i currently have single 30 amp service and so am going to add a second 30 amp receptacle and panel and split the loads.

my question is: can the neutrals from both inputs still be connected together, or should they be isolated from each other?

(the grounds will of course be connected.)

thanks
BluegillBoy is offline   Reply With Quote
Old 26-05-2016, 10:48   #2
Registered User

Join Date: Oct 2009
Location: Boise, ID
Boat: AMF Force 5 -- 14ft long
Posts: 23
Re: question on twin 30 amp shore power service

I would run the neutral legs separately due to you don't know how bad the wiring you are plugging into is. It's very possible some marina guy swapped your hot and neutral leads.

Sent from my SM-G900V using Cruisers Sailing Forum mobile app
jason902 is offline   Reply With Quote
Old 26-05-2016, 14:11   #3
Registered User

Join Date: Feb 2015
Posts: 1,243
Images: 1
Re: question on twin 30 amp shore power service

And if the two 30A circuits are in phase then then current in a common neutral would be additive and might overload wiring that is otherwise expected to be limited to 30A.
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 26-05-2016, 15:32   #4
Moderator Emeritus
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,083
Re: question on twin 30 amp shore power service

Keep them separate doing different jobs. And, while you're at it, invest in an isolation (1:1) transformer for each (Triad Magnetics $95 each). Then, you never need worry about stray voltage in the water or wrong polarity at your equipment. Your boat's AC is completely isolated from the big bad world. Or, at least, purchase a receptacle tester ($5.97 at Home Depot) for each that will tell you if someone has reversed hot and neutral as mentioned in a post above.
tkeithlu is offline   Reply With Quote
Old 26-05-2016, 20:42   #5
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,733
Re: question on twin 30 amp shore power service

separate. as each will be running through it's own double pull breaker as it enters the boat. if you combined them after you can end up with false tripping.

if you are using ELCI's then you'll definably have tripping.
smac999 is offline   Reply With Quote
Old 26-05-2016, 20:54   #6
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,309
Re: question on twin 30 amp shore power service

ABYC requires they be separate. It is potentially lethal to do otherwise.
Don't even consider the Triad isolation transformer, it does not come close to meeting ABYC Standards. Real marine transformers such as the Charles units will cost you 2k each and you can achieve close to the same protection with a couple of $350 failsafe galvanic isolators.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 27-05-2016, 08:42   #7
Retired musician & 50T master
 
Symphony's Avatar

Cruisers Forum Supporter

Join Date: Jul 2011
Location: Ct
Boat: Pisces 21
Posts: 710
Re: Question On Twin 30 Amp Shore Power Service

the Yandina galvanic isolator is around $100 at Defender. Worked for me over the years although it isn't ABYC any more due to lack of a test light.
__________________
"In my experience travelers generally exaggerate the difficulties of the way." - Thoreau
Symphony is offline   Reply With Quote
Old 27-05-2016, 09:51   #8
Registered User

Join Date: Feb 2011
Posts: 2,150
Re: Question On Twin 30 Amp Shore Power Service

You are about to electrocute yourself. Buy life insurance before fussing with your electrical system. The question you poised indicates you need a licensed electrician to do your electrical work . A lot of folks have gone to heaven from bravado in the face of ignorance. Our condolences.
reed1v is offline   Reply With Quote
Old 27-05-2016, 10:12   #9
Registered User
 
artisanmach's Avatar

Join Date: Aug 2013
Location: Anacortes, WA
Boat: Gulfstar 37 Sloop
Posts: 187
Re: Question On Twin 30 Amp Shore Power Service

so, why are you adding a 2nd 30 amp service? unless your adding an AC unit or some large current device.
artisanmach is offline   Reply With Quote
Old 27-05-2016, 10:45   #10
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: question on twin 30 amp shore power service

