Voltage drop solar controller to batteries

What % voltage drop should I be aiming for when sizing the wire gauge between mppt controller and batteries?

400 watts of panels. About 8-10ft from controller to 12v bank.

Putting the maximum potential 32.5 amps into online wire calculator, says 2awg for 1% or 4awg for 2% drop. But am I ever really gonna see those numbers enough to be worth using 2awg?

It's a 1 time purchase so i will spend the extra for 2 awg if it makes sense. But I question whether that is unnecessary overkill?
SKMT is offline   Reply With Quote
Old 12-07-2021, 07:22   #2
Registered User

Join Date: Nov 2018
Location: Panama
Boat: Norseman 447
Posts: 1,628
Re: Voltage drop solar controller to batteries

Wire sizing calculators tell you the minimum size you can get away with. Every watt lost in the wiring is a watt that you’ve paid for but are throwing away. Why spend hundreds of dollars for high-output panels and a exotic regulator, then throw away the efficiency gains to save maybe $40 on wire?
Bycrick is offline   Reply With Quote
Old 12-07-2021, 08:19   #3
Registered User
 
Nord Sal's Avatar

Join Date: Sep 2014
Location: POW Alaska
Boat: Trlåren 31
Posts: 340
Re: Voltage drop solar controller to batteries

Quote:
Originally Posted by SKMT View Post
What % voltage drop should I be aiming for when sizing the wire gauge between mppt controller and batteries?

400 watts of panels. About 8-10ft from controller to 12v bank.

Putting the maximum potential 32.5 amps into online wire calculator, says 2awg for 1% or 4awg for 2% drop. But am I ever really gonna see those numbers enough to be worth using 2awg?

It's a 1 time purchase so i will spend the extra for 2 awg if it makes sense. But I question whether that is unnecessary overkill?

1% voltage drop at maximum rate (which will only occur a small fraction of the time) is overkill. AWG 8 will work with a 3% voltage drop for a 16 foot circuit (round trip) at max current. AWG 10 will work for 16 feet with a 5% loss. Most of the time you're current will be much less and the voltage drop will be less accordingly.
Nord Sal is offline   Reply With Quote
Old 12-07-2021, 08:36   #4
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Voltage drop solar controller to batteries

Normally 3% for power distribution and 10% for loads.

1% would be crazy. especially when solar will never see 100% current anyways.
smac999 is offline   Reply With Quote
Old 12-07-2021, 08:57   #5
Registered User

Join Date: Jun 2012
Location: Port Aransas, Texas
Boat: 2019 Seawind 1160 Lite
Posts: 2,126
Re: Voltage drop solar controller to batteries

840 watts solar, LiFePO4 house battery. Rewired the boat to alleviate voltage drop and used 2 AWG between solar controller and common negative and positive bus bars. Then 4/0 to the LiFePO4 battery. Yeah, it was overkill, but wanted to eek out as much as possible from solar, and not have to install more panels/second controller.

To me, additional cost of the wire was lesser consideration. Upsizing and pulling wire thru limited circuit box openings, etc., on a fully-wired boat was a PITA that I never wanted to repeat. Also invested in tool to cut large diameter wire and another to make proper four-sided crimps. 4/0 cable is not easy to cut, nor crimp. Some good tips on Maine Sail's website.
sailjumanji is offline   Reply With Quote
Old 12-07-2021, 10:12   #6
Senior Cruiser

Cruisers Forum Supporter

Join Date: Dec 2011
Location: Buzzards Bay MA
Boat: Beneteau 423
Posts: 905
Re: Voltage drop solar controller to batteries

The other consideration is that you will seldom, if ever, see 400W. For example, I have 380W of Solbian flexible panels on my bimini. During May in the Bahamas my controller claimed to have a max power of 369W. More typically it is max of 280-300. And remember that is an instantaneous maximum. Most of the day it is less. You definitely want to be sized adequately, but if you consider typical is likely to be more like 300W, then using a 3% factor at 400W will get you 2% at 300W for the same size wire. Re-run the numbers based on your own assumptions (mounting position, latitude, typical max power, etc.) and targets.
Harry
hlev00 is offline   Reply With Quote
Old 12-07-2021, 10:27   #7
Registered User

Join Date: Jul 2021
Posts: 22
Re: Voltage drop solar controller to batteries

Some really good comments

Basically you want to be as close and heavy as practible

Yes it may be overkill, and yes you'll never see max watts, but what is the true cost?

It's your time, money and energy dealing in the first place

The price differential between guages is peanuts compared to the other factors

Do it once, do it right, and forget about it
Snerf1 is offline   Reply With Quote
Old 12-07-2021, 10:35   #8
Registered User

Join Date: Aug 2019
Location: New England
Boat: Building myself... FTW
Posts: 183
Re: Voltage drop solar controller to batteries

Quote:
Originally Posted by Snerf1 View Post
Some really good comments

Basically you want to be as close and heavy as practible

Yes it may be overkill, and yes you'll never see max watts, but what is the true cost?

