Cruisers Forum
 


Reply
  This discussion is proudly sponsored by:
Please support our sponsors and let them know you heard about their products on Cruisers Forums. Advertise Here
 
Thread Tools Search this Thread Rate Thread Display Modes
Old 08-10-2015, 13:57   #1
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Wiring Woes - Never Assume

As the third owner of my current boat, I occasionally run across "improvements" made by the prior owners. One recent discovery I thought might be of interest to the forum.

I have a small water-cooled heat pump in the forward cabin. I believe that it was installed by the original owner. It was tapped into the 15A Starboard Receptacles circuit, so that simultaneous use of the heat pump (roughly ten amps), and say a toaster (about seven amps) would trip the breaker. The solution, and the correct way to wire this originally, is a dedicated circuit for the heat pump. Here is what I discovered as I was installing a new feed.

Pic #1. This is the added receptacle serving the heat pump. The white cable to the left is the existing starboard 120V receptacle feed, installed by the factory, that serves an adjacent duplex receptacle. The metal handy box and the 20A receptacle were the work of the heat pump installer. Note that the round black cable entering the bottom of the handy box is the feed taken from the last factory duplex receptacle - they used the "pass-thru" terminals at the existing receptacle to piggy-back onto the existing circuit. No strain clamp used on the black cable.

Pic #2. Note the terminals used. These are spade ends, and do not have the mandatory locking tabs required for marine applications. Also the cheap insulation has cracked from crimping and should have been remade.

Pic #3. Here is the empty handy box. If you look closely, you will see the knock-out tab has not been fully removed, just bent inward. If you look back at the prior pics you will see where the sharp edge of the tab would rubbed on the black 120V cable.

Pic #4. These are the terminals used where they tapped into the existing duplex receptacle, and where they connected to the new receptacle they installed.

Pic #5. This is the cable they used to extend the existing receptacle circuit. This is 16-3 gauge. The original receptacle circuit is 12-3, with a 15A breaker. This is a weather resistant flexible cable. It is not boat cable, and the wiring is not tinned.

Pic #6. This is the re-wired receptacle, complete with new dedicated 10-3 boat cable. The bent-over knock-out tab was removed and the box rotated 180 degrees. Proper strain relief is provided at the box entry. Still doing some modifications in this area, so a "work in progress".

I was really a bit taken aback by this situation. First, I managed to ignore this situation for many years as we did not use the heat pump very often. Second, I would have expected a better installation, especially since I think that this was done by a "qualified installer". In addition to the issues addressed above, the routing of the black 120V cable was precarious with no concerns for chafe protection, the use of non-reinforced supply and return hose for the seawater supply, installation of the control wiring (line voltage in this case), routing of the condensate drain, cutting of openings in the bulkhead, etc.

In all, a very poor installation. The take away from all this - don't assume that existing is correct, and that you will frequently not get what you pay for from professional installations.
Attached Thumbnails
Click image for larger version

Name:	boat repairs,10-2015 001 (600x800).jpg
Views:	289
Size:	182.1 KB
ID:	110666   Click image for larger version

Name:	boat repairs,10-2015 004 (800x600).jpg
Views:	309
Size:	227.1 KB
ID:	110667  

Click image for larger version

Name:	boat repairs,10-2015 007 (600x800).jpg
Views:	310
Size:	226.3 KB
ID:	110668  
redsky49 is offline   Reply With Quote
Old 08-10-2015, 14:02   #2
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wiring Woes - Never Assume

Additional pics:
Attached Thumbnails
Click image for larger version

Name:	001 (800x600).jpg
Views:	285
Size:	261.8 KB
ID:	110669   Click image for larger version

Name:	boat repairs,10-2015 011 (800x600).jpg
Views:	233
Size:	245.2 KB
ID:	110670  

Click image for larger version

Name:	boat repairs,10-2015 010 (800x600).jpg
Views:	245
Size:	226.9 KB
ID:	110671  
redsky49 is offline   Reply With Quote
Old 08-10-2015, 19:19   #3
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Wiring Woes - Never Assume

I've more or less found that wiring by factory is normally pretty good. and anything done afterwards by anyone is normally suspect.
smac999 is offline   Reply With Quote
Old 08-10-2015, 19:56   #4
Moderator and Certifiable Refitter
 
