Old 18-05-2024, 14:14   #16
Registered User

Join Date: Nov 2012
Location: Steinhatchee, FL
Posts: 402
Re: Solar Disconnect & Alternator Interference

Quote:
Originally Posted by donradcliffe View Post
I always put fuses between the controller and the battery, and I have blown them more than once.....
Maybe a bigger wire and a bigger fuse? Sounds like you are leaving amps on the table.
__________________
Bill
"If I were in a hurry, I would not have bought a sail boat." Me
Be Free is offline   Reply With Quote
Old 18-05-2024, 23:24   #17
Registered User

Join Date: Nov 2020
Location: Nelson NZ
Boat: Current yacht:Alden 46, previous yachts:Cavalier 32, Joshua steel ketch -12m, Traveller 32,Rawson 30
Posts: 475
Images: 2
Re: Solar Disconnect & Alternator Interference

To Charlie J:
Here's the quote from my post regarding solar controller damage:
2) Victron says do NOT put any switches or fuses between the controller and the battery (you will find this warning in the manual). If you disconnect the controller from the battery for any reason while the panels are producing any output, you will damage the controller beyond any repair.
I also said:
3) Yes, good idea to have a fuse in the pos line from controller to panels to protect that wiring.
You will find what 3) Yes, good idea to have a fuse in the pos line from controller to panels to protect that wiring.


You'll find the citation on page 12 and 13 of the manual for the Blue Solar 70-10 which can download from the Victron website.



I have 3 different brand solar controllers and they ALL say do not disconnect the battery from controller when panels are producing output. With respect, why don't you give it a try with your own controller and let us know the result?
nuku34 is offline   Reply With Quote
Old 19-05-2024, 00:36   #18
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,887
Re: Solar Disconnect & Alternator Interference

Quote:
Originally Posted by nuku34 View Post
To Charlie J:
Here's the quote from my post regarding solar controller damage:
2) Victron says do NOT put any switches or fuses between the controller and the battery (you will find this warning in the manual). If you disconnect the controller from the battery for any reason while the panels are producing any output, you will damage the controller beyond any repair.
I also said:
3) Yes, good idea to have a fuse in the pos line from controller to panels to protect that wiring.
You will find what 3) Yes, good idea to have a fuse in the pos line from controller to panels to protect that wiring.


You'll find the citation on page 12 and 13 of the manual for the Blue Solar 70-10 which can download from the Victron website.



I have 3 different brand solar controllers and they ALL say do not disconnect the battery from controller when panels are producing output. With respect, why don't you give it a try with your own controller and let us know the result?
I don't know what you have been smoking, but I find that the Victron manual clearly states the size of the fuse to put in the wire from the controller to the battery in Section 4.2 on Page 9.
donradcliffe is offline   Reply With Quote
Old 19-05-2024, 01:10   #19
Registered User
 
NYSail's Avatar

Join Date: Jan 2012
Location: Long Island, New York
Boat: Beneteau 423 43 feet
Posts: 867
Re: Solar Disconnect & Alternator Interference

I have a breaker between panels and controller. Comes in hand when I need to turn off the power. And yes when panels and engine are running after a few hours my tach will stop. They don’t play well together…. At least my last controller which was a Renogy 40 amp mppt. Just bought a 100/50 I stalled for this season. So i turn panels off when powering long distances1+ hours.

Greg
NYSail is offline   Reply With Quote
Old 19-05-2024, 01:47   #20
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,989
Re: Solar Disconnect & Alternator Interference

Quote:
Originally Posted by nuku34 View Post
To Charlie J:
Here's the quote from my post regarding solar controller damage:
2) Victron says do NOT put any switches or fuses between the controller and the battery (you will find this warning in the manual). If you disconnect the controller from the battery for any reason while the panels are producing any output, you will damage the controller beyond any repair.
...........

You'll find the citation on page 12 and 13 of the manual for the Blue Solar 70-10 which can download from the Victron website.



I have 3 different brand solar controllers and they ALL say do not disconnect the battery from controller when panels are producing output. With respect, why don't you give it a try with your own controller and let us know the result?
With respect, you are providing erroneous advice, please stop. Not only is your advice incorrect, it is potentially dangerous to suggest not having a fuse between the battery and solar charge controller (located close to the battery). But don't take my word for it, check the various Victron manuals e.g. page 4 of https://www.victronenergy.com/upload...R_DE_ES_SE.pdf

or page 11 and 14 of https://www.victronenergy.com/upload...ual-pdf-en.pdf

Screenshots attached.


Consider the worst case scenario.
1. Fuse fitted and blows - destroys solar charge controller
2. No fuse - fault in wiring (or controller) burns boat to the waterline

Me - I'll take my chances with #1 but never with #2
Attached Thumbnails
Click image for larger version

Name:	Screenshot 2024-05-19 at 6.41.37 pm.jpg
Views:	7
Size:	120.0 KB
ID:	290047   Click image for larger version

Name:	Screenshot 2024-05-19 at 6.43.20 pm.png
Views:	14
Size:	179.0 KB
ID:	290048  

__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is online now   Reply With Quote
Old 24-05-2024, 07:04   #21
Registered User
 
OS2Dude's Avatar

Join Date: Nov 2014
Location: Atlanta, GA
Boat: Catalina 30
Posts: 686
Images: 5
Re: Solar Disconnect & Alternator Interference

Quote:
Originally Posted by Gone Gypsy View Post
Any comment based on experience on installing breaker switches on panel cables before controller? Good idea? Waste? Thanks.
You can't use any old breaker in a DC system, it MUST be a DC breaker. Breaker is a good on/off switch to disconnect panels before disconnecting bank from controller.

