Re: 48 Volt System

Quote:
Originally Posted by GrowleyMonster View Post
I always thought the cutoff was 50v nominal.

.......
Turns out that we are both right but you are much more right than I am.

Within the US there is a split between 50v & 60v being the cutoff for DC depending on the particular code with 50v being more common. (30v AC)
Even the 60v is supposed to be dry conditions, ripple free.

The fire code says 15vDC for wet or rippled current. 6v for AC.

The International Electrotechnical Commission (IEC) and the UK put the limits for Extra-low voltage at 50v AC or 120v DC (ripple free).
__________________
Num Me Vexo?
For all of your celestial navigation questions: https://navlist.net/
A house is but a boat so poorly built and so firmly run aground no one would think to try and refloat it.
Adelie is online now   Reply With Quote
Old 11-12-2022, 12:38   #32
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,515
Re: 48 Volt System

Even the IEC has various voltages, depending on wet/dry and type of equipment. Anyone have the spec for rec boats?
team karst is offline   Reply With Quote
Old 12-12-2022, 15:28   #33
Moderator

Join Date: Feb 2010
Location: Australia
Posts: 3,611
Re: 48 Volt System

I had a 32volt system in a past boat and dropped it to 24v mostly because it was difficult to source 32 volt pumps and light globes. I seem to be sensitive to low voltage DC electric shocks possibly because I live and work in the tropics with a lot of perspiration happening and usually small cuts and abrasions. I get a real jolt from 32V , about the same from 24 and an annoying shock from 12v so for me a 48 volt system would be out of the question.
On a bit of a tangent, I just got an email from my marina office informing me that they had 2 fires over a couple of days that destroyed the very large capitainerie, first was a big fire that started in the solar array on the rooftop which was put out by the local sapeurs pompiers and then 2 days later another fire in the remaining panels that finished the roof off completely. All power was off to the building and the weather is cold. Does anyone have any experience with actual solar panel fires? And might a 48volt system be more likely to torch the array?
skipperpete is offline   Reply With Quote
Old 13-12-2022, 01:12   #34
Marine Service Provider
 
SOLAR SUPPORT's Avatar

Join Date: Aug 2010
Location: Turkiye
Boat: Bavaria Match35
Posts: 410
Re: 48 Volt System

Quote:
Originally Posted by skipperpete View Post
I had a 32volt system in a past boat and dropped it to 24v mostly because it was difficult to source 32 volt pumps and light globes. I seem to be sensitive to low voltage DC electric shocks possibly because I live and work in the tropics with a lot of perspiration happening and usually small cuts and abrasions. I get a real jolt from 32V , about the same from 24 and an annoying shock from 12v so for me a 48 volt system would be out of the question.
On a bit of a tangent, I just got an email from my marina office informing me that they had 2 fires over a couple of days that destroyed the very large capitainerie, first was a big fire that started in the solar array on the rooftop which was put out by the local sapeurs pompiers and then 2 days later another fire in the remaining panels that finished the roof off completely. All power was off to the building and the weather is cold. Does anyone have any experience with actual solar panel fires? And might a 48volt system be more likely to torch the array?
You may be sensitive to electricity. Wet ground, humidity is also known to increase the effect of warping. In terrestrial solar energy systems, the voltage between the solar panels can go up to 1000V. The voltage of the system is the level at which the regulator lowers this voltage.

Incorrectly calculated cable cross-sections or insufficient maximum voltage value of the charge regulator are the main causes of this and similar accidents. Generally, when the weather is very cold and the sun's rays are strong, the performance of the system increases very much.

The reason for this is that the cell voltage increases by a certain amount for each degree below 25°C in pv cells. When the temperature of the Pv cells rises above 25°C, the cell efficiency decreases. The Wp value written on the solar panel labels can only be approached in such very cold weather and when the sun rays are strong. In case the air temperature drops below 0C°, the cell temperature may decrease below 25°C.

