Old 04-01-2024, 16:44   #31
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,218
Re: Two AGM in Parallel. One gets warm.

Quote:
Originally Posted by allendick View Post
I doubt he knows. I have a Heart monitor and a Balmar Smartgauge and they appeared to have the roughly full rated capacity until recently according to both. They did get discharged to 30 % at one point and in the last while the monitors have not agreed. Coincidence?
I don’t know, I have no experience with those monitors.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 04-01-2024, 16:51   #32
Registered User

Join Date: Apr 2007
Location: Sidney BC
Boat: 2007 Bavaria 50 Cruiser
Posts: 55
Re: Two AGM in Parallel. One gets warm.

Thanks for the help. I am going to have to work this out over the next few days. What I see is the opposite of what I expected. The warm battery is holding the voltage. The cool one, not so much.

Right now the warm one is disconnected and I'm running on the charger and the cool one (which dropped to 12.66 before I turned on the switch and charger). The other is stil at 12.81.

I'll resume the project tomorrow. I may equalise. We'll see. I need to think about it.

Just the same, I'll go to lithium before too long.
allendick is offline   Reply With Quote
Old 04-01-2024, 18:52   #33
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,218
Re: Two AGM in Parallel. One gets warm.

Quote:
Originally Posted by allendick View Post
Thanks for the help. I am going to have to work this out over the next few days. What I see is the opposite of what I expected. The warm battery is holding the voltage. The cool one, not so much.

Right now the warm one is disconnected and I'm running on the charger and the cool one (which dropped to 12.66 before I turned on the switch and charger). The other is stil at 12.81.

I'll resume the project tomorrow. I may equalise. We'll see. I need to think about it.

Just the same, I'll go to lithium before too long.
I believe Lifeline has instructions on equalizing them. It sounds like the one that went down to 12.66V may need that, but you can also make it work with a couple deep cycles, like down to just 20% state of charge, then fully recharge again. Often batteries regain most of lost capacity again from that.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 05-01-2024, 06:05   #34
Marine Service Provider
 
witzgall's Avatar

Join Date: Oct 2006
Location: Eastern Shore, MD
Boat: Camper Nicholson 44 Ketch
Posts: 2,060
Re: Two AGM in Parallel. One gets warm.

Do you have the battery cables attached to only one battery, or is the positive on one and the negative on the other? This can lead to unequal charging/discharging if they are both on the same battery. While you are at it, check the condition of the cables very carefully.

Chris
witzgall is offline   Reply With Quote
Old 05-01-2024, 07:18   #35
Registered User

Join Date: Apr 2007
Location: Sidney BC
Boat: 2007 Bavaria 50 Cruiser
Posts: 55
Re: Two AGM in Parallel. One gets warm.

They are set up properly. The negative is on one, the positive on the other.
allendick is offline   Reply With Quote
Old 05-01-2024, 09:11   #36
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,875
Re: Two AGM in Parallel. One gets warm.

My first thought is that you may have a bad connection to the hot battery, and resistance heating around the bad connection. Clean the cables and posts and try again.

If that doesn't solve the problem, unplug the charger and solar, hook up one of the batteries, and do a 20 hour load test. That means turning on enough stuff to pull 10 amps and see how long it takes for the 200 ahr battery to get down to 10.5 volts. If it lasts more than 10 hours try the same test on the other battery.
donradcliffe is offline   Reply With Quote
Old 05-01-2024, 09:36   #37
Registered User

Join Date: Mar 2014
Location: Seattle, WA
Posts: 844
Re: Two AGM in Parallel. One gets warm.

Question: shorted cells on old FLA batteries are a cause of fires. Does that same hazard exist with AGMs?
mako is offline   Reply With Quote
Old 05-01-2024, 09:45   #38
Registered User

Join Date: Apr 2007
Location: Sidney BC
Boat: 2007 Bavaria 50 Cruiser
Posts: 55
Re: Two AGM in Parallel. One gets warm.

All connections are perfect. My thoughts mirror yours. I just have to figure out how to load test.

First, I need an appropriate load that can be attached and then I need to monitor voltage.

Second, I have to be here, checking regularly, and 20 hours is longer than my waking day.

I could do a 10-hour or even 6-hour, and of course it is just a guess how long it will take at a given load if the batteries have lost capacity.

Right now I am running on just the cool battery.

I just checked the one that was warm and is now disconnected. Even 12 hours later the voltage is 12.77. It was 12.82 when I disconnected it. (It had been on float).

I am now suspecting that this is the good battery and the other might be high resistance.
allendick is offline   Reply With Quote
Old 05-01-2024, 10:01   #39
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,218
Re: Two AGM in Parallel. One gets warm.

Quote:
Originally Posted by mako View Post
Question: shorted cells on old FLA batteries are a cause of fires. Does that same hazard exist with AGMs?
Yes it does.

Quote:
Originally Posted by allendick View Post
All connections are perfect. My thoughts mirror yours. I just have to figure out how to load test.

First, I need an appropriate load that can be attached and then I need to monitor voltage.

Second, I have to be here, checking regularly, and 20 hours is longer than my waking day.

I could do a 10-hour or even 6-hour, and of course it is just a guess how long it will take at a given load if the batteries have lost capacity.

Right now I am running on just the cool battery.

