Old 29-01-2021, 07:03   #1
Registered User

Join Date: Apr 2019
Posts: 614
Reverse Polarity at Panel Only

We just plugged in to (50 amp)shore power in The Bahamas and the reverse polarity light on our panel is bright red. I plugged a tester into all of our AC outlets and they all test okay. I’ve tried a different pedestal and it’s all the same. We are at the end of a finger slip with several very large boats all plugged in.

What could cause this? We were plugged in several places in Florida and it was all okay.
crayiii is offline   Reply With Quote
Old 29-01-2021, 07:30   #2
Registered User

Join Date: Dec 2020
Posts: 750
Re: Reverse Polarity at Panel Only

Quote:
Originally Posted by crayiii View Post
We just plugged in to (50 amp)shore power in The Bahamas and the reverse polarity light on our panel is bright red. I plugged a tester into all of our AC outlets and they all test okay. I’ve tried a different pedestal and it’s all the same. We are at the end of a finger slip with several very large boats all plugged in.

What could cause this? We were plugged in several places in Florida and it was all okay.
Reverse polarity light come one when there is significant voltage difference between the neutral and ground wires. This can be caused by actual reverse polarity, or by a high resistance in the neutral wire, and then lots of power draw on the lines (i.e. several large boats!). You're portable circuit tester is likely to just be less sensitive to this.

If you have a multimeter aboard, test the voltage between the neutral wire and ground. If you see 120V (or close) that is reverse polarity, if you see less than 5 volts, that would be normal. Anything more than 5 volts or so would be a troublesome wiring system in the marina.
BillKny is offline   Reply With Quote
Old 29-01-2021, 07:44   #3
Registered User

Join Date: Apr 2019
Posts: 614
Re: Reverse Polarity at Panel Only

Quote:
Originally Posted by BillKny View Post
Reverse polarity light come one when there is significant voltage difference between the neutral and ground wires. This can be caused by actual reverse polarity, or by a high resistance in the neutral wire, and then lots of power draw on the lines (i.e. several large boats!). You're portable circuit tester is likely to just be less sensitive to this.

If you have a multimeter aboard, test the voltage between the neutral wire and ground. If you see 120V (or close) that is reverse polarity, if you see less than 5 volts, that would be normal. Anything more than 5 volts or so would be a troublesome wiring system in the marina.
There is 1v between neutral and ground at the outlet. With this info, what could cause the panel to have a bright red reverse polarity light?
crayiii is offline   Reply With Quote
Old 29-01-2021, 08:07   #4
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,262
Re: Reverse Polarity at Panel Only

Quote:
Originally Posted by crayiii View Post
There is 1v between neutral and ground at the outlet. With this info, what could cause the panel to have a bright red reverse polarity light?

What are the ohms between neutral and ground
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 29-01-2021, 08:47   #5
Registered User

Join Date: Apr 2019
Posts: 614
Re: Reverse Polarity at Panel Only

[QUOTE=boatpoker;3331231]What are the ohms between neutral and ground[/QUOTE

The dock master came by and tested the outlet and said it was fine and left.

I wanted to test my cable so I unplugged it at both ends and tested continuity between all 4 contacts and got nothing.

I then plugged it into the pedestal but kept the breaker off and tested continuity at the end of my cable. I got continuity between ground and neutral and between hot and neutral.
crayiii is offline   Reply With Quote
Old 29-01-2021, 09:25   #6
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,262
Re: Reverse Polarity at Panel Only

[QUOTE=crayiii;3331311]
Quote:
Originally Posted by boatpoker View Post
What are the ohms between neutral and ground[/QUOTE

The dock master came by and tested the outlet and said it was fine and left.

I wanted to test my cable so I unplugged it at both ends and tested continuity between all 4 contacts and got nothing.

I then plugged it into the pedestal but kept the breaker off and tested continuity at the end of my cable. I got continuity between ground and neutral and between hot and neutral.
There should be no continuity between ground and neutral.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 29-01-2021, 09:27   #7
Registered User

Join Date: Apr 2019
Posts: 614
Re: Reverse Polarity at Panel Only

[QUOTE=boatpoker;3331347]
Quote:
Originally Posted by crayiii View Post

There should be no continuity between ground and neutral (or hot).
Yeah, I packed my cable up and will continue to live off solar and wind and won't worry about hot water.

