Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 15-11-2020, 13:21   #1
Senior Cruiser
 
Madehn's Avatar

Cruisers Forum Supporter

Join Date: Nov 2014
Location: Kemah Tx
Boat: Gulfstar 51
Posts: 660
Shore Power Switch - Which is Correct?

I am in the process of adding a subpanel on my AC shorepower circuits and upgrading the old 30 amp input to 50 amps- this subpanel will handle the non inverter loads- (putting in an inverter / charger and 10kw genset at the same time). So i am almost completed but in wiring up my new shorepower switch i have come up with a question. My old shorepower selector switch has both neutral and hot wires run thru it- one set for ship and one for shore selection. The wiring diagram that came with my new 4 position switch (off/gen/Inv/shore ) has only the hot wire running through the switch. i have mapped the switch and it appears feasible to do the switch either way IE switching both neutral and Hot or just switching the hot. What is the consensus. For some reason i kind of lean toward switching both but i am not sure why.
Madehn is offline   Reply With Quote
Old 15-11-2020, 13:44   #2
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Shore Power Switch - Which is Correct?

I would always switch both lines. you can never be sure polarities don’t get reversed etc.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 15-11-2020, 15:35   #3
Moderator Emeritus
 
tkeithlu's Avatar

Cruisers Forum Supporter

Join Date: Feb 2012
Location: Carrabelle, Florida
Boat: Fiberglas shattering 44' steel trawler
Posts: 6,083
Re: Shore Power Switch - Which is Correct?

While you are at it run the shore power through a 1:1 transformer. They are not expensive, and will completely isolate shore power from your boat. This is where I got mine. It's been humming away for ten years.

https://www.newark.com/w/c/transform...%20transformer
__________________
Never let anything mechanical know that you are in a hurry.
tkeithlu is offline   Reply With Quote
Old 15-11-2020, 16:12   #4
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,712
Re: Shore Power Switch - Which is Correct?

is the boat now 240v? then you need to switch 3 wires. L1, L2, and neutral.

you must swtich the neutral. because the gen will have the neutreal to ground bonded insdie it. (or should be when you wire it) so if the gen neutreal is not switched. you end up with a perminate n-g bond on the boat which is bad.
smac999 is offline   Reply With Quote
Old 16-11-2020, 08:20   #5
Senior Cruiser
 
Madehn's Avatar

Cruisers Forum Supporter

Join Date: Nov 2014
Location: Kemah Tx
Boat: Gulfstar 51
Posts: 660
Re: Shore Power Switch - Which is Correct?

the boat is not 240v now. -- in looking at the transformers listed it looks like it will be close to $1000 for one big enough to handle the 50 amp service?
Madehn is offline   Reply With Quote
Old 16-11-2020, 10:13   #6
Registered User
 
CarinaPDX's Avatar

Join Date: Jan 2010
Location: Portland, Oregon, USA
Boat: 31' Cape George Cutter
Posts: 3,305
Re: Shore Power Switch - Which is Correct?

That sounds about right. Consider buying a multi-tap transformer that will allow you to connect to either 120VAC or 230VAC shore power with either moving some wires or a switch. It costs a bit more than a 1:1 transformer but is a great convenience when cruising.

Greg
CarinaPDX is offline   Reply With Quote
Old 16-11-2020, 11:00   #7
Registered User
 
Cadence's Avatar

Join Date: Dec 2008
Location: SC
Boat: None,build the one shown of glass, had many from 6' to 48'.
Posts: 10,208
Re: Shore Power Switch - Which is Correct?

Quote:
Originally Posted by CarinaPDX View Post
That sounds about right. Consider buying a multi-tap transformer that will allow you to connect to either 120VAC or 230VAC shore power with either moving some wires or a switch. It costs a bit more than a 1:1 transformer but is a great convenience when cruising.

