Old 09-10-2019, 03:08   #1
Registered User

Join Date: Aug 2017
Location: Yarmouth, ME
Boat: Amel 50
Posts: 336
Shore power cord set for Europe

A 50 ft, 30 amp Marinco cord set for N. America (110V / 60 Hz) costs under $100.

A 50 ft, 30 amp set for Europe (230V / 50 Hz) costs over $400!

From what I can tell, the only differences are the shoreside EU plug and a slightly different wire gauge: 10 AWG vs. 4 mm2.

Is there any downside of using a N. America cord set, and a replacement EU shoreside plug, which costs around $25?

I should mention that it’s for a European boat with 230V / 50 Hz devices (battery charger, water heater and outlets).
__________________
USCG master
Certified sailing instructor
Howler is offline   Reply With Quote
Old 09-10-2019, 03:14   #2
Registered User
 
admiralslater's Avatar

Join Date: Sep 2014
Location: Toronto summer rest somewhere else
Boat: Outremer 45/pdq36
Posts: 1,170
Re: Shore power cord set for Europe

If you have 30 amp us look for 16 amp European that might help . As the wire is a larger gauge in us I don’t see why you should not be able to put new ends on it .
__________________
“Growing older but not up”
admiralslater is offline   Reply With Quote
Old 09-10-2019, 13:11   #3
Registered User

Join Date: Nov 2016
Location: South-West Sweden
Boat: Maxi 999
Posts: 53
Re: Shore power cord set for Europe

Indeed, a typical 1-phase shore power cord over here is 2.5mm2, rated at 16A continous.
I've never, ever seen a 30A 1-phase outlet in a marina, finding one would be like finding a unicorn.

Outlets are typically 1-phase from 6 up to 16A (230V), or 3-phase 16 or 32A (230/400V).

A typical 25m (80ft) 1-phase shore power cord is about $50 to $100 at any chandler's, depending on make and plug model.
ottow is offline   Reply With Quote
Old 09-10-2019, 15:45   #4
Registered User

Join Date: Aug 2017
Location: Yarmouth, ME
Boat: Amel 50
Posts: 336
Re: Shore power cord set for Europe

Quote:
Originally Posted by ottow View Post
Indeed, a typical 1-phase shore power cord over here is 2.5mm2, rated at 16A continous.
I've never, ever seen a 30A 1-phase outlet in a marina, finding one would be like finding a unicorn.

Outlets are typically 1-phase from 6 up to 16A (230V), or 3-phase 16 or 32A (230/400V).

A typical 25m (80ft) 1-phase shore power cord is about $50 to $100 at any chandler's, depending on make and plug model.
Here’s what I’m trying to solve. When I ran a small space heater with a typical EU 16A 2.5mm cable on my last boat, it would intermittently trip the breaker at the shore outlet. I can’t explain it electrically, but when I replaced the cable with a thicker one, such as a 30A cable,, that problem subsided. I’m back to a typical 16A cable and the problem is occurring again. So I thought I’d try a higher gauge cable again. Does this make any sense?
Howler is offline   Reply With Quote
Old 09-10-2019, 16:06   #5
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,267
Re: Shore power cord set for Europe

Absolutely makes sense.
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 09-10-2019, 21:37   #6
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Shore power cord set for Europe

Quote:
Originally Posted by boatpoker View Post
Absolutely makes sense.

no it doesn't...
smac999 is offline   Reply With Quote
Old 10-10-2019, 08:14   #7
Registered User

Join Date: Dec 2009
Location: Cruising, now in USVIs
Boat: Taswell 43
Posts: 1,045
Re: Shore power cord set for Europe

When we cruised the Medd (and Asia before that) the shorepower poles were either 16amp or 32amp; they used a different plug for each, just like a 30 amp vs a 50amp plug here in the US. But since you're carrying only 16 amps, you only need a cordset (wire) capable of 16amps. We used a standard extension cord with the special end for the power pole.....it worked fine, and is a lot less bulky. Our boat, too, is built for Asia/Europe, and wired for 230v, 50Hz, 3-wire power. The only issue we've had was when we sailed here to the Caribbean!
sailcrazy is offline   Reply With Quote
Old 10-10-2019, 09:04   #8
Registered User
 