Quote:
Originally Posted by tkeithlu View Post
Keep them separate doing different jobs. And, while you're at it, invest in an isolation (1:1) transformer for each (Triad Magnetics $95 each). Then, you never need worry about stray voltage in the water or wrong polarity at your equipment. Your boat's AC is completely isolated from the big bad world. Or, at least, purchase a receptacle tester ($5.97 at Home Depot) for each that will tell you if someone has reversed hot and neutral as mentioned in a post above.
$95 for a 3.6kva isolation transformer? Really? Could sell it for scrap copper for more than that.
DotDun is offline   Reply With Quote
Old 27-05-2016, 11:39   #11
Registered User
 
wrwakefield's Avatar

Join Date: Feb 2011
Location: Meandering about the Gulf of Alaska coast [NNE Pacific]— where the internet doesn't always shine... [Even Elon's...] Homeport: Wrangell Island
Boat: Nauticat 43 [S&S Staysail Ketch]
Posts: 1,747
Re: Question On Twin 30 Amp Shore Power Service

Quote:
Originally Posted by BluegillBoy View Post
i currently have single 30 amp service and so am going to add a second 30 amp receptacle and panel and split the loads.

my question is: can the neutrals from both inputs still be connected together, or should they be isolated from each other?

(the grounds will of course be connected.)

thanks

Is there a reason not to upgrade your system to a single 50A service?

You could then use just one shore power cord. [Albeit a larger gauge for 50A]

Our 50A inlet is split into 2- 110VAC feeds at the distribution panel.

This also allows us to use a 30A shore power cord with a 50A boat-side socket on it [with the single 30A hot jumped to the 2nd hot on the 50A plug on the cord] for feeding both sides of the distribution with the 30A service when that is all that is available or needed, or when all we want to schlep is the 'smaller' cord...

If twin 30A services are all that are available, and you need the extra amperage, you can use a 'smart reverse Y' adapter with your 50A cord. [e.g., Marinco RY504-2-30

This is a safe and very flexible set-up, and only requires one shore power.

You can also use the 50A cord to a 30A service with the right adapter. [e.g., Marinco 111A]

In case this is helpful.

Best wishes with your project.

Cheers!

Bill

PS: If you go the 50A route, [or even stay with twin 30A inlets] may I recommend upgrading to the Smart Plug on your boat? [If you haven't already... Here is our blog post explaining why we chose this upgrade...]
__________________
SV Denali Rose
Learning every day- and sharing if I can.
wrwakefield is online now   Reply With Quote
Old 27-05-2016, 12:25   #12
Registered User
 
Blue Stocking's Avatar

Join Date: Dec 2008
Location: St. Georges, Bda
Boat: Rhodes Reliant 41ft
Posts: 4,131
Re: Question On Twin 30 Amp Shore Power Service

10s of thousands of 125/250, 50 amp services use a single neutral, split at the panels for 125 vac. As do just as many generators.
__________________
so many projects--so little time !!
Blue Stocking is offline   Reply With Quote
Old 27-05-2016, 12:46   #13
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,309
Re: Question On Twin 30 Amp Shore Power Service

Quote:
Originally Posted by Blue Stocking View Post
10s of thousands of 125/250, 50 amp services use a single neutral, split at the panels for 125 vac. As do just as many generators.
A generator is a power source, a panel is not. That is the difference.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 27-05-2016, 13:02   #14
Registered User

Join Date: Jul 2015
Posts: 73
Re: Question On Twin 30 Amp Shore Power Service

A simple rule of thumb....whenever possible, isolate!
svinvictus2 is offline   Reply With Quote
Old 27-05-2016, 21:05   #15
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,733
Re: Question On Twin 30 Amp Shore Power Service

Quote:
Originally Posted by wrwakefield View Post
Is there a reason not to upgrade your system to a single 50A service?
it is much easier and cheaper to add a 2nd small 30a panel and plug to the boat, then to redo the whole existing panel to 240v

depends what he is trying to get. and what's available at the marinas he uses.
smac999 is offline   Reply With Quote
Reply

Tags
service, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
For Sale: shore power marino 50 amp to twin 30amp 1265skip Classifieds Archive 2 28-03-2015 09:51
Two 30amp 125v shore power service to 50amp 125v boat input Le Tour Electrical: Batteries, Generators & Solar 40 19-12-2013 17:45
Twin Gas vs Single or Twin Diesel Banjohans Engines and Propulsion Systems 4 04-10-2011 10:50
Center board vs keel vs twin keel vs twin centerboard jscott Monohull Sailboats 32 26-03-2009 14:48

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 09:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.