Greg
Center tap/ buck boost.
Cadence is offline   Reply With Quote
Old 16-11-2020, 14:51   #8
Registered User
 
Flatswing's Avatar

Join Date: Jan 2020
Location: Hilton Head, SC, USA
Boat: DeFever Raised Pilot House 49
Posts: 236
Re: Shore Power Switch - Which is Correct?

you must swtich the neutral. because the gen will have the neutreal to ground bonded insdie it. (or should be when you wire it) so if the gen neutreal is not switched. you end up with a perminate n-g bond on the boat which is bad.[/QUOTE]

I believe that The basic rule is: the neutrals return to ground at the original source. Therefore you need to switch the neutrals also with your selector switch so the neutral returns to shore on shore power, returns to the generator on generator power. In addition, you need to ensure that the neutrals for the inverter circuits return to the inverter and are not commingled with the other neutrals. Otherwise you will be tripping the shore ELCI at any marina that has recently upgraded it’s shore power supply since the new refs have them trip at (I believe) 30 mA.

You may not need a “inverter” position on your source selector if you have an inverter charger, it will “pass through” to the inverter circuits whenever it sees shore power and should automatically switch the neutrals to shore power at the same time.
__________________
Jeremy
Flatswing is offline   Reply With Quote
Old 17-11-2020, 03:37   #9
Registered User

Join Date: Oct 2013
Posts: 272
Re: Shore Power Switch - Which is Correct?

Quote:
Originally Posted by goboatingnow View Post
I would always switch both lines. you can never be sure polarities don’t get reversed etc.
which I've found to be the case in about 40% of cases in the Med - Spanish and Frenche were consisitent, Italy diverse and N Africa dangerous.
Greece, Croatia and Turkey invariably correct.
chasfgr is offline   Reply With Quote
Old 17-11-2020, 06:00   #10
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: Shore Power Switch - Which is Correct?

To be compliant, and safe, L1, L2 and N must be switched for the reasons given upthread.

Regarding isolation transformers: To be compliant, they must have an electrostatic shield that is connected to shore safety ground between the primary and secondary windings.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 18-11-2020, 19:00   #11
Registered User

Join Date: Aug 2007
Location: Adelaide, South Australia, sailing in the Med.
Boat: Beneteau, Oceanis 50 G5
Posts: 1,295
Re: Shore Power Switch - Which is Correct?

Quote:
Originally Posted by Madehn View Post
I am in the process of adding a subpanel on my AC shorepower circuits and upgrading the old 30 amp input to 50 amps- this subpanel will handle the non inverter loads- (putting in an inverter / charger and 10kw genset at the same time). So i am almost completed but in wiring up my new shorepower switch i have come up with a question. My old shorepower selector switch has both neutral and hot wires run thru it- one set for ship and one for shore selection. The wiring diagram that came with my new 4 position switch (off/gen/Inv/shore ) has only the hot wire running through the switch. i have mapped the switch and it appears feasible to do the switch either way IE switching both neutral and Hot or just switching the hot. What is the consensus. For some reason i kind of lean toward switching both but i am not sure why.
Definitely both Active and Neutral - next best thing to pulling the plug, and ensures you are not caught out with a shore reversal.

You may also want to consider a galvanic isolator in the earth circuit. I went for one of these with remote monitoring. Well priced, well made and they will post to you.

https://www.safeshoremarine.com/asse.../details/6.pdf
__________________
'53 was a good year!
Thankful for the wonders of this world - and the waters that cover much of it.
David B is offline   Reply With Quote
Reply

Tags
shore power


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Only one power cord is getting power from my shore power. Privilege Electrical: Batteries, Generators & Solar 10 11-09-2019 08:35
Which tach is correct? nichollsjr Engines and Propulsion Systems 11 13-06-2018 19:10
VHF Splitter - power from which switch? terah Marine Electronics 7 11-07-2015 11:24
Battery switch with shore power breaker keelsidedown Electrical: Batteries, Generators & Solar 17 10-05-2015 20:46
Correct Connection for 4-Way Battery Switch anglooff Electrical: Batteries, Generators & Solar 4 11-06-2010 08:55

Advertise Here