Nicholson58's Avatar

Cruisers Forum Supporter

Join Date: Jan 2011
Location: Caribbean live aboard
Boat: Camper & Nicholson58 Ketch - ROXY Traverse City, Michigan No.668283
Posts: 6,480
Images: 84
Re: Shore power cord set for Europe

Quote:
Originally Posted by Howler View Post
Here’s what I’m trying to solve. When I ran a small space heater with a typical EU 16A 2.5mm cable on my last boat, it would intermittently trip the breaker at the shore outlet. I can’t explain it electrically, but when I replaced the cable with a thicker one, such as a 30A cable,, that problem subsided. I’m back to a typical 16A cable and the problem is occurring again. So I thought I’d try a higher gauge cable again. Does this make any sense?
Makes total sense. The heating element cannot get as hot due to voltage drop in the small cord. Heating elements resistance increases as they get hot. Running cooler they have less resistance and draw higher amps. Normally the inrush high current drops as the element gets hot. High induction loads also draw more current if they are under design voltage. Different reason, same results. An oversized cord never hurts and will reduce fire risk.

Our European ready boat has an isolation transformer. This converts all single phase 230-250 to two isolated 115 single phase for the boat. All AC devices we have are tolerant of 50-60 Hz.
Nicholson58 is offline   Reply With Quote
Old 10-10-2019, 09:12   #9
Registered User

Join Date: Aug 2017
Location: Yarmouth, ME
Boat: Amel 50
Posts: 336
Re: Shore power cord set for Europe

Quote:
Originally Posted by Nicholson58 View Post
Makes total sense. The heating element cannot get as hot due to voltage drop in the small cord. Heating elements resistance increases as they get hot. Running cooler they have less resistance and draw higher amps. Normally the inrush high current drops as the element gets hot. High induction loads also draw more current if they are under design voltage. Different reason, same results. An oversized cord never hurts and will reduce fire risk.

Our European ready boat has an isolation transformer. This converts all single phase 230-250 to two isolated 115 single phase for the boat. All AC devices we have are tolerant of 50-60 Hz.
I think you nailed it on the head. Thanks.
__________________
USCG master
Certified sailing instructor
Howler is offline   Reply With Quote
Old 10-10-2019, 09:14   #10
Registered User

Join Date: Aug 2017
Location: Yarmouth, ME
Boat: Amel 50
Posts: 336
Re: Shore power cord set for Europe

Quote:
Originally Posted by Nicholson58 View Post
Makes total sense. The heating element cannot get as hot due to voltage drop in the small cord. Heating elements resistance increases as they get hot. Running cooler they have less resistance and draw higher amps. Normally the inrush high current drops as the element gets hot. High induction loads also draw more current if they are under design voltage. Different reason, same results. An oversized cord never hurts and will reduce fire risk.

Our European ready boat has an isolation transformer. This converts all single phase 230-250 to two isolated 115 single phase for the boat. All AC devices we have are tolerant of 50-60 Hz.
... And I recall the cable getting warm when this phenomenon occurred, which supports your point about a voltage drop in the small cord.
__________________
USCG master
Certified sailing instructor
Howler is offline   Reply With Quote
Old 10-10-2019, 10:58   #11
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Shore power cord set for Europe

Quote:
Originally Posted by Howler View Post
Here’s what I’m trying to solve. When I ran a small space heater with a typical EU 16A 2.5mm cable on my last boat, it would intermittently trip the breaker at the shore outlet. I can’t explain it electrically, but when I replaced the cable with a thicker one, such as a 30A cable,, that problem subsided. I’m back to a typical 16A cable and the problem is occurring again. So I thought I’d try a higher gauge cable again. Does this make any sense?
I think your experiencing line lose. Google rated amperage for wire gauge and length. I'm an advocate of the larger the gauge the better.
Cadence is offline   Reply With Quote
Old 10-10-2019, 11:44   #12
Registered User

