Old 12-07-2023, 10:22   #16
Registered User

Join Date: Dec 2019
Location: on our boat cruising the Bahamas and east coast
Boat: 2000 Catalina 470 #058
Posts: 1,320
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by Senojev View Post
Not be contentious but a fuse is not “required”. ABYC states “overcurrent protection device” and goes on to give the options of a breaker or fuse.

so noted
__________________
Sailing a Catalina 470; now retired
GreenWave is offline   Reply With Quote
Old 12-07-2023, 10:22   #17
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,740
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by Celestialsailor View Post
Also, I guess it would not be a good idea to wire the MPPT to the battery switch. But to the house batteries directly. And if I want to charge up my starter battery, I could switch my battery switch to "Both" and charge it that way. Does that sound feasible?

Yes. Just like any other single output charging source, of course depending on how it's wired.
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 12-07-2023, 11:46   #18
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Hunter 340
Posts: 1,432
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by Senojev View Post
Comment 2) does not apply just to LiFePO4, it applies to any large bank.
Very true I worded that badly. All fuses should have appropriate AIC but the very high short circuit current of LFP cells means that generally speaking you are going to need a Class T fuse (or something with even higher AIC). Lead Acid batteries due to the higher internal resistance still should have appropriate AIC but it being a lower value means more fuse types are acceptable.
Statistical is offline   Reply With Quote
Old 12-07-2023, 13:42   #19
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,352
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by Senojev View Post
If you are using 10AWG yes but using 10AWG is a mistake. You should be using 6AWG to get a voltage drop of around 3%. With 10AWG you are giving away almost 1V. That’s why S/v Jedi says to use 6AWG and a 60A fuse. I prefer a good quality breaker but others prefer fuses.
Exactly.

It doesn’t matter how much current there is between solar panels and the controller; that is a different circuit. Between controller and battery you have the battery charge current that can be up to 40A. To limit cable losses, this should be an AWG 6 cable and the rule of thumb fuse value is 1.5x maximum of 40A so that is 60A. The AWG 6 can handle 120A (with big losses) so at half of that we have plenty safety margin.

For fuses, I use a fuse box but you can use MRBF fuses as well, like these: https://www.bluesea.com/products/215...k_-_30_to_300A

I use these: https://www.bluesea.com/products/cat...ocks/SafetyHub
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 12-07-2023, 13:48   #20
Registered User

Join Date: Feb 2023
Posts: 16
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by Celestialsailor View Post
Also, I guess it would not be a good idea to wire the MPPT to the battery switch. But to the house batteries directly. And if I want to charge up my starter battery, I could switch my battery switch to "Both" and charge it that way. Does that sound feasible?
I’d suggest you do a bit more research here…controllers are not usually set up to charge dual battery banks in parallel, especially if they are different types/capacities. There are options, but require more hardware.
SunnyIsleMark is offline   Reply With Quote
Old 12-07-2023, 13:59   #21
Registered User
 
Celestialsailor's Avatar

Join Date: Nov 2006
Location: Back in Northern California working on the Ranch
Boat: Pearson 365 Sloop and 9' Fatty Knees.
Posts: 10,477
Images: 5
Re: MPPT to Batteries Circuit breaker.

Thanx everyone, I'm glad I posted this. I will take all this advice and be able to sleep at night...

I would also like to confirm that if the MPPT feeds the house bank, that by switching the battery bank selector to both will flow a charge into the starter battery as well.
__________________
"Life is not a journey to the grave with the intention of arriving safely in a pretty and well-preserved body, but rather to skid in broadside, thoroughly used up, totally worn out, and loudly proclaiming: Wow - what a ride!"
Celestialsailor is offline   Reply With Quote
Old 12-07-2023, 13:59   #22
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,740
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by SunnyIsleMark View Post
I’d suggest you do a bit more research here…controllers are not usually set up to charge dual battery banks in parallel, especially if they are different types/capacities. There are options, but require more hardware.

It still amazes me how much misinformation gets written almost matter-of-factly




Why not? Most house banks ARE parallel batteries. While correct about different types, only (not especially) if their charging requirements are different (i.e., AGM and FLA are very very similar). The B position on a 1-2-B switch stands for both, which means parallel, and requires no more hardware. Controllers don't know what's downstream of them.


The real issue is any voltage sensing, but the OP is asking if could do this on a limited, controlled manner. Not an issue, I believe. Just dump a few amps into the reserve/start bank.
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 12-07-2023, 14:24   #23
Registered User
 
thomm225's Avatar

Join Date: Aug 2011
Location: Lower Chesapeake Bay Area
Boat: Bristol 27
Posts: 10,785
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by Senojev View Post
Not be contentious but a fuse is not “required”. ABYC states “overcurrent protection device” and goes on to give the options of a breaker or fuse.
Right.

