And with an ungrounded neutral... guess what... you don’t connect ground to neutral

Haha. I know the 50A is different. What is supposed to be the neutral in the outlet gets a potential to ground, which isn’t normal. But with an ungrounded neutral, that’s how it is.

Let’s take a different approach: you show me a “dangerous” situation with ungrounded neutral and I’ll explain why it isn’t dangerous. Nobody ever came up with something except for the two simultaneous appliance isolation failures that are touched simultaneously... which highly unlikely situation is protected by gfci outlets.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-05-2021, 16:01   #101
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by s/v Jedi View Post
For reading up on this, start with section 7.5 on page 60 here: https://www.victronenergy.com/upload...limited-EN.pdf

The section is about mobile installations, where no grounding rods are hammered into the earth.

It amazes me why this is so hard to understand... let’s make it simple: you have a car or motorhome with an inverter: what is your ground? You drive a rod into the soil when you switch on the inverter or start the generator? No you don’t! Yet all ground wiring is in place... it’s called chassis ground instead of earth ground.
Quote:
A mobile system typically connects to a variety of power sources it is sometimes not clear which of the leads in
the shore power supply is connected to earth or if earth is connected at all. Also phase and neutral may have
not been wired correctly. Connecting a supply like this to a mobile system can potentially create a short circuit
to earth. Or earth is missing completely
As per your diagram, if you have your 50A supply plugged in, you are connected to shore ground and therefore shore neutral. You don't want your isolated outlets to safety ground to that.
Thumbs Up is offline   Reply With Quote
Old 09-05-2021, 16:06   #102
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by s/v Jedi View Post
Well... no, they connect to the galvanic isolator. And with an ungrounded neutral... guess what... you don’t connect ground to neutral
A galvanic isolator passes the ground connection but filters out any DC current. You had stated in an earlier post that all of your outlet grounds are connected to these wires. They should not be. Not only are you introducing shore ground/neutral potential to your appliance cases, this connection is also not providing any safety benefit. Your outlet grounds would be better off left open.
Thumbs Up is offline   Reply With Quote
Old 09-05-2021, 16:09   #103
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by s/v Jedi View Post

Let’s take a different approach: you show me a “dangerous” situation with ungrounded neutral and I’ll explain why it isn’t dangerous. Nobody ever came up with something except for the two simultaneous appliance isolation failures that are touched simultaneously... which highly unlikely situation is protected by gfci outlets.
I am not arguing against the merits of a floating AC supply, It is just that you have your outlet grounds tied to the wrong place.
Thumbs Up is offline   Reply With Quote
Old 09-05-2021, 16:12   #104
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,401
Re: Marine AC - Why Tie Neutral and Earth?

Quote:
Originally Posted by smac999 View Post
so answer this question...
Okay. Remember, both wires are to be considered “hot” because the neutral isn’t grounded. When you create a short between a hot and boat ground, nothing happens. I know it’s dull but absolutely nothing happens. You can freely touch the ground wire, metal appliances, even when touching earth with your other hand. In fact, like someone mentioned, in some cases they do this on purpose. The simple reason is that nor ground, nor earth is a return path.

So there is one exception and that is when the 50A shore power is active. In that case a breaker trips. This is one of the reasons why a true floating power distribution is better: you need at least two isolation faults before a breaker trips. If you install a detector, you can most likely prevent that by installing an isolation fault monitor which warns when the first fault develops so it can be fixed before another fault develops. This is why they use floating power distribution in demanding high availability situations like operating rooms etc.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 09-05-2021, 16:13   #105
cruiser

Join Date: May 2011
Boat: Hitchhiker, Catamaran, 40'
Posts: 1,827
Re: Marine AC - Why Tie Neutral and Earth?

If you connect your outlet grounds to your transformer neutral, it is still a floating system, because those grounds are not earthed, and your neutral is not really neutral. And if you have RCD breakers in the panel, that outlet ground wire becomes a sense wire that will trip the RCD at 30ma as a safety backup to your GFCI outlets.
Thumbs Up is offline   Reply With Quote
Reply

Tags
marine


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Why can't people tie dinghies up properly ? chrisr Seamanship & Boat Handling 53 08-01-2021 12:48
Why does Yanmar recommend leaving SD20 in neutral while sailing MikeTC Engines and Propulsion Systems 45 01-01-2020 18:15
Is it OK to use common earth and neutral for AC wiring routes? dinghysailor Electrical: Batteries, Generators & Solar 21 02-02-2019 19:49
Google Earth plugin doesn't start Google Earth balticsailor OpenCPN 11 02-07-2015 03:07
Why Tie Stuff Down in a Storm . . . SaltyMonkey General Sailing Forum 23 08-09-2010 12:08

Advertise Here


All times are GMT -7. The time now is 00:19.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.