Ring terminals for 110v

Have happily used heat shrink adhesive ring terminals (some from Ancor, some direct from TinnedMarineWire.com which actually seem nicer than the Ancors) for some time now on 12v systems with good success.

Need to redo some 110 AC wiring next, just realized none of these ring terminals seem to list an approved voltage range:
https://tinyurl.com/tinnedmarine
https://www.ancorproducts.com/en/p/311303

I assume these are appropriate to use for connecting my new 10ga triplex tinned wire to my new Blue Sea Systems A Series breakers, am I correct in that assumption (or am I making an ass out of me an umption)?

TIA.

-- Bass
__________________
Hailey, Idaho & Bellingham, WA
Sailing blog: https://Sailing.PictureOfNectar.com
basssears is offline   Reply With Quote
Old 24-08-2021, 12:40   #2
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,514
Re: Ring terminals for 110v

I would use them. note that the EU DoC does not list the low voltage directive, only RoHS. So, for euro, there is no voltage hazard. I might agree, "insulated" crimps don't mean they are touchable to a IP20 rating, for instance. ie; lots of exposed HV there...and insulation/safety is to be applied by other means (box, panel, etc)
team karst is offline   Reply With Quote
Old 24-08-2021, 12:46   #3
Registered User

Join Date: Sep 2015
Location: Hailey, ID
Boat: Gulf 32
Posts: 712
Re: Ring terminals for 110v

Just for reference or others who check this post, I did get reply to my question from TinnedMarineWire:

"Good up to 600 volts, so you are good."

-- Bass
__________________
Hailey, Idaho & Bellingham, WA
Sailing blog: https://Sailing.PictureOfNectar.com
basssears is offline   Reply With Quote
Old 24-08-2021, 12:47   #4
Registered User

Join Date: Sep 2015
Location: Hailey, ID
Boat: Gulf 32
Posts: 712
Re: Ring terminals for 110v

Quote:
Originally Posted by team karst View Post
I would use them. note that the EU DoC does not list the low voltage directive, only RoHS. So, for euro, there is no voltage hazard. I might agree, "insulated" crimps don't mean they are touchable to a IP20 rating, for instance. ie; lots of exposed HV there...

Are you referring to whether a ring terminal is still a high voltage shock hazard? My plan (doesn't exist in current 1988 setup) is to have a cover over the whole back of the A/C side of the panel to prevent shock hazard, so I'm not too worried about each actual wire's shock potential.
__________________
Hailey, Idaho & Bellingham, WA
Sailing blog: https://Sailing.PictureOfNectar.com
basssears is offline   Reply With Quote
Old 24-08-2021, 12:54   #5
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,514
Re: Ring terminals for 110v

Quote:
Originally Posted by basssears View Post
Just for reference or others who check this post, I did get reply to my question from TinnedMarineWire:

"Good up to 600 volts, so you are good."

-- Bass
I think that means they will accommodate 600Volt insulated wire, in the sizes called out. Not convinced it has anything to do with shock hazard. Half the terminal is exposed.
team karst is offline   Reply With Quote
Old 24-08-2021, 12:58   #6
Registered User

Join Date: May 2011
Location: Lake Ont
Posts: 8,561
Re: Ring terminals for 110v

Quote:
Originally Posted by basssears View Post
Have happily used heat shrink adhesive ring terminals (some from Ancor, some direct from TinnedMarineWire.com which actually seem nicer than the Ancors) for some time now on 12v systems with good success.

Need to redo some 110 AC wiring next, just realized none of these ring terminals seem to list an approved voltage range:
https://tinyurl.com/tinnedmarine
https://www.ancorproducts.com/en/p/311303

I assume these are appropriate to use for connecting my new 10ga triplex tinned wire to my new Blue Sea Systems A Series breakers, am I correct in that assumption (or am I making an ass out of me an umption)?
The connectors you linked to are the "blue" range which is for wire gauge 16 to 14, to fit a #10 screw. Confusing, isn't it? You need to get ring terminals for 10 gauge wire, with a ring hole sized for the breaker's screws.

In this application, you don't need to worry about voltage rating. Current rating is more important, but I'm going to go out on a limb here and say that any terminal meant to crimp onto a 10 AWG wire is probably rated to handle that current.
Lake-Effect is online now   Reply With Quote
Old 24-08-2021, 13:04   #7
Registered User
 
Dsanduril's Avatar

Join Date: Aug 2011
Location: Petersburg, AK
Boat: Outremer 50S
Posts: 4,229
Re: Ring terminals for 110v

The tech specs for the linked Ancor product show that they are listed to UL 486C.