If the system is designed by taking into account the possibility of experiencing these conditions, the cooling air will not cause any problems in the system. A system voltage of 48 volts is a fairly normal level for off-grid installations.
SOLAR SUPPORT is offline   Reply With Quote
Old 13-12-2022, 05:34   #35
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,515
Re: 48 Volt System

Quote:
Originally Posted by SOLAR SUPPORT View Post
... A system voltage of 48 volts is a fairly normal level for off-grid installations.
Curiously, large solar arrays are running just above 1kV.
At least the 75MW arrays I have been working around.
team karst is offline   Reply With Quote
Old 13-12-2022, 07:09   #36
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,326
Re: 48 Volt System

Quote:
Originally Posted by team karst View Post
Curiously, large solar arrays are running just above 1kV.
At least the 75MW arrays I have been working around.
I think he means battery voltage, not solar array voltage. Victron sells higher voltage units, here is one for up to 450V solar arrays but it’s 48V battery: https://www.victronenergy.com/invert...rs-smart-solar
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 13-12-2022, 11:50   #37
Registered User
 
GrowleyMonster's Avatar

Join Date: Dec 2012
Location: New Orleans
Boat: Bruce Roberts 44 Ofshore
Posts: 2,917
Re: 48 Volt System

Quote:
Originally Posted by skipperpete View Post
I had a 32volt system in a past boat and dropped it to 24v mostly because it was difficult to source 32 volt pumps and light globes. I seem to be sensitive to low voltage DC electric shocks possibly because I live and work in the tropics with a lot of perspiration happening and usually small cuts and abrasions. I get a real jolt from 32V , about the same from 24 and an annoying shock from 12v so for me a 48 volt system would be out of the question.
On a bit of a tangent, I just got an email from my marina office informing me that they had 2 fires over a couple of days that destroyed the very large capitainerie, first was a big fire that started in the solar array on the rooftop which was put out by the local sapeurs pompiers and then 2 days later another fire in the remaining panels that finished the roof off completely. All power was off to the building and the weather is cold. Does anyone have any experience with actual solar panel fires? And might a 48volt system be more likely to torch the array?
Back in the day, Gulf of Mexico shrimp boats used a 32VDC system, and some other vessels in other fisheries, too. There were a lot of electrical goods available and maybe still are, if you look to a fisherman's chandlery rather than a yacht chandlery. Chest freezers and refrigerators, potable water pumps, electric bilge pumps, lights and incandescent light bulbs, fans, (very good ones, too!) and of course 32v electric starter for the engine. Even the old Wood Freeman hunting type autopilots that ran off a flat top magnetic compass. Radar. Fathometer, especially the stylus type that uses a roll of special paper and burned the mark with the electrically charged stylus. Many AC equipped boats still use the 32VDC system for some things, particularly engine starting or for fans and lights in the house, for when the 120VAC plant is shut down. I always wondered why 32V and not 36V. I guess electric golf carts and 6V golf cart batteries weren't really a thing back in the 70's. Many trucks, buses, and heavy equipment used the 8v X 4 system,
__________________
GrowleyMonster
1979 Bruce Roberts Offshore 44, BRUTE FORCE
GrowleyMonster is offline   Reply With Quote
Old 13-12-2022, 12:48   #38
Registered User

Join Date: Apr 2007
Location: Australia
Boat: Island Packet 40
Posts: 6,501
Images: 7
Re: 48 Volt System

Quote:
Originally Posted by s/v Jedi View Post
I think he means battery voltage, not solar array voltage. Victron sells higher voltage units, here is one for up to 450V solar arrays but it’s 48V battery: https://www.victronenergy.com/invert...rs-smart-solar
My guess would be that the promoters of large solar arrays, like the power line folks before them, have discovered that running high volts instead of high amps keeps the outlays on copper down.

My prediction is that now that solar systems become more ubiquitous a greater availability of higher voltage DC storage and generation systems will come available for us boating folks to exploit.

Switch mode power conversion systems are dirt cheap and everywhere these days, hardly a transformer and diode rectifier system in sight anymore, and as lithium, with it's high current acceptance capability, replaces lead more higher voltage storage and charging systems will come into use.
__________________
Satiriker ist verboten, la conformité est obligatoire
RaymondR is offline   Reply With Quote
Old 13-12-2022, 18:59   #39
Marine Service Provider
 
SOLAR SUPPORT's Avatar

Join Date: Aug 2010
Location: Turkiye
Boat: Bavaria Match35
Posts: 410
Re: 48 Volt System

It should be noted that the cost advantages that come with increasing voltage levels of batteries, energy converters and power transmission infrastructure are not limited to the reduction in cable cross-sections.

The costs of devices such as solar charge controllers, inverters, ac-dc chargers and electrical control equipment also decrease as the system voltage increases. This is what I am trying to convey. It's definitely not a discovery.
SOLAR SUPPORT is offline   Reply With Quote
Old 14-12-2022, 00:57   #40
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,326
Re: 48 Volt System

Quote:
Originally Posted by SOLAR SUPPORT View Post
It should be noted that the cost advantages that come with increasing voltage levels of batteries, energy converters and power transmission infrastructure are not limited to the reduction in cable cross-sections.

