Wire size

Is there any disadvantage in running two wires instead of one wire if the total amp capacity of either is the same ??
Thanks. Nick
Cat Nap3 is offline   Reply With Quote
Old 14-08-2020, 14:27   #2
Registered User

Join Date: Jan 2014
Location: Panama City FL
Boat: Island Packet 32 Keel/CB
Posts: 995
Re: Wire size

Not typically the first choice but will work fine if you are carefull/ thoughtfull.


I have run as many as 10 or 12 parallel conductors (per phase) on large underground electrical services.


Frankly
Frankly is offline   Reply With Quote
Old 14-08-2020, 15:02   #3
Moderator
 
Jammer's Avatar

Join Date: Jan 2010
Location: Minnesota
Boat: Tartan 3800
Posts: 5,090
Re: Wire size

Quote:
Originally Posted by Cat Nap3 View Post
Is there any disadvantage in running two wires instead of one wire if the total amp capacity of either is the same ??
Thanks. Nick

The problem is that if a connection comes loose all the current flows through one wire, overloading it, with no obvious signs of the failure.


It is sometimes done with much larger wires (4/0 and larger) to improve heat dissipation and to keep the wire size down to the point where it is manageable but is always an approach that has to be taken with care and awareness of the risk.
Jammer is offline   Reply With Quote
Old 15-08-2020, 16:55   #4
Registered User

Join Date: Jul 2020
Location: Virginia, USA
Boat: Hunter 340
Posts: 1,273
Re: Wire size

It can be done but understand that by ABYC standards each wire would need to be fused separately. That way if one wire fails the other wire's fuse will trip.

I would just run a single larger wire unless a larger wire is not available (often hard to find marine wire larger than 4/0) or you can't source tools (some lug crimpers max out at 2/0).
Statistical is offline   Reply With Quote
Old 16-08-2020, 07:48   #5
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,556
Re: Wire size

@Jammer post #3: +1

Per ABYC E-11, for DC circuits:
> AWG 10 or larger
> Same length
> Run in same raceway/chase
> OCPD to protect single conductor
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Reply

Tags
size


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Lofrans tigress wire size? Voltage drop/wire size calc question.. Eastward ho 24 Construction, Maintenance & Refit 30 09-06-2020 09:50
Bumping the rigging up one size (wire) do I compensate for streched old wire? Eastward ho 24 Construction, Maintenance & Refit 17 02-07-2019 13:56
110V(3 wire) panel split to 230V(3 wire) and 110V(3 wire) breakers? BrettB Electrical: Batteries, Generators & Solar 22 29-04-2019 00:30
How to Wire a Battery Isolator with a Three Wire Alternator ? bazzer Electrical: Batteries, Generators & Solar 7 05-12-2010 12:47

Advertise Here


All times are GMT -7. The time now is 15:34.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.