Wotname's Avatar

Join Date: Jan 2008
Location: South of 43 S, Australia
Boat: C.L.O.D.
Posts: 21,034
Re: Wiring Woes - Never Assume

Yes, unfortunately a common story.
FWIW, I personally hate spade terminals, give me ring terminals any day. I get the convenience factor but that is a distant second consideration in my view.
__________________
All men dream: but not equally. Those who dream by night in the dusty recesses of their minds wake in the day to find it was vanity: but the dreamers of the day are dangereous men, for they may act their dreams with open eyes, to make it possible. T.E. Lawrence
Wotname is offline   Reply With Quote
Old 09-10-2015, 05:53   #5
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wiring Woes - Never Assume

It was not just the terminals, though the safety ground connection was either loose or disconnected at one of the receptacles.

How the cable did not chafe through at the entry to the metal handy box, I will never know. And the 16ga. wiring used to extend the existing circuit was at risk with a 15A circuit breaker.

Just be careful out there.
redsky49 is offline   Reply With Quote
Old 09-10-2015, 06:26   #6
Registered User

Join Date: Nov 2013
Location: Homeport: Fair Haven, NY
Boat: 1993 Sabre 362 #113
Posts: 615
Re: Wiring Woes - Never Assume

Why is there a metal box on a boat? Especially in a relatively exposed location?

Locking spade terminals can be used safely. These terminals have a slight bend at the end of the forks that make it harder to remove if the screw is a little loose.

The terminals should also be heat shrink terminals.

At least they used stranded wire.
Dave Lochner is offline   Reply With Quote
Old 09-10-2015, 07:36   #7
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wiring Woes - Never Assume

My personal opinion is that ring terminals should be used wherever possible. The only exceptions that come to mind are for 120V receptacles, where the receptacle terminal screws are captive and cannot be removed to allow a ring terminal.

In the pic below, you can see the receptacle terminals, the green nut at the end for the safety ground connection, and the silver screw on the side for the white neutral connection. These will not fully unscrew, and thus not permit ring terminals. This is a 15A GFCI duplex receptacle, which accounts for the depth of the receptacle.

Below the receptacle is a proper open spade terminal, with the upturned ends that reduce the chance of the terminal falling off the connecting post. This is not a heat-sealed terminal, but a standard high-quality terminal.

While heat sealed terminals are desirable, and certainly indicated in the bilge, exterior locations, etc., I am comfortable using good quality non-heat sealed terminals for most locations. The reason being that heat-sealed terminals utilize a single crimp, while the standard terminals can use a double crimp where there is an additional crimp that helps to provide strain relief. You can always slide some heat-shrink tubing over a standard double-crimped terminal, if needed.
Attached Thumbnails
Click image for larger version

Name:	001.jpg
Views:	225
Size:	415.3 KB
ID:	110709  
redsky49 is offline   Reply With Quote
Old 09-10-2015, 08:41   #8
Registered User

Join Date: Oct 2011
Location: Wherever the wind takes me
Boat: Bristol 41.1
Posts: 1,006
Re: Wiring Woes - Never Assume

Regarding heat-sealed terminals, I also include "adhesive" terminals in the same group.
redsky49 is offline   Reply With Quote
Old 09-10-2015, 08:42   #9
Registered User
 
captainwireman's Avatar

Join Date: Nov 2012
Location: Rio Dulce
Boat: Dean Oceancomber 10M
Posts: 133
Re: Wiring Woes - Never Assume

I always use an anti oxidant compound such as Noalox and have had great results in side by side experimental comparisons. The proper crimp tool for the brand you are using, the proper place to crimp, wire strip length all are important and easy to do, however, this has nothing to do with the violations here. UL laboratories standards say if the terminal is installed following the manufacturers instructions, it shall exceed the ampacity of a 90C insulation wire rating provided both are UL listed.
__________________
All that wander are not lost.
captainwireman is offline   Reply With Quote
Old 09-10-2015, 09:52   #10
Registered User

Join Date: Mar 2015
Location: Boston's North Shore
Boat: Pearson 10M
Posts: 839
Re: Wiring Woes - Never Assume

The adhesive lined, heat shrink terminals I use are double crimp terminals.
guyrj33 is offline   Reply With Quote
Old 09-10-2015, 10:01   #11
Registered User

Join Date: Mar 2014
Location: Anacortes
Boat: previous - Whitby 42 new - Goldenwave 44
Posts: 1,835
Re: Wiring Woes - Never Assume

Those type of household boxes will rust pretty quick on a boat. Should never be used. But even a plastic or wood box should use strain reliefs. In the trades we called such work "ownerizing", which sometimes was done by sub-par installers hired by the owner.

