We have been having some battery issues for about a week. The house bank didn't seem to be holding a charge well and could only run the Lectra San (which draws about 30 amps for a couple minutes) when fully charged.

This morning we started charging using an Iota 75 amp charger and within minutes smelled an acrid smell and saw a small amount of smoke coming from the main house bank ground wire which had become hot enough to melt the rubber/plastic coating. The charger was putting out about 65 amps at the time.

The ground wire is about three feet long and runs form the battery negative post to a shunt for the battery monitor. This piece of wire was a 6 gauge wire at least 20 years old. The ground wire from the other side of the shunt to the engine block is a 1/0 gauge wire.

I replaced the hot 3 foot piece of 6 guage ground wire with a similar length 1/0 gauge ground wire and we started charging again, this time using the engine alternator which only puts out about 35 amps. Quite frankly, I was a bit spooked by the hot wire and concerned the the Iota was putting out too much amps for this set of batteries.

We have been charging now for about 3 hours starting at 35 amps decreasing slowly to 13 amps with no problem. No hot ground wire. No acrid battery smell. Batteries are warm, but not hot. They are in the engine compartment so some warmth is normal. Batteries were filled with water a week ago. None of the cells were unusually low.

The battery bank is a 440 hour bank made up of 4 Trojan T-105 6 volt golf cart batteries wired in series/parallell to make up a 12 volt bank. Two of them are about 4 years old and the other two are about 2 years old. One set of two have cases that bulge somewhat. We have been using this arrangement for two years and living aboard for the past 6 months, mostly on the hook. We've been charging the battery bank about twice a week with the Iota charger running off either a Honka 2kw generator or on shore power. Added the Lectra San about 4 months ago and it was working fine until a few days ago.

Sorry for the long post, but my concern is that even though the problem seems to be fixed, maybe there is some other issue besides the too small ground wire.

Is it possible that the ground wire has been undersized for the last couple years and did what it could for as long as it could, then finally just gave up?

Or was the hot ground wire just a symptom and I should be looking for something else that caused the problem?

All thoughts are welcome.
Zydeco is offline   Reply With Quote
Old 13-02-2011, 11:25   #2
Registered User

Join Date: Dec 2009
Posts: 2,959
Images: 4
The #6 wire was not too small for that current. It must have been a bad connection at one of the ends. Replacing the wire repaired the connection. #1/0 is a better choice.
daddle is offline   Reply With Quote
Old 13-02-2011, 11:29   #3
Registered User
 
swisscraft's Avatar

Join Date: May 2010
Location: on my boat
Boat: searching...
Posts: 172
Hi,
have you checked the replaced old wire for corrosion internally? If not I would start there.
Second check each battery independently - mixing old and new batteries in one bank is not recommended.

good luck! Marco
swisscraft is offline   Reply With Quote
Old 13-02-2011, 11:48   #4
Registered User

Join Date: Dec 2008
Location: ontario canada
Boat: grampian 26
Posts: 1,743
Using a good multi meter do a voltage drop test on the connections to isolate the area of high resistance.
perchance is offline   Reply With Quote
Old 13-02-2011, 12:29   #5
Senior Cruiser
 
atoll's Avatar

Cruisers Forum Supporter

Join Date: Mar 2010
Location: gettin naughty on the beach in cornwall
Boat: 63 custom alloy sloop,macwester26,prout snowgoose 37 elite catamaran!
Posts: 10,594
Images: 75
sounds like your old ground wire was corroded to **$k,and acting like a resistor,hence heating up,replacing it and cleaning contacts was the correct thing to do.
atoll is offline   Reply With Quote
Old 13-02-2011, 13:01   #6
Registered User
 
CDunc's Avatar

Join Date: Nov 2010
Location: Jacksonville Florida
Boat: 1972 Tartan 34C Fleur De Mer
Posts: 141
I would check the batteries witht the bulging cases, this is not normal, I would bet those batteries are defective/bad.
CDunc is offline   Reply With Quote
Old 13-02-2011, 13:13   #7
Registered User

Join Date: Nov 2008
Location: Bahamas, US Gulf Coast, and East Coast
Boat: 38' 1983 Pearson 385 - "Zydeco"
Posts: 154
Images: 3
Quote:
Originally Posted by daddle View Post
The #6 wire was not too small for that current. It must have been a bad connection at one of the ends. Replacing the wire repaired the connection. #1/0 is a better choice.
Quote:
Originally Posted by atoll View Post
sounds like your old ground wire was corroded to **$k,and acting like a resistor,hence heating up,replacing it and cleaning contacts was the correct thing to do.
Well, the #6 wire had a layer of corrosion on each terminal end and when I pried it apart, the area where it melted had some greenish corrosion on the wires. Maybe the wire was the problem?

