Just got my Morningstar TS-MPPT-60 in the mail and an unanticipated issue came to mind and I can't find the answer.

Morningstar seems to want the positive and negative battery and PV cables connected by just screwing them in place. Back in my un-enlightened days I would be OK with this; however, after reading all of Maine Sail's articles I really want to crimp the cables, but there is simply no room for ring terminals.

Are people really find with tighten the screws down on the cables for these controllers? For up to 60 amps? There has to be a better way.

Here is the manual. Will also post a pic in the next.

http://www.morningstarcorp.com/wp-co...ors-Manual.pdf

Am thinking of trying a spade connector, but I would have to trim it to be narrower and I'm not sure the screws tighten down enough.
__________________
Stephen

s/v Carpe Ventum
1983 Sabre 38
My Intro
fallingeggs is offline   Reply With Quote
Old 20-04-2015, 19:12   #2
Registered User

Join Date: Aug 2014
Location: Astoria, NY
Boat: Sabre 38
Posts: 566
Re: Question On Connection To Morningstar MPPT

Click image for larger version

Name:	ImageUploadedByCruisers Sailing Forum1429582353.982014.jpg
Views:	216
Size:	129.8 KB
ID:	100711

For reference, that is a 6 awg ring terminal size #10.

Sent from my iPhone using Cruisers Sailing Forum
__________________
Stephen

s/v Carpe Ventum
1983 Sabre 38
My Intro
fallingeggs is offline   Reply With Quote
Old 20-04-2015, 19:36   #3
Registered User
 
svmariane's Avatar

Join Date: May 2007
Location: On the hard due to wife's medical condition.
Boat: Sold, alas, because life happens.
Posts: 1,829
Re: Question On Connection To Morningstar MPPT

I installed the same controller about 4 years ago - wired up as per instructions provided in the manual. Never had an issue with the wiring or suitability of the product. Extremely happy, in fact.

Went thru Force 12 winds/seas coming out of New Zealand (ref prior posts elsewhere), got nailed, lots of boat damage, seawater flying about the motor room where the controller is mounted - but NEVER had problems or troubles with the solar controller nor with the wiring/connections.

Just my practical experience. YMMV......


'Course, during that big blow it sure helped that the solar panels were double-secured with extra lines!
__________________
"Being offended is not the same thing as being right." Dave Barry.
Laughter is the salve that keeps reality from scaring.
¯\_(ツ)_/¯
svmariane is offline   Reply With Quote
Old 20-04-2015, 20:57   #4
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Question On Connection To Morningstar MPPT

This type of terminal is known as a compression terminal. It has most of the same features as a crimp terminal. It can be hard to measure torque on slotted screw terminals like these but they specify 50 in-lbs which should be adequate. I don't recommend trying to jury rig a ring lug terminal into these compression terminals. The bare stranded wire will work ok if the terminal is torqued correctly.

Make sure the cable is stress relieved so that it does not pull on the compression joint. They provide knockouts for strain relief and these should be used to secure the wire. That will help a lot in preventing the connection from loosening. Also, check the screw terminal for tightness after the system has been running for a while and thereafter every few months check for signs of heating.
transmitterdan is offline   Reply With Quote
Old 21-04-2015, 12:48   #5
Registered User

Join Date: Aug 2014
Location: Astoria, NY
Boat: Sabre 38
Posts: 566
Re: Question On Connection To Morningstar MPPT

Thanks. Will give it a try then, but will keep my eye open for something involving a crimp.


Sent from my iPhone using Cruisers Sailing Forum
__________________
Stephen

s/v Carpe Ventum
1983 Sabre 38
My Intro
fallingeggs is offline   Reply With Quote
Old 21-04-2015, 14:11   #6
Registered User

Join Date: Jan 2013
Posts: 203
Re: Question On Connection To Morningstar MPPT

Maybe you can crimp on a butt connector and cut it in half.

With 4 gauge wire it may be a tight fit.

I just used the screws and check them every 2 year's. Been fine for 4 years so far.

Sent from my VS840 4G using Cruisers Sailing Forum mobile app
twinboat is offline   Reply With Quote
Old 21-04-2015, 15:28   #7
Registered User
 
transmitterdan's Avatar

Join Date: Oct 2011
Boat: Valiant 42
Posts: 6,008
Re: Question On Connection To Morningstar MPPT

Quote:
Originally Posted by twinboat View Post
Maybe you can crimp on a butt connector and cut it in half.

With 4 gauge wire it may be a tight fit.

I just used the screws and check them every 2 year's. Been fine for 4 years so far.

Sent from my VS840 4G using Cruisers Sailing Forum mobile app
I strongly recommend against doing this. Compression terminals are designed for stranded wire and only stranded wire.
transmitterdan is offline   Reply With Quote
Old 21-04-2015, 18:24   #8
Registered User

Join Date: Dec 2009
Posts: 140
Re: Question On Connection To Morningstar MPPT

Screw terminals are used in commercial electrical installations for considerably higher voltages and amperages even when there is considerable vibration. Many marine components use screw terminals. Morningstar Mppts aren't the only ones.

