Old 14-06-2014, 02:48   #1
Registered User
 
Flying Knight's Avatar

Join Date: Mar 2014
Location: Morro Bay, CA
Boat: Cal 34 Mk. III
Posts: 39
Properly Securing Batteries

What are the requirements for secure installation of batteries?

I have a house and starting bank, located on either side of the ship. In short I'd like to relocate the house bank to the same side as the starting bank. I've made some other changes to the boat so there won't be an issue of weight distribution, but I'm having trouble relocating the house batteries because of space limitations.

The starting batteries are installed in a compartment under a quarter berth. I could locate the house and starting together in the same compartment, but only if they're installed without being in boxes. I'm just not sure if there are reasons other than keeping the batteries secure for having them in the boxes. I could secure the batteries in the compartment with straps, would that be enough for a proper installation? (I do realize there are ventilation issues to consider as well but I've already taken this into consideration.)

Sent from my Nexus 5 using Tapatalk
Flying Knight is offline   Reply With Quote
Old 14-06-2014, 03:07   #2
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,265
Re: Properly Securing Batteries

ABYC "Storage Batteries" Standard E-10 requires in part that batteries be vented outside of accommodation spaces and that batteries be secured so as not to move more than one inch in any direction, that neither battery chargers nor inverters be mounted directly above batteries, have a means of containing spilled electrolyte, that positive terminals be protected by dielectric material, prohibits wing nuts as a means of securing conductors 6AWG and larger, prohibits the use of spring clamp connectors and requires positive conductors be fuse protected within 7” of the battery or 40” if the conductor is fully enclosed with the exception of conductors running to engine starter motors. It is the surveyors opinion that all battery positive conductors be fuse protected.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 14-06-2014, 12:25   #3
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Properly Securing Batteries

if they are flooded acid batterys you need the boxes. if they are agm's you can ditch them.

but I prefer boxes as it protects the terminals.

depending on the type of batteries you can get plain square boxes with nothing sticking out which take up less space, and then secure as needed yourself.
smac999 is online now   Reply With Quote
Old 14-06-2014, 12:33   #4
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,265
Re: Properly Securing Batteries

Quote:
Originally Posted by smac999 View Post
if they are flooded acid batterys you need the boxes. if they are agm's you can ditch them.
Not if you want to be ABYC compliant.
I'll try to dig it out but somewhere in my files I have a photo of an exploded AGM.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 14-06-2014, 12:37   #5
֍֎֍֎֍֎֍֎֍֎

Join Date: Apr 2006
Posts: 15,136
Re: Properly Securing Batteries

So, you can't just drill a couple of 1" holes down through the battery and use lag bolts to secure it to the keel?
hellosailor is offline   Reply With Quote
Old 14-06-2014, 12:48   #6
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,265
Re: Properly Securing Batteries

Quote:
Originally Posted by hellosailor View Post
So, you can't just drill a couple of 1" holes down through the battery and use lag bolts to secure it to the keel?
Only if you use silicone bronze bolts.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 14-06-2014, 13:03   #7
running down a dream
 
gonesail's Avatar

Join Date: Mar 2006
Location: Florida
Boat: cape dory 30 MKII
Posts: 3,152
Images: 7
Send a message via Yahoo to gonesail
Re: Properly Securing Batteries

for flooded: sturdy plastic boxes with lids .. then strapped or bolted down. heres one for 2 golf cart batteries.

__________________
some of the best times of my life were spent on a boat. it just took a long time to realize it.
gonesail is offline   Reply With Quote
Old 14-06-2014, 13:09   #8
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,265
Re: Properly Securing Batteries

The vast majority of battery installations I see look more like this ....
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 14-06-2014, 15:36   #9
Registered User
 
Flying Knight's Avatar

Join Date: Mar 2014
Location: Morro Bay, CA
Boat: Cal 34 Mk. III
Posts: 39
Re: Properly Securing Batteries

So are boxes required by the standard? Just looking at it I don't see why the storage space couldn't meet the standard while ditching the boxes. Any exploding batteries would be contained within, there just needs to be a lining in the entire compartment that will handle the leaking electrolyte. What am I missing?

Sent from my Nexus 10 using Tapatalk
Flying Knight is offline   Reply With Quote
Old 14-06-2014, 19:06   #10
Registered User

Join Date: Dec 2010
Location: W Carib
Boat: Wildcat 35, Hobie 33
Posts: 13,488
Re: Properly Securing Batteries

Quote:
Originally Posted by boatpoker View Post
ABYC "Storage Batteries" Standard E-10 requires in part that ...have a means of containing spilled electrolyte...[/I]
Other than eletrolyte containment, I don't see what in the quoted standard actually requires a box?

