Re: Size of DC ground wire question

If there is one "series cable" then it"s 400A, if there are 3 "series cables" then it's 133A. Is it called respectively 3P/2S and 2P/3S ? I always forget that part ...
rom is offline   Reply With Quote
Old 09-11-2019, 09:10   #32
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,345
Re: Size of DC ground wire question

I know the OP thinks he has all the answers but here’s what he -should- do:

- confirm if your alternator has a DC negative cable and if it has, wire it to the same bolt on the block that gets the 4/0 negative cable. The cables on the alternator should be rated for the alternator output, not for any other cable size in use. Example: my 225A alternators have 4/0 cable, smaller alternators should get smaller cables (their contacts are designed for smaller terminals).

- there should not be any extra DC negative cables attached to the block.

- the positive and negative cables that run to the engine block should be sized for the biggest load which normally is the starter motor, not the alternator. The engine owners manual will recommend proper cable size. I can’t believe 4/0 is required.

- off-topic but before investing in LiFePO4 batteries, I recommend to invest in a proper inverter/charger
s/v Jedi is offline   Reply With Quote
Old 09-11-2019, 18:50   #33
Registered User

Join Date: Mar 2007
Location: San Francisco
Boat: Tayana 52, AC
Posts: 135
Images: 5
Re: Size of DC ground wire question

Quote:
Originally Posted by s/v Jedi View Post
I know the OP thinks he has all the answers but here’s what he -should- do:

- confirm if your alternator has a DC negative cable and if it has, wire it to the same bolt on the block that gets the 4/0 negative cable. The cables on the alternator should be rated for the alternator output, not for any other cable size in use. Example: my 225A alternators have 4/0 cable, smaller alternators should get smaller cables (their contacts are designed for smaller terminals).

- there should not be any extra DC negative cables attached to the block.

- the positive and negative cables that run to the engine block should be sized for the biggest load which normally is the starter motor, not the alternator. The engine owners manual will recommend proper cable size. I can’t believe 4/0 is required.

- off-topic but before investing in LiFePO4 batteries, I recommend to invest in a proper inverter/charger
No where close to having "all" the answers. Slowly and carefully picking the ripe berries found among all the thorns.

Planning to upgrade to an approx 200A alternator (not sure which one yet) but I want my DC neg alt cable to run to the DC negative bus, which will go to my shunt then terminate at the house negative post. I'll think more about your suggestion; perhaps it would work better than my current plan. I'll look again.

Not sure about your last recommendation. I've already invested in LiFePO4 batteries and the Xantrex (though it would not have been my pick) was installed by the previous owner and has worked great. Specs and functionality are ideal for me and I was quite surprised to find the advanced custom charge settings are excellent. No reason I can see to swap it out at this point.
gscriba is offline   Reply With Quote
Old 09-11-2019, 19:17   #34
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,345
Re: Size of DC ground wire question

Quote:
Originally Posted by gscriba View Post
No where close to having "all" the answers. Slowly and carefully picking the ripe berries found among all the thorns.

Planning to upgrade to an approx 200A alternator (not sure which one yet) but I want my DC neg alt cable to run to the DC negative bus, which will go to my shunt then terminate at the house negative post. I'll think more about your suggestion; perhaps it would work better than my current plan. I'll look again.

Not sure about your last recommendation. I've already invested in LiFePO4 batteries and the Xantrex (though it would not have been my pick) was installed by the previous owner and has worked great. Specs and functionality are ideal for me and I was quite surprised to find the advanced custom charge settings are excellent. No reason I can see to swap it out at this point.
Yes for a 200A alternator I would install 4/0 as well. Just use the schematic from the installation guide, which will show one DC negative cable from engine to busbar and one DC positive cable as well. Do not add more cabling. If your boat has a bonding system, then any bonding wires connected to the engine, should be connected at the same bolt that the DC negative is connected to. Do not create a bonding system when there isn’t one now.
If you divert from the manufacturer schematic, you run the risk of creating ground loops and currents through secondary wires, or at least a sub-optimal, higher resistance setup.