Section 4.2 of the Victron MPPT 100|50 manual states you MUST have a fuse between battery and controller.
4.2. Battery
The battery supply must be protected by a fuse as per the below table.
Solar charger type Minimum battery fuse rating Maximum battery fuse rating
MPPT 100/30 35A 40A
MPPT 100/50 55A 70A

Every connection to a battery should be fused. It -may- harm the controller if the fuse blows while the array is operating but even if it does it is better than risking a fire.
OS2Dude is offline   Reply With Quote
Old 24-05-2024, 07:26   #22
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: Solar Disconnect & Alternator Interference

nuku34:
Quote:
2) Victron says do NOT put any switches or fuses between the controller and the battery (you will find this warning in the manual)
Please provide the citation for your assertion/interpretation. And while you are in the manual, read it closely and review the illustration.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 24-05-2024, 07:34   #23
Registered User
 
Gone Gypsy's Avatar

Join Date: Jan 2013
Location: Cortez / Annapolis
Boat: McIntosh 47
Posts: 137
Re: Solar Disconnect & Alternator Interference

Thanks everyone for your input. I have planned DC disconnects on both legs between panels and controller. I had planned a 40 amp fuse between Victron 100/50 controller and battery because I am only delivering 27 amps max but understand 70 amp fuse would be appropriate for full 50 amp output.

We are leaving boat so I can order and be home for delivery of the goodies in 3 days. Will keep you updated on install. Will post install to the popular solar picture string in this forum.

Thanks again,
Gone
Gone Gypsy is offline   Reply With Quote
Old 24-05-2024, 12:08   #24
Registered User
 
robbjd's Avatar

Join Date: Nov 2020
Location: Sarnia, Ontario, Canada
Boat: Catalina 34 MKII
Posts: 19
Re: Solar Disconnect & Alternator Interference

Seems some of this forums contributors are dyslexic or just plain dumb! Read your manual and it clearly shows protection between the panels and controller, and the controller and batteries. I have 1-230 watt panel feeding through a 40A double pole breaker to a Victron 100/30 Smartsolar charge controller, which then feeds my LiFePo batteries via a 40A fuse. Depending on your panel setup,without the breaker or fuse upstream of the controller you could expose yourself to a high enough voltage to do yourself harm, or worse.
robbjd is offline   Reply With Quote
Old 25-05-2024, 05:53   #25
Registered User

Join Date: May 2023
Posts: 25
Re: Solar Disconnect & Alternator Interference

Hi All,
I did a major redo of my Bene 331 which had quite troublesome DC system. My observations:
-solar doesn’t interfere with my Balmar 120A alternator and 618 regulator- it pumps 90A onto batteries that are low on SOC no problem
- fusing is a must and do it if you want to be safe and alive
- I have a couple of switches that allow me to do solar’s parallel or in series but I found parallel more efficient most likely due to shading
mroc is offline   Reply With Quote
Old 25-05-2024, 07:02   #26
Registered User
 
Gone Gypsy's Avatar

Join Date: Jan 2013
Location: Cortez / Annapolis
Boat: McIntosh 47
Posts: 137
Re: Solar Disconnect & Alternator Interference

mroc,
I pushed the button and ordered. Order includes Y connectors for parallel so I can test series against parallel in my exact application. Not a switch like your setup for quick comparison, but capable. Victron in particular says series will deliver higher total energy when coupled with panels that have diodes. From my reading most cruisers - More than 80%, say parallel is the way to go. This number I think is weighted by lots of Bimini installs that have considerable shading. Our install is on davits with minimal shading using diode panels. We’ll see!
Gone Gypsy is offline   Reply With Quote
Old 25-05-2024, 15:57   #27
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 20,989
Re: Solar Disconnect & Alternator Interference

Quote:
Originally Posted by Gone Gypsy View Post
Thanks everyone for your input. I have planned DC disconnects on both legs between panels and controller. I had planned a 40 amp fuse between Victron 100/50 controller and battery because I am only delivering 27 amps max but understand 70 amp fuse would be appropriate for full 50 amp output.

We are leaving boat so I can order and be home for delivery of the goodies in 3 days. Will keep you updated on install. Will post install to the popular solar picture string in this forum.

Thanks again,
Gone
Sounds like a good plan. Just make sure the fuse between the solar controller and battery is placed as close as practicable to the battery end of the wire.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is online now   Reply With Quote
Reply

Tags
alternator, enc, interference, solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Myth of alternator damage cause by BMS disconnect? tanglewood Lithium Power Systems 283 04-02-2024 16:00
Alternator Field Disconnect? Extemporaneous Electrical: Batteries, Generators & Solar 32 03-01-2022 14:25
Airmar "Transom&q uot ; style triducer does not give wate Franziska Marine Electronics 3 04-10-2021 12:45
Alternator disconnect BigAl.NZ Electrical: Batteries, Generators & Solar 4 27-10-2017 17:33
Disconnect Alternator While Running ? Cruisin Cat Electrical: Batteries, Generators & Solar 10 09-12-2011 13:35

Advertise Here


All times are GMT -7. The time now is 19:06.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.