I personally will cut off many ring terminals and replace them with locking spades if it is something I may have to remove and replace more than once - like terminal blocks for bilge pumps. Nothing worse than losing the little brass or tinned screws. They can be hard to replace since they are shorter than you can commonly get at a hardware store. And they can be very difficult to put back on with a ring terminal - a high percentage of them fall off. I have NEVER had a failure from a locking spade pulling off of a terminal, but I do take extra care in putting them on every time. And compression term blocks are OK too provided the screw pushes down on a metal strip rather than the screw only capturing the wire. ABYC approved.
exMaggieDrum is offline   Reply With Quote
Old 09-10-2015, 13:45   #12
Marine Service Provider

Join Date: Dec 2011
Posts: 1,540
Re: Wiring Woes - Never Assume

Personally I don't know why the ABYC and many boat owners are so in love with, no they absolutely DEMAND that all electrical connections be by ring terminal. Ring terminals do not provide any better security than does the spade type that has the little flanges on the tips. Ring terminals are a pain in the ass because usually the screw ends up in bilge when you are fumbling (in a seaway) trying to insert the screw into the ring and maneuver the two pieces back into the circuit board or bus bar. Plus the process is slowed down substantially over just backing out the screw and inserting a spade. Lets face it, if the concern is a broken connection due to a loose screw you'll have the same problem with a loose screw and a ring terminal. In fact worse because the failure will be intermittent and more difficult to trouble shoot (again in a seaway). OK, maybe a ring will avoid a short from a dangling wire but proper looming of the wire bundle will usually prevent this.
jmschmidt is offline   Reply With Quote
Old 09-10-2015, 19:40   #13
Marine Service Provider
 
mitiempo's Avatar

Join Date: Sep 2008
Location: Victoria B.C.
Boat: Wauquiez Centurion 32
Posts: 2,875
Re: Wiring Woes - Never Assume

Quote:
Originally Posted by guyrj33 View Post
The adhesive lined, heat shrink terminals I use are double crimp terminals.
Which terminals do you use?
mitiempo is offline   Reply With Quote
Old 10-10-2015, 15:27   #14
cruiser

Join Date: Jan 2012
Location: Lake Ontario
Boat: Ontario 38 / Douglas 32 Mk II
Posts: 3,250
Re: Wiring Woes - Never Assume

Wait a minute; this changed from "I think"it was a professional installation" to "professional installation sucks" thread.

First of all, there is a big difference between "hired" and "professional" installation. The person who installed this may have been paid , but they certainly were not a professional installer.

When seeking professional installation, you must request to "see" the qualifications of the installer. Any qualified installer will pull the card out of their wallet, that indicates the organization that has certified them. If they can't produce it, they aren't "professional". Expect to pay more for professional installation. If you shop for lowest possible installed cost, you are most likely not getting a professional installation, but rather, the installation you (or the previous owner) paid for.

Ramblin Rod
About Sheen Marine
ramblinrod is offline   Reply With Quote
Old 10-10-2015, 16:48   #15
Registered User

Join Date: May 2013
Location: Oregon to Alaska
Boat: Wheeler Shipyard 83' ex USCG
Posts: 3,552
Re: Wiring Woes - Never Assume

I solder after crimping. I'm an old guy that has chased too many problems that turned out to be corrosion between the wire and terminal.
You think you have wiring problems... Try a 73 year old war built vessel that every previous owner just added and deleted circuits without removing no longer used wiring. Metal boxes held together by rust. Each owner using a method unknown to any standards. And then we can talk plumbing.
Lepke is offline   Reply With Quote
Reply

Tags
wiring


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Yanmar RPM Woes PaulM Engines and Propulsion Systems 24 12-11-2008 13:40
Yanmar 2QM15 woes SailboatJimmy Engines and Propulsion Systems 11 18-07-2008 18:08
Help! Prop shaft woes svwhisper Construction, Maintenance & Refit 14 17-11-2006 15:12
Engine idle woes-Will not idle after warm Pa La O La Engines and Propulsion Systems 5 24-09-2006 12:13

Advertise Here


All times are GMT -7. The time now is 22:12.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.