Northern Lights Generator Stator

I have a Northern Lights M673M 5.5KW marine diesel generator set with the TF-276KM generator backend.

I've measured the U2-V2 stator coil and measured the resistance at infinite - meaning its an open circuit. The U1-V1 measures fine, so does the rotor.

So it looks like it has to be replace/repaired.

Has anyone ever had to do this with a Northern Lights generator before, and what would you recommend. Having it rewound or replacing the backend?

If you have had it rewound where did you have it done and would you recommend them to me?

If you had to replace the backend can you share the distributor you used?

Sincerely,

BugOutBoat (BOB)
Bugoutboat is offline   Reply With Quote
Old 21-02-2020, 14:01   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,066
Images: 241
Re: Northern Lights Generator Stator

Greetings and welcome aboard the CF, Bob.
Where are you located?
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 22-02-2020, 10:37   #3
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

Quote:
Originally Posted by GordMay View Post
Greetings and welcome aboard the CF, Bob.
Where are you located?

I’m located in Maryland. South of Annapolis.
Bugoutboat is offline   Reply With Quote
Old 22-02-2020, 10:52   #4
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Re: Northern Lights Generator Stator

I would certainly have it rewound, but can’t help you with telling who to take it to there.
Well, actually price it first and compare to replacement cost, but rewinding should be significantly cheaper
a64pilot is offline   Reply With Quote
Old 23-02-2020, 08:59   #5
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

They are hand wound units. So far I have not found anyone who can rewind them. If anyone is aware of a company please do share.
Bugoutboat is offline   Reply With Quote
Old 23-02-2020, 09:26   #6
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,066
Images: 241
Re: Northern Lights Generator Stator

(25) Motor Rewinding & Repair Services serving Maryland
https://www.thomasnet.com/maryland/m...2350808-1.html
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 26-02-2020, 17:25   #7
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

Thank you I will certainly give them a call!!
Bugoutboat is offline   Reply With Quote
Old 19-04-2020, 07:47   #8
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

So after striking out with several companies that offer rewinding I ended up buying a new backend from Northern lights. I've completed the install, the generator starts, but I have the same failure indications as I had before the back end replacement.

Basically the generator does not load, the AVR is holding the voltage but once you load the generator the AVR trips so it's like the AVR is providing all of the loaded output. This is exactly the same problem as before which lead to measuring the stator with infinite resistance, that lead to replacing the backend. Wow this is a bad problem to have.

Open to any ideas?
Bugoutboat is offline   Reply With Quote
Old 23-04-2020, 20:59   #9
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

I disconnected the generator from the boat electrical system to measure the output on the U1 and U2 terminals and measures about 17.5 VAC being supplied by the AVR. When I flip up the output load breaker the diesel bogs as the AVR is telling off voltage. The. Shortly after the AVR breaker trips. The 17.5 volts does not sound good. Boy this is a booger of a problem.
Bugoutboat is offline   Reply With Quote
Old 24-04-2020, 04:28   #10
Registered User
 
Chotu's Avatar

Join Date: Jan 2018
Boat: 50ft Custom Fast Catamaran
Posts: 11,832
Re: Northern Lights Generator Stator

This thread is a heartbreaking one to read. Wow. What about northern lights? They just sold you a very expensive powerhead. Don’t they owe you a little bit of technical support at this point?
Chotu is offline   Reply With Quote
Old 24-04-2020, 06:19   #11
Registered User
 
Sailmonkey's Avatar

Join Date: Sep 2009
Location: Houston
Boat: ‘01 Catana 401
Posts: 9,626
Re: Northern Lights Generator Stator

Quote:
Originally Posted by Bugoutboat View Post
I disconnected the generator from the boat electrical system to measure the output on the U1 and U2 terminals and measures about 17.5 VAC being supplied by the AVR. When I flip up the output load breaker the diesel bogs as the AVR is telling off voltage. The. Shortly after the AVR breaker trips. The 17.5 volts does not sound good. Boy this is a booger of a problem.


What are you loading the gen with when you say it bogs the engine?
Sailmonkey is offline   Reply With Quote
Old 29-04-2020, 09:29   #12
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

Quote:
Originally Posted by Chotu View Post
This thread is a heartbreaking one to read. Wow. What about northern lights? They just sold you a very expensive powerhead. Don’t they owe you a little bit of technical support at this point?
Northern Lights is working with me and have been great through this hole process. It’s just difficult to debug with a customer remotely. They can’t see and check everything. It will get solved and I’ll post the results when done so other boaters can learn from it.
Bugoutboat is offline   Reply With Quote
Old 29-04-2020, 09:32   #13
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

Measuring the stator coils I read 11.2 ohms on both stator coils. The exciter read 22.3 ohms. The values appear close enough to good enough to work. Double checking all connections.
Bugoutboat is offline   Reply With Quote
Old 19-06-2020, 15:21   #14
Registered User

Join Date: Jul 2018
Location: Maryland
Boat: Hunter 460
Posts: 21
Re: Northern Lights Generator Stator

Its been a while and I wanted to get back to finish up on the resolution. So the installation went well, I called up the Bayshore Marine that is a Northern Lights distributor and service provider. They came out and basically the generator was working as soon as they turned it on. So I had basically did everything right and needed the Ora of a mechanic to show up, start it and run the vessels air conditioning off the generator. That cost 451.00 dollars. Felt like kicking the generator. Its all good now and if I every go to sell the boat I can always show that I had a professional check it for 451 dollars. Generator is rocking now though!
Bugoutboat is offline   Reply With Quote
Reply

Tags
generator, Northern Lights


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Air-X stator winding resistances phorvati Electrical: Batteries, Generators & Solar 0 12-09-2019 09:01
Stator failure- Northern Lights 6kw David Hughes Electrical: Batteries, Generators & Solar 69 14-09-2016 11:43
Stepping up the Stator Wavewacker Electrical: Batteries, Generators & Solar 6 24-02-2012 09:24
Want To Buy: Northern Lights Generator Overlord Classifieds Archive 5 10-03-2011 16:01
No Voltage from 6KW Northern Lights Generator Dreaming Yachtsman Electrical: Batteries, Generators & Solar 12 20-12-2007 17:04

Advertise Here


All times are GMT -7. The time now is 10:36.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.