Re: Multiple solar panels to a common bus bar?

If you still only have two 12V nominal panels and an mppt controller you may get better performance by wiring the two panels in series.

Big difference between the requirements for domestic solar, which tends to use higher voltages from a lot of series wired panels, and boats where voltages tend to be much lower.
__________________
Satiriker ist verboten, la conformité est obligatoire
RaymondR is offline   Reply With Quote
Old 08-11-2022, 22:25   #47
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by Mike OReilly View Post
Assuming you're measuring in optimal conditions; clear noonish sky, no panel shading, panels oriented as much as possible toward the sun... then it does seem low, unless you're in a pretty high latitude. I've never hit my theoretical max of 400 watts on my system, but I often see over 300 watts, although the norm is more around 200. I run a Victron MPPT 100/30.

If all the more obvious problems are ruled out, are you sure both panels are producing? Sounds like the right peak amount from just one panel.
I'm looking at the app on my victron smart charger.
It shows the max watts on the day.
Im in Sydney and they are getting good unobstructed sun at times through the day.
I've tossed a towel over individual panels and saw roughly a 50 percent decline as each was covered.
I've used my tester to check the amps travelling through the wires coming out of each panel.
Oddly. For example
Panel 1 positive lead shows 10 Amps.
Panel 1 negative lead shows 5 amps
Panel 2 positive lead shows 5 amps
Panel 2 negative lead shows 10 Amps
This is an example of what I read you would have thought that both the positive leaves will it read the same and negative leads read the same what are your thoughts? Is this normal?
I did think that one of my quality Chinese panels may have been factory wired and reverse but I checked this and found that they were both wired correctly from the factory.
I will post the new figures tomorrow.
Hoohaa is offline   Reply With Quote
Old 08-11-2022, 22:27   #48
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by RaymondR View Post
If you still only have two 12V nominal panels and an mppt controller you may get better performance by wiring the two panels in series.

Big difference between the requirements for domestic solar, which tends to use higher voltages from a lot of series wired panels, and boats where voltages tend to be much lower.
I suppose the real question I wanted answered is if I have a 350 watt panel and put it out in the sun is there any chance I'm going to get 350 Watts from the panel assuming or conditions are perfect?
Hoohaa is offline   Reply With Quote
Old 08-11-2022, 22:44   #49
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Multiple solar panels to a common bus bar?

Yes that what was my original thought I will double check it tomorrow.
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 08-11-2022, 22:49   #50
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Multiple solar panels to a common bus bar?

On a side note.
For anyone that's interested I'm using Emily and Clark's bbms system 2 combine my 705 amp hour lead bank with my 150 amp hour lithium battery.
So far it's working brilliantly. So far I'm only a couple of weeks in on this.
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 08-11-2022, 22:50   #51
Registered User

Join Date: Apr 2007
Location: Australia
Boat: Island Packet 40
Posts: 6,501
Images: 7
Re: Multiple solar panels to a common bus bar?

With MPPT it comes down to watts in and watts out. However I notice with mine, which I rewired to series, after I discovered how little charging was actually taking place, that the performance was far better in the mornings, evenings and overcast days. I think the reason may be that MPPT has a higher overhead than series or PWM controllers.
__________________
Satiriker ist verboten, la conformité est obligatoire
RaymondR is offline   Reply With Quote
Old 09-11-2022, 02:45   #52
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,103
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by Hoohaa View Post
I suppose the real question I wanted answered is if I have a 350 watt panel and put it out in the sun is there any chance I'm going to get 350 Watts from the panel assuming or conditions are perfect?
Yes, maybe more even. Of course you have to have a suitable load for the panel to deliver the power into. For instance, if you only have a 200W load and fully charged batteries, all you can get from the panel is 200W. However if you have say a 400W load, then the panel will supply 350W and the battery will provide the other 50W.

If they are quality panels, the rated power is nominally derated slightly to allow for ageing and to ensure warranty considerations.

Output is also dependent panel temperature; colder is better.

What make and model are your panels?
Do you have a picture of the specification label on the back of the panel?
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 09-11-2022, 04:00   #53
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Multiple solar panels to a common bus bar?

I will post some pictures in the morning.
I just got back on board tonight.
Wotname.
Thanks for that answer. My main load would be recharging my lithium in the morning. I assume it will take whatever the panel's can supply.
I will monitor things when the sun comes out tomorrow.
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 09-11-2022, 05:54   #54
Registered User
 
Mike OReilly's Avatar

Join Date: Sep 2011
Location: Good question
Boat: Rafiki 37
Posts: 14,396
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by Wotname View Post
Yes, maybe more even. Of course you have to have a suitable load for the panel to deliver the power into. For instance, if you only have a 200W load and fully charged batteries, all you can get from the panel is 200W. However if you have say a 400W load, then the panel will supply 350W and the battery will provide the other 50W.
This occurred to me as well. Your charge controller will only produce power sufficient for the demand. How large is your battery bank? And what is its state of charge when you are doing all your observations?