In my installation for example, the house bank is contained in its own fiberglass compartment which would contain any spills. It meets all the quoted requirements...except for being vented outside (I can think of only one I've seen that meets this one). No box(es), although they could be accomdated.

Would you still interpret that installation to require a box to be compliant?
belizesailor is offline   Reply With Quote
Old 15-06-2014, 03:17   #11
Registered User
 
Flying Knight's Avatar

Join Date: Mar 2014
Location: Morro Bay, CA
Boat: Cal 34 Mk. III
Posts: 39
Re: Properly Securing Batteries

What constitutes chargers or inverters being "directly above" batteries? My installation will have the batteries in a compartment below the quarter berth, with the charger and inverter installed at the far end of the birth about 3 - 4 feet away. Would that be considered "directly" above?

Sent from my Nexus 5 using Tapatalk
Flying Knight is offline   Reply With Quote
Old 15-06-2014, 04:42   #12
Registered User
 
bletso's Avatar

Join Date: Nov 2013
Location: Louisville, KY
Boat: Globe, cutter/ketch,38
Posts: 726
Re: Properly Securing Batteries

Quote:
Originally Posted by boatpoker View Post
The vast majority of battery installations I see look more like this ....
They all look normal to me heh heh
__________________
www.sailboatvigah.com Boats don't like being neglected, but then neither do significant others!
bletso is offline   Reply With Quote
Old 15-06-2014, 06:40   #13
Registered User
 
colemj's Avatar

Join Date: Oct 2005
Location: Presently on US East Coast
Boat: Manta 40 "Reach"
Posts: 10,108
Images: 12
Re: Properly Securing Batteries

ABYC are not "rules" and there is no requirement to be compliant with them for recreational craft. They are useful as good practice guidelines for most things, but one should use common sense in applying them in particular situations. For example, on most boats, it is almost impossible to fuse the battery within 7". Does having that fuse 14" away make you a dangerous boat?

Venting to the outside vs. interior has been discussed here many times. Hydrogen gas does not collect, is not flammable in low dilute quantities, and is the most easily and readily dispersed gas possible. To have an explosions, your entire bank would need to be boiling out of control, in a closed container, and with an active spark/flame source present.

Batteries venting hydrogen gas into a normal living space is neither dangerous (health) nor flammable. The hydrogen vent rate of normally charged undamaged flooded batteries is very, very small.

Mark
__________________
www.svreach.com

You do not need a parachute to skydive. You only need a parachute to skydive twice.
colemj is offline   Reply With Quote
Old 15-06-2014, 11:48   #14
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Properly Securing Batteries

Quote:
Originally Posted by belizesailor View Post
Other than eletrolyte containment, I don't see what in the quoted standard actually requires a box?

In my installation for example, the house bank is contained in its own fiberglass compartment which would contain any spills. It meets all the quoted requirements...except for being vented outside (I can think of only one I've seen that meets this one). No box(es), although they could be accomdated.

Would you still interpret that installation to require a box to be compliant?
sounds like you already have a big box.
smac999 is online now   Reply With Quote
Old 15-06-2014, 13:41   #15
֍֎֍֎֍֎֍֎֍֎

Join Date: Apr 2006
Posts: 15,136
Re: Properly Securing Batteries

belize-
"Other than eletrolyte containment, ...except for being vented outside "

If you take on sea water and if gets into the batteries, chlorine gas will be released. Which will promptly chew out the eyes and lungs of anyone anywhere that it is vented to.

So...unless you've got sealed batteries, venting *outside* the hull could be a good thing. Just in case the ocean gets to the batteries.
hellosailor is offline   Reply With Quote
Reply

Tags
rope


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Securing 60kg Batteries ! FraidNot Electrical: Batteries, Generators & Solar 3 16-02-2011 07:40
How Do I Know if My Turbo Is Operating Properly ? duncan_ellison Engines and Propulsion Systems 10 11-10-2010 05:10
Depth / Speed Monitor Not Working Properly...Help ! shibbershabber Marine Electronics 6 29-05-2010 13:31
Batteries Not Charging Properly Silpe Electrical: Batteries, Generators & Solar 10 29-12-2009 11:43
How to properly purchase a boat outside of USA Princewig General Sailing Forum 10 20-11-2006 09:00

Advertise Here


All times are GMT -7. The time now is 21:29.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.