It's your time, money and energy dealing in the first place

The price differential between guages is peanuts compared to the other factors

Do it once, do it right, and forget about it
Another reason to install heavier gauge is that it is a form of future proofing/resisting.

The only downsides that I see initial material cost and the possibility of a more difficult install.

The trend in electric transportation is bigger wires for the main bus.
bdgWesternMass is offline   Reply With Quote
Old 12-07-2021, 10:37   #9
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,560
Re: Voltage drop solar controller to batteries

It depends a bit on your solar controller. With my Victron controllers and the other Victron gear in the system, my controllers are sensing voltage at the batteries, not at the controller. So they compensate for any voltage drop in the controller wiring. I've only got about 2.5% voltage drop anyway as wired, but it has no real impact on charging performance for my setup.
rslifkin is offline   Reply With Quote
Old 12-07-2021, 10:46   #10
Registered User

Join Date: Apr 2012
Posts: 353
Re: Voltage drop solar controller to batteries

I would use the largest wire gauge that is flexible enough to work with considering tools and space available. Connectors are a very important part of wiring a circuit.

Good luck with your vessel.
oleman is offline   Reply With Quote
Old 12-07-2021, 11:11   #11
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: Voltage drop solar controller to batteries

I would wire for a minimal voltage drop.

But the first thing I would do is install the solar controller closer to the batteries. 8-10 feet is too far in my opinion.
mitiempo is offline   Reply With Quote
Old 12-07-2021, 11:32   #12
Registered User

Join Date: Sep 2007
Location: Delray Beach, Fl
Boat: 1998 Rosborough 246 LSV
Posts: 564
Re: Voltage drop solar controller to batteries

You can place the sensor wire the controller uses on the batteries rather than close to the sensor. If you do this, the controller raises the voltage at its end of the wires to adjust for voltage drop.

In the long run, providing wire gauge for the nominal condition is best, but voltage drop in the controller to battery leg is compensated by the controller if the sensor is placed correctly.
__________________
Capt. Stuart Bell
Rosborough 246 LSV Shearwater V
stu@shearwater-sailing.com
captstu is offline   Reply With Quote
Old 12-07-2021, 11:42   #13
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: Voltage drop solar controller to batteries

Quote:
Originally Posted by captstu View Post
You can place the sensor wire the controller uses on the batteries rather than close to the sensor. If you do this, the controller raises the voltage at its end of the wires to adjust for voltage drop.

In the long run, providing wire gauge for the nominal condition is best, but voltage drop in the controller to battery leg is compensated by the controller if the sensor is placed correctly.
Many controllers do not have a separate voltage sense wire.
mitiempo is offline   Reply With Quote
Old 12-07-2021, 14:16   #14
Registered User

Join Date: Jul 2012
Location: North East USA
Boat: 1975 Tartan 41'
Posts: 1,052
Re: Voltage drop solar controller to batteries

Quote:
Originally Posted by smac999 View Post
Normally 3% for power distribution and 10% for loads.

1% would be crazy. especially when solar will never see 100% current anyways.

My Panels regularly exceed their rated max watt value. I have a pair of 265W (530W total) Kyocera brand. In the tropic sun, It was not unusual to see 550-560W mid day per the Victron blue 100V/50A MPPT controller.
zstine is offline   Reply With Quote
Old 12-07-2021, 14:23   #15
Registered User

Join Date: May 2016
Location: Corona ville, via TT
Boat: Beneteau 36CC
Posts: 34
Re: Voltage drop solar controller to batteries

Quote:
Originally Posted by captstu View Post
You can place the sensor wire the controller uses on the batteries rather than close to the sensor. If you do this, the controller raises the voltage at its end of the wires to adjust for voltage drop.

In the long run, providing wire gauge for the nominal condition is best, but voltage drop in the controller to battery leg is compensated by the controller if the sensor is placed correctly.
The first sentence leaves me unsure if your intent. Good idea if I understood better.

Isn’t the sensor wire connected to the sensor? And the other end of that node is the controller.

Apart from any consequence . . . Where else does the battery voltage sensor go ??
stevo_002 is offline   Reply With Quote
Reply

Tags
batteries, solar


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
New batteries, voltage drop pas63 Electrical: Batteries, Generators & Solar 21 21-10-2020 08:49
Big voltage drop at controller connection CurtisM Electrical: Batteries, Generators & Solar 7 17-07-2020 10:17
Solar panels - sizing wiring for voltage drop galacticair Electrical: Batteries, Generators & Solar 44 05-10-2019 14:56
Combining a diversion controller with a MPPT Solar controller GILow Electrical: Batteries, Generators & Solar 6 19-01-2016 04:45
Solar Charge Controller Voltage and Current Matching DefinitelyMe Electrical: Batteries, Generators & Solar 4 12-06-2013 08:40

Advertise Here


All times are GMT -7. The time now is 23:34.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.