486C has two insulation ratings, 300V and 600V. Since the tech specs don't specify, I'd assume that they meet only the 300V requirements. The voltage ratings show up in several places in the standard, but this pretty much covers it (i.e., there is no option for an insulated connector < 300V).

Quote:
6.3.6 Insulation employed as part of a connector shall be suitable for the tested voltage rating of the connector in accordance with Table 2 [Table 2 has entries for 300V and 600V (1000V in signs and luminaires)]...

10.5 e) for an insulated connector, the marked voltage rating shall be "300 volts maximum", "600 volts maximum, or "600 volts maximum building wire; 1000 volts maximum, signs or luminaires". The marking may be on the unit container or on an information sheet packed in the unit container;
[edit] I see you got 600V back while I was typing[/edit]
Dsanduril is offline   Reply With Quote
Old 24-08-2021, 13:48   #8
Registered User
 
rwidman's Avatar

Join Date: Feb 2008
Location: North Charleston, SC
Boat: Camano Troll
Posts: 5,176
Re: Ring terminals for 110v

Those terminals are fine but be sure to get the ones rated for the gauge of wire that you are using and the size of the screw that the terminals will be attached to.
__________________
Ron
HIGH COTTON
rwidman is offline   Reply With Quote
Old 24-08-2021, 14:23   #9
Registered User

Join Date: Sep 2015
Location: Hailey, ID
Boat: Gulf 32
Posts: 712
Re: Ring terminals for 110v

Quote:
Originally Posted by rwidman View Post
Those terminals are fine but be sure to get the ones rated for the gauge of wire that you are using and the size of the screw that the terminals will be attached to.

Thanks all, yes I know the ring terminal size I need (based on what the Blue Sea breaker accepts which is #6) they're the yellow 12-10 AWG sized, all I needed to confirm was I could run 110v through them.
__________________
Hailey, Idaho & Bellingham, WA
Sailing blog: https://Sailing.PictureOfNectar.com
basssears is offline   Reply With Quote
Old 24-08-2021, 22:32   #10
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Ring terminals for 110v

the standard blue sea breakers are #10 screw. the bigger ones with studs will be 1/4". #6 is a tiny screw.
smac999 is offline   Reply With Quote
Old 25-08-2021, 02:56   #11
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 49,831
Images: 241
Re: Ring terminals for 110v

Quote:
Originally Posted by smac999 View Post
the standard blue sea breakers are #10 screw. the bigger ones with studs will be 1/4". #6 is a tiny screw.
Blue Seas Circuit Breakers don’t have a “standard” screw/stud terminal size, [although many are #10/32].
Look up your specific breaker, for details.
https://www.bluesea.com/products/cat...rcuit_Breakers
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 25-08-2021, 05:54   #12
Registered User

Join Date: Sep 2015
Location: Hailey, ID
Boat: Gulf 32
Posts: 712
Re: Ring terminals for 110v

Quote:
Originally Posted by smac999 View Post
the standard blue sea breakers are #10 screw. the bigger ones with studs will be 1/4". #6 is a tiny screw.

Oh, so what, now I have to be able to read??


Just glanced at the specs when I wrote that last post, mounting screws to mount breakers to panel are #6, mounting studs are #10. Doh.
__________________
Hailey, Idaho & Bellingham, WA
Sailing blog: https://Sailing.PictureOfNectar.com
basssears is offline   Reply With Quote
Old 24-10-2021, 20:14   #13
Registered User

Join Date: Oct 2010
Location: Boise, Idaho and Port Ludlow, WA
Boat: Yamaha 33
Posts: 223
Re: Ring terminals for 110v

Consider using captive spade terminals instead of ring terminals so you don't drop the tiny little screws down in the bilge.

ABYC allows their use: 11.14.3.4 Terminal connectors shall be the ring or captive spade types.
MerMike is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
Ring Terminals on 120vac Outlets (vs ... hook terminals ) Navi2016 Electrical: Batteries, Generators & Solar 5 26-11-2018 17:54
Blue Wave Swageless Rigging Terminals tomj Deck hardware: Rigging, Sails & Hoisting 28 27-09-2016 12:58
A/C receptacles for use with ring terminals? Rusty123 Electrical: Batteries, Generators & Solar 11 25-11-2013 07:04
3/4" ID Ring Terminals rognvald Electrical: Batteries, Generators & Solar 4 24-06-2013 07:48

Advertise Here


All times are GMT -7. The time now is 19:31.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.