Multiple Shunts

Hello,

I picked up a box of clever dual display Amp and Volt meters at an auction of a electrical supplier that was going out of business.

Since I have these, I thought I could place them in several locations (Flybridge and engine room) for easy reference.

I have the Victron Blue Power Panel at the pilot house, and I do not want to do anything to disrupt its accuracy.

I am wondering if I have several shunts inline, is it OK ? I have emailed Victron but have not received a reply yet.

Have a look at the diagram and tell me your thoughts...

Alan
Attached Thumbnails
Click image for larger version

Name:	Meters2.png
Views:	887
Size:	268.6 KB
ID:	60565  
Hkalan is offline   Reply With Quote
Old 09-05-2013, 04:32   #2
Registered User

Join Date: Apr 2012
Posts: 585
Re: Multiple Shunts

As installed in your drawing you will only display current. The shunts' voltage drop will vary due to current and you will drive the instruments' ampere readings with that small voltage. If the instrument is sensitive enough it will display the millivolt drop across the shunt but not the house bank voltage which you desire. In order to sense the house bank voltage you must wire the displays to the positive (red) side of the house bank (note the red wire to the Victron shunt which allows it to monitor the voltage as well as power the instrument.

Several shunts in line are fine but why not use the same shunt that the Victron uses? The Victron should never know the other instruments are there as long as they are small electronic loads.
fryewe is offline   Reply With Quote
Old 09-05-2013, 04:46   #3
Registered User
 
Hkalan's Avatar

Join Date: Nov 2011
Location: Hong Kong
Boat: Bertram 46.6 FBMY
Posts: 260
Re: Multiple Shunts

Hello,

I do have the meters being fed from the positive post of the battery to read the voltage of the bank.

The meter does not require any additional feed to power the LED's. I am not sure how it is done... but I have one installed on each engine bank, and it works nice.

I talked to the Victron dealer I bought the 24/5000 Multiplus from here. He said that I cannot connect any other meter to the Victron Shunt. It will effect accuracy. They did not know how to answer the question (100%) about the multiple shunts inline, so passed me to Victron directly.

Alan
Hkalan is offline   Reply With Quote
Old 09-05-2013, 04:52   #4
Registered User

Join Date: Apr 2012
Posts: 585
Re: Multiple Shunts

Those additional shunts will have ZERO effect on the VICTRON.

They are added complexity in your system and the connections have to kept tight to avoid high resistance and its associated heating but they are no different electrically than any other load put on your system - a fan or a laptop or other - except they are such a small load they should be imperceptible to your VICTRON.
fryewe is offline   Reply With Quote
Old 09-05-2013, 05:14   #5
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,206
Re: Multiple Shunts

Quote:
Originally Posted by Hkalan View Post
Hello,

I picked up a box of clever dual display Amp and Volt meters at an auction of a electrical supplier that was going out of business.

Since I have these, I thought I could place them in several locations (Flybridge and engine room) for easy reference.

I have the Victron Blue Power Panel at the pilot house, and I do not want to do anything to disrupt its accuracy.

I am wondering if I have several shunts inline, is it OK ? I have emailed Victron but have not received a reply yet.

Have a look at the diagram and tell me your thoughts...

Alan
Both of those meters can be fed from a single shunt. You don't need both there. You can't use the Victron shunt because it is a 50mV shunt and the other shunts you show are 75mV...

Make sure your new meters are calibrated for a 75mV shunt and not a 50mV shunt. A lot of the stuff showing up from China eBay re-sellers these days is 75mV..

If the displays are set for a 50mV shunt then you could just tap into the batt and load sides of the Victron shunt and get your amperage readings with a single shunt.
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 09-05-2013, 05:38   #6
Registered User
 
Hkalan's Avatar

Join Date: Nov 2011
Location: Hong Kong
Boat: Bertram 46.6 FBMY
Posts: 260
Hello,

The shunt and meter are together in the package and matching 75mV.

On the back of the package it says "engineered in Japan, Manufactured in China". Same as my Sony TV HaHaHa...

I am going to try with individual shunts, then with 2 in parallel off 1 shunt.

Thanks for your feedback !!

Alan
Hkalan is offline   Reply With Quote
Old 09-05-2013, 05:45   #7
Registered User

Join Date: Aug 2009
Location: between the devil and the deep blue sea
Boat: a sailing boat
Posts: 20,469
Re: Multiple Shunts

That's also my idea. Maybe one shunt is enough?

b.
barnakiel is offline   Reply With Quote
Old 09-05-2013, 05:47   #8
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
Re: Multiple Shunts

The current is the same anywhere in a series circuit (basic law). It's the voltage which changes with loads/resistances.