I still haven't added a fuse to my Victron 75/15 MPPT Controller or any of the other 5 PWM Controllers I have used since 2011 but may at some point.

I only have 115 watts of panels feeding my two 6 volt 220 ah batteries at this time so not a lot of current.

Using 14 Gauge Wire from the controller to the batteries. 10 and 14 Gauge from the panels to the controller.

My old 65 Watt Panel faces straight up as it is on the Aft Lazarette and the Renogy 50 Watt to the side. I rotate it as necessary to face the Sun.

Neither is hard mounted.
Attached Thumbnails
Click image for larger version

Name:	IMG_1213 (2).jpg
Views:	53
Size:	401.8 KB
ID:	278095   Click image for larger version

Name:	IMG_1210 (2).jpg
Views:	54
Size:	397.0 KB
ID:	278096  

Click image for larger version

Name:	IMG_1207 (2).jpg
Views:	47
Size:	410.2 KB
ID:	278097   Click image for larger version

Name:	IMG_0642 (4).jpg
Views:	52
Size:	454.4 KB
ID:	278098  

thomm225 is offline   Reply With Quote
Old 12-07-2023, 14:38   #24
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,352
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by thomm225 View Post
Right.

I still haven't added a fuse to my Victron 75/15 MPPT Controller or any of the other 5 PWM Controllers I have used since 2011 but may at some point.

I only have 115 watts of panels feeding my two 6 volt 220 ah batteries at this time so not a lot of current.

Using 14 Gauge Wire from the controller to the batteries. 10 and 14 Gauge from the panels to the controller.
The fuses are not for the current coming from the controller; they are for the current that can come from the battery in case of something bad happening to a controller. This is why the fuse is as close to the battery as possible and why it is rated for the wiring used.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 12-07-2023, 14:41   #25
Registered User

Join Date: May 2016
Posts: 108
Re: MPPT to Batteries Circuit breaker.

Although the current from your controller is small, you still need to protect the cable if a short develops between the battery and the controller to prevent the cable from becoming overheated and burning. Have you ever touched a wrench to both positive and negative terminals? Not fun, especially if it welds itself!

Please add a fuse of the appropriate size as close to the battery as you can, ideally within 7” or if not possible a max. of 40” and cover the cable with protective wire loom.

End of PSA!
Senojev is offline   Reply With Quote
Old 12-07-2023, 14:48   #26
Registered User
 
thomm225's Avatar

Join Date: Aug 2011
Location: Lower Chesapeake Bay Area
Boat: Bristol 27
Posts: 10,785
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by s/v Jedi View Post
The fuses are not for the current coming from the controller; they are for the current that can come from the battery in case of something bad happening to a controller. This is why the fuse is as close to the battery as possible and why it is rated for the wiring used.
That makes sense although a bit far fetched.

You wouldn't want a fire offshore though so I have ordered these inline fuse holders w/fuses.

https://www.amazon.com/MulWark-Inlin...zcF9hdGY&psc=1

To be installed before I round the Outer Banks. Or sooner...

You never can tell though.

We had a 28 volt/125 Amp Power Supply that was being pulled down by shorted wires just last week. The wire bundle had been up against the Rudder Pedals adjuster.

https://www.bellnw.com/products/ametek-dlm-32-125e

You can adjust the rudder pedals on this aircraft to suit you as the pilot.

Over the years the wire bundle covering got worn off then 2 wires had gotten exposed after the insulation on them got worn through.

Took us hours to figure it out as this power supply didn't crowbar but would come back on as soon as it's overcurrent protection current dropped the voltage down far enough. I hadn't seen that before so was observing the troubleshooting.

We rarely get old school problems these days.

So the cockpit lighting and Instruments would cycle on and off continuously. Techs finally started disconnect Phoenix I/O Module Banks then individual Instruments until the problem stopped.

The wires had shorted out to an Instrument's Metal framing.

It powered the Phoenix I/O which powered all the Instruments in the Cockpit.
Attached Thumbnails
Click image for larger version

Name:	Phoenix.jpg
Views:	48
Size:	9.1 KB
ID:	278099  
thomm225 is offline   Reply With Quote
Old 12-07-2023, 15:19   #27
Registered User

Join Date: Feb 2023
Posts: 16
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by Stu Jackson View Post
It still amazes me how much misinformation gets written almost matter-of-factly




Why not? Most house banks ARE parallel batteries. While correct about different types, only (not especially) if their charging requirements are different (i.e., AGM and FLA are very very similar). The B position on a 1-2-B switch stands for both, which means parallel, and requires no more hardware. Controllers don't know what's downstream of them.


