I already know the general formula for sizing an a/c unit. What I want to know, and can't find, is what temperature or temperature drop does the formula hope to achieve? I have talked to a/c people and they recommend x btu and say "you could hang meat". Well i don't want to hang meat I just want to get the temperature to where I don't sweat at night, around 75F. My thinking is if the recommended 16k btu lets me hang meat then I should be comfortable with 6-10k btu. I suspect my thinking is wrong but don't know why. Thanks.
clayzone is offline   Reply With Quote
Old 21-11-2011, 08:18   #2
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,066
Images: 241
Re: sizing a/c

The typical “Tropical” rule of thumb probably assumes a Delta T of about 35 degrees F.
The Temperate rule of thumb probably assumes a Delta T of about 20 degrees F.

Sizing Air-Conditioning:

A “rule of thumb” recommendation* for sizing marine air-conditioning is about ± 14-to- 15 BTU/Hr per cubic foot of cabin volume.
More glazing, pilot house, etc = more heat gain; so perhaps up to 17 BTU/Hr per cu. ft of volume.

* For Tropical climates: 105°F (41°C) air, 95°F (35°C) water, high humidity.
You can reduce the figures to about 75% of above for Temperate climates: 95°F (35°C) air, 85°F (35°C) water, moderate humidity; hence 10 - 12 BTU/Hr per Cu. Ft.

A professional (which I am not) will size the air conditioner based on the latent cooling load (which considers the relative humidity of the air), as well as the sensible cooling load (which considers the Delta T between outdoor & indoor design air temperatures) for your boat & location.
A (theoretically) perfectly-sized air conditioner will run continuously during the hottest 2.5% summer design (outdoor) temperatures.

Don't buy an oversized unit. An over-sized unit short-cycles (turns on & off too rapidly), so doesn’t properly de-humidify*, and uses more energy (starting currents).

On the other hand, make sure any ducting is sized large enough to allow low-velocity air distribution.

* The ability of the air conditioner to remove moisture (latent capacity) is lowest at the beginning of the air conditioner cycle. The moisture removed from the indoor air is dependent upon the indoor coil temperature being below the dew-point temperature of the air. The moisture then wets the indoor coil and, should the unit run long enough, will begin to flow off the coil and be removed out of the condensate drain. For short cycles (< 10 min, or so), the coil does not have time to operate at the low temperature, and when the unit stops, the moisture on the coil evaporates back into the indoor air. Thus, in humid climates, a properly sized air conditioner will do a far better job of removing moisture from the air than oversized units.

See the formulae ➥ Cooling and Heating Equations
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 21-11-2011, 08:30   #3
Registered User

Join Date: Feb 2009
Posts: 2,428
Re: sizing a/c

I have a34' pilot house trawler and am currently in south fl looks like I have 952cf in the house with 12 windows including the windshield not counting the v berth at the lower level I keep the curtains closed most times I dont think I can get the duct work up high probably just out of the floor I suspect most boats have this issue Thoughts? Size of unit?
motion30 is offline   Reply With Quote
Old 21-11-2011, 08:52   #4
Registered User
 
Dennis.G's Avatar

Join Date: May 2011
Location: Sea of Cortez and the U.P. of Michigan
Boat: Celestial 48
Posts: 904
Re: sizing a/c

On a boat with a lot of window area, as it sounds like you have, can see most of the heat gains resulting from solar gains - sunshine coming in through windows. Need to get very good window shading to reduce these gains and give air conditioner any chance of keeping up. Curtains help, but much more effective to shade windows on the outside. Think solar screens. Screening materials that mount outside of the windows can reflect more than half the solar energy. Make sure these, or a full awning, are in your plans.
Dennis.G is offline   Reply With Quote
Old 22-11-2011, 11:29   #5
Registered User
 
clayzone's Avatar

Join Date: Jul 2011
Posts: 56
Re: Sizing A/C

Thanks Gordmay but that still does not tell me what most a/c guys hope to accomplish with the recommended btu's. I believe they talk in degrees of temperature drop, i.e. "you will get 20 degrees drop from outside temperature with this setup", but I am not sure. The point is if someone says I need x with the intent of dropping the temperature to 65 degrees then I think I should be able to use y instead because I only want to go to 75 degrees. Right or not?
clayzone is offline   Reply With Quote
Old 22-11-2011, 15:34   #6
Senior Cruiser
 
GordMay's Avatar

Cruisers Forum Supporter

Join Date: Mar 2003
Location: Thunder Bay, Ontario - 48-29N x 89-20W
Boat: (Cruiser Living On Dirt)
Posts: 50,066
Images: 241
Re: Sizing A/C

Quote:
Originally Posted by clayzone View Post
... I believe they talk in degrees of temperature drop, i.e. "you will get 20 degrees drop from outside temperature with this setup", ...
Right.
Outside to inside temperature drop is what I referred to as "Delta T".

Quote:
The typical “Tropical” rule of thumb probably assumes a Delta T of about 35 degrees F.
The Temperate rule of thumb probably assumes a Delta T of about 20 degrees F.

Sizing Air-Conditioning:

A “rule of thumb” recommendation* for sizing (Tropical) marine air-conditioning is about ± 14-to- 15 BTU/Hr per cubic foot of cabin volume.
More glazing, pilot house, etc = more heat gain; so perhaps up to 17 BTU/Hr per cu. ft of volume...
__________________
Gord May
"If you didn't have the time or money to do it right in the first place, when will you get the time/$ to fix it?"



GordMay is offline   Reply With Quote
Old 23-11-2011, 12:27   #7
Registered User
 
clayzone's Avatar

Join Date: Jul 2011
Posts: 56
Re: Sizing A/C

Thanks for clarifying the Delta T. That is the information I was looking for.
clayzone is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Anchor Sizing . . . Newbie Grateful for Help ! ti325v Anchoring & Mooring 49 01-06-2012 02:53
Sizing a Generator (120v ac) witzgall Electrical: Batteries, Generators & Solar 4 11-09-2011 06:25
Growth in Saltwater A/C Cooling System Conch Cruzer Plumbing Systems and Fixtures 7 13-08-2011 10:59
Want To Buy: 16,500 btu Marine A/C coxjam Classifieds Archive 6 07-08-2011 14:42
A/C Duct Sizing Sailorman375 Plumbing Systems and Fixtures 5 31-07-2011 21:06

Advertise Here


All times are GMT -7. The time now is 10:25.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.