Join Date: Apr 2018
Location: Scotland
Boat: 42ft Moody Ketch
Posts: 643
Re: Shore power cord set for Europe

Quote:
Originally Posted by smac999 View Post
no it doesn't...
Agreed it is not the cable it is a fault with your space heater you say it is small therefore it should never draw 16amps and if you need 30 amps then the heater can go bang 16amp 1 phase is common in all campsites and marinas in the UK and I can run a fan heater water heater battery charger electronics all at once no trips or it it's a fault at the marina side 30amps is over kill unless your pulling some serious power
tarian is offline   Reply With Quote
Old 10-10-2019, 16:08   #13
Registered User
 
SV Bacchus's Avatar

Join Date: Apr 2016
Location: Back on dirt in Florida
Boat: Currently in between
Posts: 1,338
Re: Shore power cord set for Europe

Quote:
Originally Posted by Cadence View Post
I think your experiencing line lose. Google rated amperage for wire gauge and length. I'm an advocate of the larger the gauge the better.
Me too..
SV Bacchus is offline   Reply With Quote
Old 12-10-2019, 13:34   #14
Registered User
 
Auspicious's Avatar

Join Date: Jun 2003
Location: Chesapeake Bay
Boat: HR 40
Posts: 3,651
Send a message via Skype™ to Auspicious
Re: Shore power cord set for Europe

Quote:
Originally Posted by Nicholson58 View Post
Makes total sense. The heating element cannot get as hot due to voltage drop in the small cord. Heating elements resistance increases as they get hot. Running cooler they have less resistance and draw higher amps. Normally the inrush high current drops as the element gets hot. High induction loads also draw more current if they are under design voltage. Different reason, same results. An oversized cord never hurts and will reduce fire risk.

There is something wrong here. I-squared-R is power loss (i.e. heat) in a conductor. That's why 220V 16A cords are smaller than 117V 30A cords.



"Running cooler they have less resistance and draw higher amps" makes no sense at all.



Bigger conductors are not bad per se but not necessary for 220V 16A.



If you had a voltage drop of substance different between 220V and 117V there was something else wrong. Longer docks, poorly installed end connectors ... something. An IR thermometer and a voltmeter should have nailed that down pretty fast.
__________________
sail fast and eat well, dave
AuspiciousWorks
Beware cut and paste sailors
Auspicious is offline   Reply With Quote
Old 12-10-2019, 13:50   #15
Registered User

Join Date: Jan 2015
Posts: 123
Re: Shore power cord set for Europe

Quote:
Originally Posted by Howler View Post
I think you nailed it on the head. Thanks.
In principle correct but a bit oversimplified, it doesn't work quite like that or you could just drop the voltage to make the kettle boil quicker, say use a 230v kettle in the US on 110v think how good that would be......

Your main problem with the larger cable will be safely terminating it in a 16a plug, some makes of plug will take it most dont. The idea of just stripping the outer sheath off and leaving the insulated cores showing isnt very safe but is quite common with imported motor boats imported from the US.
paul2884 is offline   Reply With Quote
Reply

Tags
Europe, rope, shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Only one power cord is getting power from my shore power. Privilege Electrical: Batteries, Generators & Solar 10 11-09-2019 08:35
For Sale: Shore Power Cord 30 Amps 50ft w/Cord Pro XL velero Classifieds Archive 0 07-07-2014 10:56
Shore Power Cord vs. RV Cord Blc7 Electrical: Batteries, Generators & Solar 5 04-11-2013 11:05
Shore Power Cord adaptor over40pirate Classifieds Archive 0 24-03-2009 08:21
Shore Power Cord Adaptor over40pirate Classifieds Archive 1 12-03-2009 07:29

Advertise Here


All times are GMT -7. The time now is 15:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.