On our boat, the ac circuits are protected with two-pole breakers. For each circuit, the grounds are led to a common ground , with the hot and neutral each disrupted when the breaker is tripped. The neutral is wired back to the main ac two-pole breaker as well as the hot.

All of the outlets are let to a single breaker. Since we are wintering on the boat, this will not power two heaters, as we would like. So my plan is to add an additional breaker to split up the fore and aft outlets. There is not room on the panel for another double pole breaker. I believe it would be ok to put a new, single pole breaker on the hot wire, the ground to the common ground bus bar, and the neutral to the neutral of the main ac breaker. Am I correct?

A whole new panel might be in the future, but we have other things we would like to spend the ###, and the current one seems to be in good order.

The Panel:

Closeup of the AC side. The double pole breaker that has green wires leading to it is the AC Main:

and the rest of the spaghetti:
witzgall is offline   Reply With Quote
Old 18-11-2013, 07:29   #2
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: two-pole branch protection

Usually you only see the neutral broken on branch circuits on aluminum or steel hulls. In general yes you only need the hot broken on a 120V circuit. ABYC states that the only requirement for breaking a branch circuit with a single pole in the hot is that the AC system must be equipped with a reverse polarity indicator or transformer.
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Old 18-11-2013, 11:47   #3
Registered User

Join Date: Aug 2011
Location: Atlantic City, NJ
Boat: Beneteau 49
Posts: 81
I was about to ask the same question. I presently have a Beneteau. They breaker both the neutral and hot except for the air conditioning panel, where only the hot is through a breaker. My previous 2 boats were Catalina's where only the hots went through the breakers. I am also looking to split up a double breaker into 2 separate circuits breaking only the hots.
georgec is offline   Reply With Quote
Old 18-11-2013, 13:06   #4
Registered User
 
Viking Sailor's Avatar

Join Date: Nov 2006
Location: San Francisco Bay
Boat: Fantasia 35
Posts: 1,251
Re: Two-pole branch protection

Usually, when an AC panel has a single breaker it is sized to support the maximum power the shore side plug/wiring is capable of handling. So, if shore power is setup for a 30A connection you should have a 30A panel breaker installed. If the panel breaker is less then what the shore plug/wiring is designed to handle -- then replace the current breaker with a correctly sized breaker.

Viking Sailor is online now   Reply With Quote
Old 18-11-2013, 22:20   #5
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Two-pole branch protection

Quote:
Originally Posted by Viking Sailor View Post
Usually, when an AC panel has a single breaker it is sized to support the maximum power the shore side plug/wiring is capable of handling. So, if shore power is setup for a 30A connection you should have a 30A panel breaker installed. If the panel breaker is less then what the shore plug/wiring is designed to handle -- then replace the current breaker with a correctly sized breaker.

this has nothing to do with the question...


as posted already. the single is fine. most boats are single with a dual master. by abyc you should have a rev. poliarty light if only single breakers. (I would have one either way though..)


it also looks like your main is a triple pole and breaking the ground. this should be bypassed. you don't want the green to disconnect. it should bypass the breaker and always be connected. it's fine it just leave the 3re pole empty once you move the green wire.
smac999 is offline   Reply With Quote
Old 18-11-2013, 23:17   #6
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Two-pole branch protection

Quote:
Originally Posted by smac999 View Post
this has nothing to do with the question...


as posted already. the single is fine. most boats are single with a dual master. by abyc you should have a rev. poliarty light if only single breakers. (I would have one either way though..)


it also looks like your main is a triple pole and breaking the ground. this should be bypassed. you don't want the green to disconnect. it should bypass the breaker and always be connected. it's fine it just leave the 3re pole empty once you move the green wire.
smac,

That's a Paneltronic's panel, and the main is not actually a 3 pole breaker, breaking the earth by design. It's design is part of the reverse polarity circuit. If the shore side is wired reverse polarity, then the ships main will trip automatically. The third pole is a trip coil for the reverse polarity trip circuit.

Now if some hack has been aboard and re-wired it improperly...all design functions go out the window.

Lloyd
FlyingCloud1937 is offline   Reply With Quote
Old 18-11-2013, 23:39   #7
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Two-pole branch protection

Quote:
Originally Posted by FlyingCloud1937 View Post
smac,

That's a Paneltronic's panel, and the main is not actually a 3 pole breaker, breaking the earth by design. It's design is part of the reverse polarity circuit. If the shore side is wired reverse polarity, then the ships main will trip automatically. The third pole is a trip coil for the reverse polarity trip circuit.

Now if some hack has been aboard and re-wired it improperly...all design functions go out the window.

