Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 10-07-2018, 08:31   #1
Registered User

Join Date: Jul 2018
Posts: 1
Portable generator grounding safety

I bought a small, 2000 watt portable generator from sportsman for powerful lights on an aluminum boat to gig flounder. The instruction manual says that the generator should be grounded by a copper wire into a ground stake.

Is there any way to safely ground a generator on an aluminum boat in salt water? Do most people even ground their generators on land?

I have no experience with generators.
Josephgriffith is offline   Reply With Quote
Old 10-07-2018, 08:49   #2
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 365
Re: Portable generator grounding safety

Do not ground your portable generator.
Zil is offline   Reply With Quote
Old 10-07-2018, 08:52   #3
Moderator Emeritus
 
a64pilot's Avatar

Cruisers Forum Supporter

Join Date: Oct 2013
Location: Jacksonville/ out cruising
Boat: Island Packet 38
Posts: 31,351
Portable generator grounding safety

Almost all are used with what I think of as a floating ground, or ungrounded if you will.
I know of no one who grounds one on a boat, CO is your killer, seemingly not the lack of a ground.
I want to think that maybe GFCI outlets may be defeated by a lack of a ground, but I’m unsure.

Your far safer from electrocution in salt water, it’s fresh water that is really much more dangerous
a64pilot is offline   Reply With Quote
Old 11-07-2018, 10:15   #4
Zil
Registered User

Join Date: Mar 2013
Location: South Jersey
Posts: 365
Re: Portable generator grounding safety

The GFCI work because the reference is back to the portable. It doesn't need earth ground. The generator is more dangerous if earth grounded. as the black is hot to everything. No earth ground, the hot is only to the generator.
Zil is offline   Reply With Quote
Old 18-10-2018, 16:48   #5
DHC
Registered User

Join Date: Nov 2015
Location: Maryland
Boat: Fountaine Pajot Tobago
Posts: 3
Re: Portable generator grounding safety

A Honda EU2000 portable generator came with my sailboat. When plugged in via my shorepower inlet the reverse polarity light comes on at the AC distribution panel. Is this a problem? Other posts say not to ground the generator

DHC
DHC is offline   Reply With Quote
Old 19-10-2018, 03:27   #6
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,501
Images: 241
Re: Portable generator grounding safety

Greetings and welcome aboard the CF, Joseph.

Per ABYC 11.5.5.2.3
The generator neutral shall be grounded at the generator. (See DIAGRAM 2 or DIAGRAM 4.)

http://www.elettronavigare.it/files/...0americane.pdf

For boats without isolation transformers, to comply with the above requirements in the case of the on-board generator, a very specifically engineered source transfer switch is required. That switch transfers the boat’s AC electrical distribution panel between either 1) off-the-boat shore power as the source of AC power or 2) the on-board generator (genset) as the source of AC power. That switch must be of a double-pole, break-before-make design. That switch design transfers BOTH the hot and the neutral wires of the boat’s AC electrical system.
When the switch is in the “shore power” position, the on-board neutral and the safety ground are bonded together ashore, but NOT connected together on-board the boat.
When the switch is in the “generator” position, the on-board neutral and the safety ground ARE bonded together at the frame of the genset. Remember, the genset, when in operation and switched online, is the “derived source” of the boat’s AC power.
Realize that in that state, the incoming shore power neutral is not connected to the boat’s operational AC electrical system, even if the shore power cords are still connected to the dockside pedestal. That is prevented by the break-before-make design of the Generator Transfer Switch.
FWIW: Portable generators are not generally approved for use aboard boats.
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Reply

Tags
generator, safety


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Portable Inverter Generator or Reg. Generator? Hatch Liveaboard's Forum 54 15-06-2017 23:05
DC Negative Grounding to grounding plate - Isolated shaft Thistle1969 Electrical: Batteries, Generators & Solar 17 27-09-2015 04:51
Portable Generator vs Solar Panels or Wind Generator Sweet As Electrical: Batteries, Generators & Solar 120 16-09-2010 18:27

Advertise Here


All times are GMT -7. The time now is 09:53.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.