The pedestal is a bit corroded and like I said there are several boats on this dock plugged into 100amps, one is plugged into two 100 amps and one has some type of box on the dock between the pedestal and the boat. I'll skip AC power for now.
crayiii is offline   Reply With Quote
Old 30-01-2021, 10:25   #8
Registered User

Join Date: Dec 2009
Posts: 140
Re: Reverse Polarity at Panel Only

[QUOTE=boatpoker;3331347]
Quote:
Originally Posted by crayiii View Post

There should be no continuity between ground and neutral.
The neutral is the grounded conductor and there should be continuity when the cable is plugged into the pedestal. There should not be any continuity between the hot and the neutral. Did you try checking the pedestal outlet to see if you were getting continuity between the hot and neutral with the breaker off?

If you have reverse polarity from the pedestal the reverse polarity light should come on on your panel even if the pedestal breaker is turned off. Neutrals are never switched.
ebs001 is offline   Reply With Quote
Old 30-01-2021, 17:49   #9
Registered User

Join Date: Dec 2012
Location: Mannum, Australia
Boat: Houseboat, 60ft.
Posts: 290
Re: Reverse Polarity at Panel Only

""Neutrals are never switched.""
Except in maybe Australia?
BruceS is offline   Reply With Quote
Old 30-01-2021, 19:28   #10
Registered User

Join Date: Dec 2020
Posts: 750
Re: Reverse Polarity at Panel Only

GROUNDS are not switched, but Neutrals most certainly can be!

But in this case, NOT. There is a double pole breaker at the pedistal, which on a 50AMP 120/240 supply shuts off the TWO hots. The neutral and ground SHOULD be connected at the marina power panel, and SHOULD show continuity. If not, you would not have a functioning safety ground.

But this is the case of asking a complex question on the internet. People who do not know the details of the situation are happy to post an answer and with AC power especially that can be dangerous.

Lots of things could be wrong, and giving specific advice without actually knowing all the details is foolish.
BillKny is offline   Reply With Quote
Old 31-01-2021, 03:47   #11
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Reverse Polarity at Panel Only

if you actually had reverse politary on a 240v boat you'd know pretty soon. smoke would be pouring out of half your appliances. as half the panel would now be running 240v instead of 120v. and the other half the 120v stuff would still be 120v but in rev pol... hopefully breakers would blow before stuff caught on fire...

if you feel like plugging back in. with the main breaker off measure the voltage between all 4 wires in every pair combo before the main it should be easy to tell what's going on.

should be:

red to black 240
red to white 120
black to white 120
white to green 0
black to green 120
red to green 120

you can also measure right at the wires for the rev pol light too to see what's going on. it should still have power with the main breaker off.
smac999 is offline   Reply With Quote
Old 31-01-2021, 05:26   #12
Registered User

Join Date: Feb 2015
Location: Jacksonville, Fl
Boat: S2 10.3 & TMC Custom 41 Trawler
Posts: 133
Images: 1
Re: Reverse Polarity at Panel Only

I also suggest you look at the reverse polarity light wiring itself behind your panel. I once had a situation where a little overcurrent wire melting behind the panel cause the reverse polarity light to come on.
NakedCity is offline   Reply With Quote
Old 31-01-2021, 13:00   #13
Registered User

Join Date: Sep 2020
Location: Seabrook, TX
Boat: Catalina 30
Posts: 562
Re: Reverse Polarity at Panel Only

There is also supposed to be a small resistor in line with the lamp to prevent stray voltages from erroneously illuminating it.

My internet search for the resistor size came up with the following blog, which also has some good comments / troubleshooting info:

The Marine Installer's Rant: The reverse polarity light AC leaking musing
sinnerman is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Reverse Polarity?? SV Someday Came Electrical: Batteries, Generators & Solar 30 03-11-2014 06:50
Reverse Polarity nelsonsmoody Electrical: Batteries, Generators & Solar 55 12-10-2014 12:03
Reverse Polarity (AC) GordMay Electrical: Batteries, Generators & Solar 13 30-06-2013 12:12
Reverse Polarity in alternating current Sandero Electrical: Batteries, Generators & Solar 8 06-12-2008 19:01
Reverse Polarity Light alanperry Electrical: Batteries, Generators & Solar 24 06-09-2006 03:13

Advertise Here


All times are GMT -7. The time now is 06:58.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.