Shunts measure voltage-drops across the shunt. In this case, each shunt individually.

Ergo....you can put them in series without affecting their accuracy.

Bill
btrayfors is offline   Reply With Quote
Old 09-05-2013, 06:48   #9
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,206
Re: Multiple Shunts

Quote:
Originally Posted by btrayfors View Post
The current is the same anywhere in a series circuit (basic law). It's the voltage which changes with loads/resistances.

Shunts measure voltage-drops across the shunt. In this case, each shunt individually.

Ergo....you can put them in series without affecting their accuracy.

Bill
Yes exactly! But, why add all the unnecessary connections if you don't have to. A 0-75mV drop is the same anywhere in the system so one shunt with both panels measuring the VD on the same shunt will work fine. It will also avoid any more connections than necessary in the large gauge wiring.... All that is needed is to stack the load and batt wires for the meters on the load and batt side of one shunt.

Of course in order to get accurate measurements the Victron and Japan meter shunts need to be "equal" and no loads can bypass either shunt or they will be inaccurate.

As drawn the ship ground (assuming going off to engine) and the Japan meter neg leads all need to be run to the 500A buss bar...

__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 09-05-2013, 07:12   #10
Registered User

Join Date: Dec 2006
Location: Seattle
Boat: Cal 40 (sold). Still have a Hobie 20
Posts: 2,955
Images: 7
Re: Multiple Shunts

I don't think the Victron works this way, but there is a situation where you can't share shunts. Stewart Warner has (had?) an ammeter that uses a shunt where the gage is an ammeter, not a volt meter. Both paths are low resistance, with the gage getting 1/6th of the total current. Adding another gage to this shunt, gages in series or parallel, will change the resistance ratios and mess you up.
cal40john is offline   Reply With Quote
Old 09-05-2013, 07:51   #11
Marine Service Provider
 
Maine Sail's Avatar

Join Date: Jan 2007
Location: Maine
Boat: CS-36T - Cupecoy
Posts: 3,206
Re: Multiple Shunts

Quote:
Originally Posted by cal40john View Post
I don't think the Victron works this way, but there is a situation where you can't share shunts. Stewart Warner has (had?) an ammeter that uses a shunt where the gage is an ammeter, not a volt meter. Both paths are low resistance, with the gage getting 1/6th of the total current. Adding another gage to this shunt, gages in series or parallel, will change the resistance ratios and mess you up.
All these displays are doing is looking at the mV drop across the shunt. I have done this many times with Blue Sea and other simple ammeters so long as they are both the same mV range display & shunt it will not be an issue. The two wires measuring the mV drop across the shunt really carry no meaningful current they are just sensing voltage. The meters are fed by a separate power wire and the load and batt side wires are simply mV sensing wires.

It's really no different than putting my Fluke across a shunt set to the mV scale. It would read the same on both shunts thus one shunt will avoid more terminations than are necessary and be easier to install....

Course the OP can wire it however he decides is best, I am just trying to make his life a little easier....
__________________
Marine How To Articles
Maine Sail is offline   Reply With Quote
Old 09-05-2013, 17:23   #12
Registered User
 
Hkalan's Avatar

Join Date: Nov 2011
Location: Hong Kong
Boat: Bertram 46.6 FBMY
Posts: 260
Re: Multiple Shunts

Hello,

Great feedback ! Thank you so very much !

I was not thinking about the voltage negative coming from the 500A buss bar. Had my eyes on the shunts all the time worrying about the current reading ! Thanks !!!

I will try this...

Alan
Attached Thumbnails
Click image for larger version

Name:	Meters3.png
Views:	480
Size:	267.0 KB
ID:	60607  
Hkalan is offline   Reply With Quote
Old 02-06-2013, 04:44   #13
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,712
Re: Multiple Shunts

you need the ship ground on the bus as well. if they were battery monitors I would use all 3 shunts. the 2 gauges in parallel would probably effect the readings a bit. although if it's just an amp gauge, and not a battery monitor calculating AH I probably wouldn't worry about the minor error you're probably end up with. and go with 2.
smac999 is offline   Reply With Quote
Old 10-06-2013, 06:55   #14
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 363
Re: Multiple Shunts

Why is a wire from the pos battery to the neg shunt?
Zil is offline   Reply With Quote
Old 10-06-2013, 07:32   #15
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Multiple Shunts

Just be aware that some of these DPMs cannot be powered from the device under test , check your documentation, `ie they cannot measure relative to their supply GND.

Usually a negative rail generator is needed, some DPMS have then , real cheapies dont.

dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 08:00.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.