Lloyd

how does that work? where would those green wires normally go to? there would have to be some other device in that system. looks awfully like 10awg main feed wires in and out to me but hard to tell without following them.
smac999 is offline   Reply With Quote
Old 19-11-2013, 00:07   #8
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Two-pole branch protection

Quote:
Originally Posted by smac999 View Post
how does that work? where would those green wires normally go to? there would have to be some other device in that system. looks awfully like 10awg main feed wires in and out to me but hard to tell without following them.
Smac

Paneltronics Main

Recognize that the third pole/earth is not a breaker it's a trip coil. It will pass even when the hot/neutral is tripped.

Again remember I said as long as no hacks have been aboard.

Lloyd
FlyingCloud1937 is offline   Reply With Quote
Old 19-11-2013, 04:06   #9
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Quote:
Originally Posted by FlyingCloud1937 View Post

Smac

Paneltronics Main

Recognize that the third pole/earth is not a breaker it's a trip coil. It will pass even when the hot/neutral is tripped.

Again remember I said as long as no hacks have been aboard.

Lloyd
What's the device connected across the terminals , a MOV. If so not a great idea.

Dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 19-11-2013, 06:03   #10
Registered User
 
Colin A's Avatar

Join Date: Mar 2013
Location: East of the river CT
Boat: Oday Mariner 19 , Four Winns Marquis 16 OB, Kingfisher III
Posts: 657
Send a message via Skype™ to Colin A
Re: Two-pole branch protection

Yeah it's a MOV. This was a pretty common design for main power breakers on panels until recently to provide auto disconnect on reverse polarity. I have heard these can cause nuisance tripping with ELCI's thou.
__________________
mysite: Colinism.com
Colin A is offline   Reply With Quote
Old 19-11-2013, 06:05   #11
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: Two-pole branch protection

Quote:
Originally Posted by Colin A View Post
Yeah it's a MOV. This was a pretty common design for main power breakers on panels until recently to provide auto disconnect on reverse polarity. I have heard these can cause nuisance tripping with ELCI's thou.

Yeah thats what I meant , also as they are tripped , the lower they tripped voltage, essentially getting worse as they get older.


dave
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 19-11-2013, 07:11   #12
Marine Service Provider
 
witzgall's Avatar

Join Date: Oct 2006
Location: Eastern Shore, MD
Boat: Camper Nicholson 44 Ketch
Posts: 2,060
Re: Two-pole branch protection

How do you know it is a paneltronics panel? This is a 1978 Camper and Nicholsons, an english boat. I would think the stuff would be made over there.

The ground is not broken.

Is there any source of those old-style push to set and reset breakers?

Thanks for all of the replies. Now I Just have to mount the new breaker, and split the wiring run from the outlets with some new wire back to the panel for 1/2 of the outlets.

Chris
witzgall is offline   Reply With Quote
Old 19-11-2013, 08:53   #13
Marine Service Provider

Join Date: Oct 2011
Posts: 1,109
Re: Two-pole branch protection

Quote:
Originally Posted by witzgall View Post
How do you know it is a paneltronics panel? This is a 1978 Camper and Nicholsons, an english boat. I would think the stuff would be made over there.

The ground is not broken.

Is there any source of those old-style push to set and reset breakers?

Thanks for all of the replies. Now I Just have to mount the new breaker, and split the wiring run from the outlets with some new wire back to the panel for 1/2 of the outlets.

Chris
Paneltronics Breakers

They are a large OEM panel builder, when your boat was built they were one of the largest.

Quote:
goboatingnow Quote:
Originally Posted by FlyingCloud1937

Smac

Paneltronics Main

Recognize that the third pole/earth is not a breaker it's a trip coil. It will pass even when the hot/neutral is tripped.

Again remember I said as long as no hacks have been aboard.

Lloyd


What's the device connected across the terminals , a MOV. If so not a great idea.

Dave
There thousands upon thousands of those breakers in service. Every SeaRay, Tolley and countless other large boat manufactures. I have never seen a failure in 30 some years.

Lloyd
FlyingCloud1937 is offline   Reply With Quote
Reply

Tags
rot


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Whisker Poles Dockhead Deck hardware: Rigging, Sails & Hoisting 15 26-06-2013 01:12
Telescoping Whisker Pole Dockhead Deck hardware: Rigging, Sails & Hoisting 19 08-03-2013 19:25
Sail Inventory for a Large Cruiser Dockhead Deck hardware: Rigging, Sails & Hoisting 24 09-11-2012 00:24
Lightning Strikes sokari The Sailor's Confessional 185 24-07-2012 19:31
Double Pole Breakers on Metal Boats? msponer Electrical: Batteries, Generators & Solar 29 28-12-2011 14:00

Advertise Here


All times are GMT -7. The time now is 09:25.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.