The real issue is any voltage sensing, but the OP is asking if could do this on a limited, controlled manner. Not an issue, I believe. Just dump a few amps into the reserve/start bank.
Thanks for the rude response to my well intended comment, but I stand by my suggestion.
You have touched on a couple of the reasons why both more information and more research is warranted. Amount of relative depletion is another.
But I’m done here.
SunnyIsleMark is offline   Reply With Quote
Old 12-07-2023, 15:20   #28
Registered User
 
thomm225's Avatar

Join Date: Aug 2011
Location: Lower Chesapeake Bay Area
Boat: Bristol 27
Posts: 10,785
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by thomm225 View Post
That makes sense although a bit far fetched.

You wouldn't want a fire offshore though so I have ordered these inline fuse holders w/fuses.

https://www.amazon.com/MulWark-Inlin...zcF9hdGY&psc=1

To be installed before I round the Outer Banks. Or sooner...

You never can tell though.

We had a 28 volt/125 Amp Power Supply that was being pulled down by shorted wires just last week. The wire bundle had been up against the Rudder Pedals adjuster.

https://www.bellnw.com/products/ametek-dlm-32-125e

You can adjust the rudder pedals on this aircraft to suit you as the pilot.

Over the years the wire bundle covering got worn off then 2 wires had gotten exposed after the insulation on them got worn through.

Took us hours to figure it out as this power supply didn't crowbar but would come back on as soon as it's overcurrent protection current dropped the voltage down far enough. I hadn't seen that before so was observing the troubleshooting.

We rarely get old school problems these days.

So the cockpit lighting and Instruments would cycle on and off continuously. Techs finally started disconnect Phoenix I/O Module Banks then individual Instruments until the problem stopped.

The wires had shorted out to an Instrument's Metal framing.

It powered the Phoenix I/O Module that powered that Instrument in the Cockpit.
Correction.

Took us hours to figure it out as this power supply didn't crowbar but would come back on as soon as it's overcurrent protection dropped the current down far enough. I hadn't seen that before so was observing the troubleshooting.
thomm225 is offline   Reply With Quote
Old 12-07-2023, 16:21   #29
Registered User
 
Stu Jackson's Avatar

Join Date: Jan 2011
Location: Cowichan Bay, BC (Maple Bay Marina)
Posts: 9,740
Re: MPPT to Batteries Circuit breaker.

Quote:
Originally Posted by s/v Jedi View Post
The fuses are not for the current coming from the controller; they are for the current that can come from the battery in case of something bad happening to a controller. This is why the fuse is as close to the battery as possible and why it is rated for the wiring used.

Quote:
Originally Posted by thomm225 View Post
That makes sense although a bit far fetched.

>>>>>>

jedi,


I guess thomm225 still hasn't gotten the Memo about his battery bank, however small it may be, is just a BIG BOMB waiting to go off and the only protection is that fuse he thinks is far fetched.


Heck, decades ago when somebody explained it to me that way, I hastened to listen and understand.


Anybody who still doesn't "get it" and thinks the fuse is only to protect the equipment downstream oughta get the Memo, too.
__________________
Stu Jackson
Catalina 34 #224 (1986) C34IA Secretary
Cowichan Bay, BC, SR/FK, M25, Rocna 10 (22#) (NZ model)
Stu Jackson is offline   Reply With Quote
Old 12-07-2023, 16:30   #30
Registered User

Join Date: May 2015
Location: Muskegon, Mi
Boat: Columbia 36
Posts: 1,259
Re: MPPT to Batteries Circuit breaker.

Yeah that's not far fetched at all. If the wires or controller short out, you need a fuse in there. One might get confused thinking the controller is a power source so the fuse goes on that end. You could put a fuse on both ends but lacking that, put it at the bigger source end. A battery capable of putting out maybe 1000 amps in a short or the controller at 20 amps? It goes at the battery end. And again it's perfectly ok to fuse at below the wire's capacity. The fuse will just blow quicker and that's not a bad thing.
capt jgw is offline   Reply With Quote
Reply

Tags
batteries, mppt


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Windlass+engine to LFP hybrid starter/house:only breaker or breaker+disconnect relay? CaptainRivet Lithium Power Systems 11 26-05-2023 07:41
Breaker sizing (Amps) in breaker panel geoffr Electrical: Batteries, Generators & Solar 33 28-04-2017 08:26
Earth Leak Circuit Breaker Wire Overheating...! raya Electrical: Batteries, Generators & Solar 8 27-05-2010 21:22
Fuse or Circuit Breaker ? ggray Electrical: Batteries, Generators & Solar 5 15-10-2009 15:41
parallel a circuit breaker skyking2 Electrical: Batteries, Generators & Solar 13 03-11-2006 22:00

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 22:09.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.