Quote:
Originally Posted by CDunc View Post
I would check the batteries witht the bulging cases, this is not normal, I would bet those batteries are defective/bad.
It doesn't seem normal to me either.

Quote:
Second check each battery independently - mixing old and new batteries in one bank is not recommended.

good luck! Marco
Yu're right, but I was just too cheap to buy 4 new batteries when the two old ones were "just" two years old. I should have done it when we were in the states. I can hardly wait to find out what they are going to set me back in Marsh Harbour.
Zydeco is offline   Reply With Quote
Old 14-02-2011, 21:29   #8
Eternal Member

Join Date: Jul 2006
Posts: 4,046
Images: 4
They'll cost you a few drinks, for sure :-)

I think you probably had at least two things going on:

(1) the AWG6 wire was old, corroded, and likely had very high resistance at the terminal ends; and

(2) the bulging batteries may have internal damage to the plates and should be replaced.

Actually, ALL the batteries should be replaced with new ones. It's costly, alright, but at least you'll know what you've got and you can take care of them. I'd also add HydroCaps or WaterMiser caps to reduce the loss of water.

By the way, four T-105's in series/parallel gives you 450AH at the 20-hour rate. These batteries can easily take 90A in the bulk & acceptance charging stages; your Iota is not too big.

I don't agree that the AWG6 wire was large enough, even had it been new. For a sustained 75A charge -- which the Iota can put out -- 1/0 is a much better choice. It offers much lower resistance and this is very desirable when dealing with battery charging.

Check ALL your battery connections. The series/parallel jumper cables should be clean and tight. Ideally, they should also be 1/0 or larger. The wise thing to do would probably be to replace all the cables with new ones which have been properly terminated.

Bill
btrayfors is offline   Reply With Quote
Old 14-02-2011, 23:02   #9
Registered User
 
capnorv's Avatar

Join Date: Sep 2010
Location: Bainbridge Island Washington on the Salish Sea
Boat: Hardin 45 Voyager Alice B., Gig Harbor 10, Orca 7 1/2 sloop, 16' sea kayak
Posts: 439
Images: 1
Your #6 wire would be peachykeen at 65 amps if you were running AC or high voltage DC electricity, but you are running neither. So even without the corroded terminations, the heat buildup of 65amp, 12 voltsdc through a #6 wire is BAD for fire suppression. Kicking up the wire gauge was a very astute plan. As for warped battery cases, very few times is this a good sign, sorry. You could waste money getting them load tested or drain the kitty on new ones and have peace of mind. Would I replce all 4, depends if I had the money or could put the old ones on one bank and new ones on the other. Good Luck
capnorv is offline   Reply With Quote
Old 15-02-2011, 04:52   #10
Registered User

Join Date: Nov 2008
Location: Bahamas, US Gulf Coast, and East Coast
Boat: 38' 1983 Pearson 385 - "Zydeco"
Posts: 154
Images: 3
Update

Thanks all for the wise counsel. I feel better now.

We were able to find 4 new 6 volt golf cart batteries in Marsh Harbour. Only cost about twice the US price. These are generics that the battery guy said were made by Trojan. Who knows, but they seem to be working well. Put them in yesterday and charged with the Iota with no problems.

The hydrocaps sound like a good idea. I'll look into those when we get back to the US.
Zydeco is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
How to Wire a Battery Isolator with a Three Wire Alternator ? bazzer Electrical: Batteries, Generators & Solar 7 05-12-2010 12:47
Hot Water System - Extra Hot Water Needed ? Harben Plumbing Systems and Fixtures 8 07-10-2010 16:20
Bilge Pump Switch 'Hot' or 'Ground' ? sailorboy1 Plumbing Systems and Fixtures 28 06-06-2010 22:06
Ohhhhh Hot! Hot! Hot! knottybuoyz Marine Electronics 6 01-06-2007 07:43
hot wire tauras Health, Safety & Related Gear 17 01-08-2004 23:22

Advertise Here


All times are GMT -7. The time now is 06:33.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.