On your inverter/charger: keep fingers crossed but do know that Xantrex units have damaged batteries in the past. Most break down pretty quick before they harm the batteries (can’t deal with the high charge rates of LFP). It has cost me $4k to learn that lesson in the past but you may have a newer redesigned model that is better, I haven’t kept up with the brand but never heard of good changes yet...
s/v Jedi is offline   Reply With Quote
Old 09-11-2019, 19:42   #35
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: Size of DC ground wire question

What specific Xantrex device do you have?
john61ct is offline   Reply With Quote
Old 09-11-2019, 19:43   #36
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,128
Re: Size of DC ground wire question

FWIW, I think s/v Jedi's posts (below) are on the money and are a good starting point for any re-design of the DC negative wiring. However I can't speak to the merits or otherwise of the Xantrex units.


Quote:
Originally Posted by s/v Jedi View Post
I know the OP thinks he has all the answers but here’s what he -should- do:

- confirm if your alternator has a DC negative cable and if it has, wire it to the same bolt on the block that gets the 4/0 negative cable. The cables on the alternator should be rated for the alternator output, not for any other cable size in use. Example: my 225A alternators have 4/0 cable, smaller alternators should get smaller cables (their contacts are designed for smaller terminals).

- there should not be any extra DC negative cables attached to the block.

- the positive and negative cables that run to the engine block should be sized for the biggest load which normally is the starter motor, not the alternator. The engine owners manual will recommend proper cable size. I can’t believe 4/0 is required.

- off-topic but before investing in LiFePO4 batteries, I recommend to invest in a proper inverter/charger
Quote:
Originally Posted by s/v Jedi View Post
Yes for a 200A alternator I would install 4/0 as well. Just use the schematic from the installation guide, which will show one DC negative cable from engine to busbar and one DC positive cable as well. Do not add more cabling. If your boat has a bonding system, then any bonding wires connected to the engine, should be connected at the same bolt that the DC negative is connected to. Do not create a bonding system when there isn’t one now.
If you divert from the manufacturer schematic, you run the risk of creating ground loops and currents through secondary wires, or at least a sub-optimal, higher resistance setup.

On your inverter/charger: keep fingers crossed but do know that Xantrex units have damaged batteries in the past. Most break down pretty quick before they harm the batteries (can’t deal with the high charge rates of LFP). It has cost me $4k to learn that lesson in the past but you may have a newer redesigned model that is better, I haven’t kept up with the brand but never heard of good changes yet...
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 09-11-2019, 19:45   #37
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,128
Re: Size of DC ground wire question

Quote:
Originally Posted by john61ct View Post
What specific Xantrex device do you have?
Xantrex SW3012 (ref post #4).
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 09-11-2019, 20:10   #38
Registered User

Join Date: Mar 2007
Location: San Francisco
Boat: Tayana 52, AC
Posts: 135
Images: 5
Re: Size of DC ground wire question

Noted re: Xantrex. I'll dig deeper.
Thanks again.
gscriba is offline   Reply With Quote
Old 09-11-2019, 20:40   #39
rom
Registered User

Join Date: Mar 2016
Boat: Lagoon 440
Posts: 736
Re: Size of DC ground wire question

Quote:
Originally Posted by s/v Jedi View Post
Yes for a 200A alternator I would install 4/0 as well.
Don't you care for the round trip distance from the alternator to the battery ? A 50mm² cable is good enough to carry 200A in a engine room. For a 10 meter round trip and 200A alt I went with 70mm²; that's about 4% voltage drop or 100W of power dissipated in the cable at max output. Good enough for that kind of application. Bigger cables are such a PITA.
rom is offline   Reply With Quote
Old 09-11-2019, 21:13   #40
rbk
Registered User
 
rbk's Avatar

Join Date: Feb 2016
Location: Canada
Boat: T37
Posts: 2,337
Re: Size of DC ground wire question