Could it be that the acceptance rate is simply maxed out? I understand lithium can take everything you throw at it, but all other battery chemistries have a limit as to how fast they can accept input amps. You might simply not need all the potential power from your 700 watt system. That is a lot of power for a 40-foot monohull.
__________________
Why go fast, when you can go slow.
BLOG: www.helplink.com/CLAFC
Mike OReilly is online now   Reply With Quote
Old 09-11-2022, 06:03   #55
Registered User
 
Mike OReilly's Avatar

Join Date: Sep 2011
Location: Good question
Boat: Rafiki 37
Posts: 14,396
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by Hoohaa View Post
I'm looking at the app on my victron smart charger.
It shows the max watts on the day.
Im in Sydney and they are getting good unobstructed sun at times through the day.
I've tossed a towel over individual panels and saw roughly a 50 percent decline as each was covered.
I've used my tester to check the amps travelling through the wires coming out of each panel.
Oddly. For example
Panel 1 positive lead shows 10 Amps.
Panel 1 negative lead shows 5 amps
Panel 2 positive lead shows 5 amps
Panel 2 negative lead shows 10 Amps
This is an example of what I read you would have thought that both the positive leaves will it read the same and negative leads read the same what are your thoughts? Is this normal?
I did think that one of my quality Chinese panels may have been factory wired and reverse but I checked this and found that they were both wired correctly from the factory.
I will post the new figures tomorrow.
Good to know they're all producing. Still possible one is under-producing though. Can you disconnect one panel, and then the other, to see what the MPPT sees?

This differing current measure is beyond my knowledge. Seems odd, but I've never checked my panels currents at the leads. Perhaps others better versed can answer (Wottie?).

Regarding max panel power, my belief (which I've never really investigated) is that the ratings are theoretical maxs that can only be achieved in ideal circumstances. Much like max fuel efficiency in a car, it's only possible in perfect conditions, and reality rarely provides perfection.

But I would expect you to be hitting the 3/4 mark, which is closer to 500 watts, not your reported 290. That seems too low -- unless there is something else going on.
__________________
Why go fast, when you can go slow.
BLOG: www.helplink.com/CLAFC
Mike OReilly is online now   Reply With Quote
Old 09-11-2022, 13:17   #56
Registered User

Join Date: Apr 2007
Location: Australia
Boat: Island Packet 40
Posts: 6,501
Images: 7
Re: Multiple solar panels to a common bus bar?

"Regarding max panel power, my belief (which I've never really investigated) is that the ratings are theoretical maxs that can only be achieved in ideal circumstances. Much like max fuel efficiency in a car, it's only possible in perfect conditions, and reality rarely provides perfection."

Hopefully they actually rest some of their panels to establish the maximum power rating.

The MPPT is supposed to hold the output from the panels at the voltage where maximum wattage of output from them can be achieved.

It's 0700 where I am and the battery monitor is showing 39+ volt and 2+ amps from the panel and 14+ volts and 5.5 amps into the battery so I guess it sort of works.
__________________
Satiriker ist verboten, la conformité est obligatoire
RaymondR is offline   Reply With Quote
Old 09-11-2022, 13:28   #57
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,596
Images: 22
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by Hoohaa View Post
Oddly. For example
Panel 1 positive lead shows 10 Amps.
Panel 1 negative lead shows 5 amps
Panel 2 positive lead shows 5 amps
Panel 2 negative lead shows 10 Amps
How odd. Are these panels wired in series or parallel?
Pete7 is offline   Reply With Quote
Old 09-11-2022, 14:16   #58
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by Pete7 View Post
How odd. Are these panels wired in series or parallel?
parallel.
Hoohaa is offline   Reply With Quote
Old 09-11-2022, 14:46   #59
Registered User
 
Hoohaa's Avatar

Join Date: Jul 2011
Location: Sydney Aus
Boat: Swarbrick 40
Posts: 868
Images: 10
Re: Multiple solar panels to a common bus bar?

This is my set up.Click image for larger version

Name:	IMG20221110090047.jpg
Views:	62
Size:	67.0 KB
ID:	267127Click image for larger version

Name:	IMG20221110090231.jpg
Views:	70
Size:	55.3 KB
ID:	267128Click image for larger version

Name:	IMG20221110090252.jpg
Views:	69
Size:	58.7 KB
ID:	267130Click image for larger version

Name:	Screenshot_2022-11-10-08-59-10-21.jpg
Views:	60
Size:	25.6 KB
ID:	267129
__________________
Drinking hot tea on a hot day is like banging your head against a wall . It feels good when you stop.... "Terry" my dad.
Hoohaa is offline   Reply With Quote
Old 09-11-2022, 15:23   #60
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,103
Re: Multiple solar panels to a common bus bar?

Quote:
Originally Posted by Hoohaa View Post
Update
I've installed my new twin 350 Watt panels.
Everything is working but is it normal to only get a maximum of 290 watts out of both the combined panels. Combined they are theoretically 700 watts.
I was told that this is normal but.
Any thoughts?
If this is the case then why the hell did I just spend over $400 upgrading my victron MPPT to A 100/50?
Quote:
Originally Posted by Hoohaa View Post
This panel don't look like a 350W panel to me. It is also a low voltage panel (nominally 12V) - not good.
1. No power stated on specification label - red flag.
2. Only .923 sq M - big red flag
3. No current stated on specification label - red flag

Do you have any other data about the panel e.g model number or sales brochure etc?

FWIW, here is a typical spec for a proper 330W panel (just one I found at random but it is a reasonable quality panel.
Especially compare the panel area which is a good start on how much power you might expect.

https://www.phonosolar.com.au/wp-con...-330W-2020.pdf
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Reply

Tags
panels, solar, solar panels


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
LiFePO4: charge bus, load bus, buffer battery s/v Jedi Lithium Power Systems 3 07-07-2020 16:19
Greenland 34: In salon DC bus bar Marcsailcat Fountaine Pajot 4 04-12-2015 12:35
Bus Bar? jhnhll Marine Electronics 36 15-01-2015 17:26
Interconnecting/Bus Bar Battery Cable Lengths - Some Closure jordiebsocal Electrical: Batteries, Generators & Solar 19 18-08-2014 11:40
Cable Size for AC Grounding Bus to DC Neg Main Bus ? Beausoleil Electrical: Batteries, Generators & Solar 1 26-10-2010 11:19

Advertise Here


All times are GMT -7. The time now is 07:52.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.