Torque should be checked from time to time as part of routine maintenance but otherwise screw terminals are a perfectly acceptable way to terminate wires.
ebs001 is offline   Reply With Quote
Old 21-04-2015, 18:39   #9
Registered User
 
Lancerbye's Avatar

Join Date: Mar 2007
Location: Cormorant Island, BC, Canada
Boat: Lancer 44 Motorsailer
Posts: 1,877
Images: 38
Re: Question On Connection To Morningstar MPPT

Quote:
Originally Posted by ebs001 View Post
Screw terminals are used in commercial electrical installations for considerably higher voltages and amperages even when there is considerable vibration. Many marine components use screw terminals. Morningstar Mppts aren't the only ones.

Torque should be checked from time to time as part of routine maintenance but otherwise screw terminals are a perfectly acceptable way to terminate wires.
+1

Also since your controller has 60 amp capability the 10 Ga. wire is a bit on the small size. Should be a 6 Ga. I think without referring to my wire code chart. Either 6 or 4 Ga. My memory is failing, happens at my age.
__________________
The basis of accomplishment is in never quitting
Mengzi Meng-tse
Lancerbye is offline   Reply With Quote
Old 21-04-2015, 18:54   #10
Registered User
 
svfinlandia's Avatar

Join Date: Jul 2012
Location: Boat currently for sale in Oriental, North Carolina
Boat: Nauticat NC36 36'
Posts: 736
Re: Question On Connection To Morningstar MPPT

I solder tinned the ends of my wires and they have been fine for more than four years now. Be sure to add strain relief.

Al, S/V Finlandia
__________________
quo fata ferunt
svfinlandia is offline   Reply With Quote
Old 22-04-2015, 13:09   #11
2kr
Registered User

Join Date: Nov 2014
Location: Panama for now
Boat: IP445
Posts: 35
Re: Question On Connection To Morningstar MPPT

I would not put on the butt connection then cut it in half. The force-displacement of screw to the connector, designed to hold the wire will be wrong. I just mounted an MPPT controller from Blue Sky. I used #6 wire from the panels to the controller and tinned the ends. There is plenty of room for them. By the way, I replaced a cheap controller with the MPPT and the #10 wire that was used by the original installer and went from 13 - 14 amps to 20 amps with 3 130 watt panels. Now I am going to get more panels. I love looking at the amp values on the controller.
2kr is offline   Reply With Quote
Old 22-04-2015, 15:06   #12
Registered User

Join Date: Aug 2014
Location: Aboard, presently in the Indian Ocean
Boat: Trisbal 36
Posts: 86
Re: Question On Connection To Morningstar MPPT

To connect my Morningstar MPPT regulator, I crimped the end of the cables with fork terminals (as in the link below). The terminals are screwed in the regulator's connectors. Has worked fine for years and makes for a nice finish and easy maintenance if necessary as it is easy to connect and disconnect.

http://www.autoconsumables.com/ekmps...low-3412-p.jpg
belle-isle is offline   Reply With Quote
Old 22-04-2015, 18:57   #13
Registered User

Join Date: Apr 2011
Location: Gulf and Caribbean
Boat: Irwin 30
Posts: 270
Send a message via Skype™ to mrlee
Re: Question On Connection To Morningstar MPPT

FWIW I crimped on and then diligently flattened out the male side of a barrel connector in the switch panel I made. Works great with a nice snug fit.
Happy solaring....
mrlee is offline   Reply With Quote
Old 24-04-2015, 02:20   #14
Registered User

Join Date: Jan 2013
Posts: 203
Re: Question On Connection To Morningstar MPPT

I don't see how you guys are getting 6 or 4 gauge wires in them yellow connectors.

I am using 12 gauge on the panel side because I run 36 volt panels in series but the battery side needs to carry 60 amps.

Sent from my VS840 4G using Cruisers Sailing Forum mobile app
twinboat is offline   Reply With Quote
Old 30-04-2015, 04:36   #15
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: Question On Connection To Morningstar MPPT

For what it is worth, the ABYC Electrical Standard does not permit compression connections unless there is a follower plate that actually makes contact with the wire strands. This is to prevent driving the screw through the fine strand wire that is used in Type 3 Boat Cable.

The correct way to make these connections is by using a properly sized ferrule crimped on the cable end. See this link: Insulated Ferrules - Wire Ferrule - UL Approved at Ferrules Direct - Largest Selection in the U.S.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Reply

Tags
mppt


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
LiFeP04 custom charge settings for Morningstar MPPT-60 steelwrk1 Electrical: Batteries, Generators & Solar 10 09-08-2020 03:38
Brunswick Landing or Morningstar Golden Isles? bigbrownpilot Our Community 28 26-04-2015 10:03
8 X 100W Flexible Solar + Morningstar MPPT-60 did I make a mistake autumnbreeze27 Electrical: Batteries, Generators & Solar 14 15-02-2015 14:15
Morningstar Sunsaver Duo daletournier Electrical: Batteries, Generators & Solar 3 31-10-2014 04:05
Pulled the trigger on 4 x 100w flexible panels and a Morningstar TS-MPPT-60 autumnbreeze27 Electrical: Batteries, Generators & Solar 62 13-05-2014 07:35

Advertise Here


All times are GMT -7. The time now is 12:30.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.