Quote:
Originally Posted by rom View Post
Don't you care for the round trip distance from the alternator to the battery ? A 50mm² cable is good enough to carry 200A in a engine room. For a 10 meter round trip and 200A alt I went with 70mm²; that's about 4% voltage drop or 100W of power dissipated in the cable at max output. Good enough for that kind of application. Bigger cables are such a PITA.
X2 ^^ size it appropriately.
rbk is offline   Reply With Quote
Old 10-11-2019, 03:25   #41
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Size of DC ground wire question

Quote:
Originally Posted by rom View Post
Don't you care for the round trip distance from the alternator to the battery ? A 50mm² cable is good enough to carry 200A in a engine room. For a 10 meter round trip and 200A alt I went with 70mm²; that's about 4% voltage drop or 100W of power dissipated in the cable at max output. Good enough for that kind of application. Bigger cables are such a PITA.
Are you basing this on a 12v system or 24v system for Start and House?
Pelagic is offline   Reply With Quote
Old 10-11-2019, 05:05   #42
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,345
Re: Size of DC ground wire question

Quote:
Originally Posted by rom View Post
Don't you care for the round trip distance from the alternator to the battery ? A 50mm² cable is good enough to carry 200A in a engine room. For a 10 meter round trip and 200A alt I went with 70mm²; that's about 4% voltage drop or 100W of power dissipated in the cable at max output. Good enough for that kind of application. Bigger cables are such a PITA.
I’m sure you will be fine. In the US, a 3% maximum drop is used as a guideline. I have runs of double 4/0 aboard (so 4 cables, two negative and two positive) in order to do with 12V where most boats go to 24V.
s/v Jedi is offline   Reply With Quote
Old 10-11-2019, 05:45   #43
rom
Registered User

Join Date: Mar 2016
Boat: Lagoon 440
Posts: 736
Re: Size of DC ground wire question

Quote:
Originally Posted by Pelagic View Post
Are you basing this on a 12v system or 24v system for Start and House?
Seriously Pelagic ? You know that current limitation (e.g. 200A) in a cable is not related to voltage. If your cable is rated 200A and you're using 12V, the good news is that switching to 24V will allow you to carry twice the power (P=VxI), still rated 200A.
rom is offline   Reply With Quote
Old 10-11-2019, 14:04   #44
CF Adviser
 
Pelagic's Avatar

Join Date: Oct 2007
Boat: Van Helleman Schooner 65ft StarGazer
Posts: 10,280
Re: Size of DC ground wire question

I'm pretty dumb when it comes to figuring that out..[emoji20] ......thanks!
Pelagic is offline   Reply With Quote
Old 10-11-2019, 19:48   #45
Registered User

Join Date: Mar 2007
Location: San Francisco
Boat: Tayana 52, AC
Posts: 135
Images: 5
Re: Size of DC ground wire question

Quote:
Originally Posted by Pelagic View Post
I'm pretty dumb when it comes to figuring that out..[emoji20] ......thanks!
I can relate. Most of us have an area of expertise and when we have to ask what may be "simple" questions (for some) it is truly humbling.
I appreciate the help on this thread.
gscriba is offline   Reply With Quote
Reply

Tags
size


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Negative Ground vs Positive Ground History Question. Wotname Electrical: Batteries, Generators & Solar 23 26-04-2021 04:22
Bumping the rigging up one size (wire) do I compensate for streched old wire? Eastward ho 24 Construction, Maintenance & Refit 17 02-07-2019 13:56
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
9 V difference between ground and ground Arrandir Electrical: Batteries, Generators & Solar 12 19-07-2018 22:51
To ground or not to ground an aluminum arch...that is my question. chrtucke Electrical: Batteries, Generators & Solar 9 06-10-2014 23:17

Advertise Here
  Vendor Spotlight
No Threads to Display.


All times are GMT -7. The time now is 03:14.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.