I just checked the one that was warm and is now disconnected. Even 12 hours later the voltage is 12.77. It was 12.82 when I disconnected it. (It had been on float).

I am now suspecting that this is the good battery and the other might be high resistance.
Lifeline also has a 10hr capacity in their specifications so you can simply do a 10hr test instead of the 20hr test using the higher load from the specs.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 05-01-2024, 10:11   #40
Registered User

Join Date: Apr 2007
Location: Sidney BC
Boat: 2007 Bavaria 50 Cruiser
Posts: 55
Re: Two AGM in Parallel. One gets warm.

Fire was my big concern, although there does not seem to be a short. High resistance in one is more likely I think.

I suspect that the ten hour test won't take anything like ten hours on four+ year old batteries.

I just need to decide on a load and set it up, while still having 12V power for my appliances, inclusing this Internet (Starlink).
allendick is offline   Reply With Quote
Old 05-01-2024, 10:22   #41
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,218
Re: Two AGM in Parallel. One gets warm.

Quote:
Originally Posted by allendick View Post
Fire was my big concern, although there does not seem to be a short. High resistance in one is more likely I think.

I suspect that the ten hour test won't take anything like ten hours on four+ year old batteries.

I just need to decide on a load and set it up, while still having 12V power for my appliances, inclusing this Internet (Starlink).
Simply use one battery to run the boat while testing the other one. Maybe you have some DC powered appliance for the load or a separate inverter?
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 05-01-2024, 10:30   #42
Registered User

Join Date: Apr 2007
Location: Sidney BC
Boat: 2007 Bavaria 50 Cruiser
Posts: 55
Re: Two AGM in Parallel. One gets warm.

That is the plan, but I do not have boosters so the cabling and layout is the issue.

I suppose I could just turn things on, turn the chargers off, use the boat circuit as load and record current draw and voltage periodically for a quick and dirty estimate.

No wiring needed. I just have to find the ten-hour test draw for the GPL-8Ds.

Then switch batteries.
allendick is offline   Reply With Quote
Old 05-01-2024, 12:11   #43
Registered User

Join Date: Apr 2007
Location: Sidney BC
Boat: 2007 Bavaria 50 Cruiser
Posts: 55
Re: Two AGM in Parallel. One gets warm.

I put a 15-Amp load on the cool battery and turned off the charger.

Immediately the voltage was lower than I expected under such a light load. At one point I tried to run the microwave oven, not ever an issue with both connected, even at 50% battery.

11:45 15A 12.06 V
12:10 13A 12.11 V - Could not power the microwave.
12:45 15A 11.98

I'm guessing that this is the problem battery,
allendick is offline   Reply With Quote
Old 05-01-2024, 12:27   #44
Registered User
 
Cheechako's Avatar

Join Date: Aug 2006
Location: Skagit City, WA
Posts: 25,636
Re: Two AGM in Parallel. One gets warm.

Quote:
Originally Posted by allendick View Post
I put a 15-Amp load on the cool battery and turned off the charger.

Immediately the voltage was lower than I expected under such a light load. At one point I tried to run the microwave oven, not ever an issue with both connected, even at 50% battery.

11:45 15A 12.06 V
12:10 13A 12.11 V - Could not power the microwave.
12:45 15A 11.98

I'm guessing that this is the problem battery,
Just charge both, immediately disconnect and let them sit. Measure voltage in a few hours. The one that stays charged is the good one.
__________________
"I spent most of my money on Booze, Broads and Boats. The rest I wasted" - Elmore Leonard











Cheechako is offline   Reply With Quote
Old 05-01-2024, 12:27   #45
Moderator
 
Pete7's Avatar

Cruisers Forum Supporter

Join Date: Aug 2009
Location: Solent, England
Boat: Moody 31
Posts: 18,561
Images: 22
Re: Two AGM in Parallel. One gets warm.

Quote:
Originally Posted by mako View Post
Question: shorted cells on old FLA batteries are a cause of fires. Does that same hazard exist with AGMs?
Oh yes very much so. I look after a server at work that has a UPS with 12v AGM batteries, eight I think. This is the second UPS, the alarm when off on the first one so went to investigate. The smell was the hint that all was not well. The scorching hot metal case also a bit of a worry. Disconnected and using a truck trolley wheeled it out into the car park. Still warm the following morning from the boiling acid inside. We didn't even bother to open it up, just scrapped the whole unit. We were lucky because it was in the same rack as the server and we were in work. If it had been a weekend the ending could have been quite different.

The problem is normally a shorted cell so the charger see 10v and thinks the battery needs charging so pumps power into it. This turns into heat and just builds up and up.

Pete
Pete7 is offline   Reply With Quote
Reply

Tags
agm


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Two 6v in series or two 12v in parallel? davenrino Electrical: Batteries, Generators & Solar 12 19-11-2021 14:35
Quick windlass gear box gets warm Sam Woodbridge General Sailing Forum 6 02-07-2021 11:06
Fuel tank gets warm when motoring zerompg Engines and Propulsion Systems 17 10-03-2017 18:27
Two solo cruisers , Two boats OR Two Captains One Boat colo.sail General Sailing Forum 8 17-12-2011 16:36
Four Solar Panels - Parallel , Series or Series-Parallel west coaster Electrical: Batteries, Generators & Solar 76 07-07-2011 14:35

Advertise Here


All times are GMT -7. The time now is 00:53.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.