The costs of devices such as solar charge controllers, inverters, ac-dc chargers and electrical control equipment also decrease as the system voltage increases. This is what I am trying to convey. It's definitely not a discovery.
Exactly, take a Victron MPPT controller. Those are rated for charge current output. This means that they double in power when you go from 12V to 24V and they quadruple in power when you go from 12V to 48V. And the price difference is significant!

There’s more: voltage drop allowance is a percentage of the voltage. Important circuits must stay within 3% voltage drop, which for 12V is 0.36V but for 24V it becomes 0.72V and for 48V it’s even 1.44V.
But this voltage drop is the result of the current times the resistance of the wire. This all adds up to enormous differences.

Let’s say we have a circuit with 1 Ohm resistance. How much power can we put through this circuit while staying in a 3% voltage drop?

For 12V: allowable drop is 0.36V. This means a maximum current of 0.36 / 1 = 0.36A. So the maximum load is 12 x 0.36 = 4.32W

For 24V: drop 0.72V, current 0.72A, max load 24 x 0.72 = 17.28W

For 48V: drop 1.44V, current 1.44A, max load 48 x 1.44 = 69.12W

So the difference is squared: When you double the voltage, you can supply 4 times as much power and when you go from 12V to 48V then you can supply 16 times as much power through the same circuit!
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 14-12-2022, 01:43   #41
Registered User

Join Date: Apr 2007
Location: Australia
Boat: Island Packet 40
Posts: 6,501
Images: 7
Re: 48 Volt System



Great post Jedi, got straight to the guts of the matter in easily understood terms.
__________________
Satiriker ist verboten, la conformité est obligatoire
RaymondR is offline   Reply With Quote
Old 14-12-2022, 03:40   #42
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,326
Re: 48 Volt System

Quote:
Originally Posted by RaymondR View Post


Great post Jedi, got straight to the guts of the matter in easily understood terms.
Thanks, I surprised myself keeping it so compact and easy
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 14-12-2022, 22:42   #43
Moderator
 
Adelie's Avatar

Join Date: Feb 2010
Location: La Ciudad de la Misión Didacus de Alcalá en Alta California, Virreinato de Nueva España
Boat: Cal 20
Posts: 20,825
Re: 48 Volt System

Quote:
Originally Posted by team karst View Post
Curiously, large solar arrays are running just above 1kV.

At least the 75MW arrays I have been working around.


Well when I get the point that I have 250kW or so of panels installed on my boat then I’ll have a look at going with higher voltage panels.
__________________
Num Me Vexo?
For all of your celestial navigation questions: https://navlist.net/
A house is but a boat so poorly built and so firmly run aground no one would think to try and refloat it.
Adelie is online now   Reply With Quote
Old 14-12-2022, 22:45   #44
Moderator
 
Adelie's Avatar

Join Date: Feb 2010
Location: La Ciudad de la Misión Didacus de Alcalá en Alta California, Virreinato de Nueva España
Boat: Cal 20
Posts: 20,825
Re: 48 Volt System

Quote:
Originally Posted by s/v Jedi View Post
Exactly, take a Victron MPPT controller. Those are rated for charge current output. This means that they double in power when you go from 12V to 24V and they quadruple in power when you go from 12V to 48V. And the price difference is significant!



There’s more: voltage drop allowance is a percentage of the voltage. Important circuits must stay within 3% voltage drop, which for 12V is 0.36V but for 24V it becomes 0.72V and for 48V it’s even 1.44V.

But this voltage drop is the result of the current times the resistance of the wire. This all adds up to enormous differences.



Let’s say we have a circuit with 1 Ohm resistance. How much power can we put through this circuit while staying in a 3% voltage drop?



For 12V: allowable drop is 0.36V. This means a maximum current of 0.36 / 1 = 0.36A. So the maximum load is 12 x 0.36 = 4.32W



For 24V: drop 0.72V, current 0.72A, max load 24 x 0.72 = 17.28W



For 48V: drop 1.44V, current 1.44A, max load 48 x 1.44 = 69.12W



So the difference is squared: When you double the voltage, you can supply 4 times as much power and when you go from 12V to 48V then you can supply 16 times as much power through the same circuit!


That also means that 4x the heat is being generated in smaller wires.
__________________
Num Me Vexo?
For all of your celestial navigation questions: https://navlist.net/
A house is but a boat so poorly built and so firmly run aground no one would think to try and refloat it.
Adelie is online now   Reply With Quote
Old 14-12-2022, 23:49   #45
Marine Service Provider
 
SOLAR SUPPORT's Avatar

Join Date: Aug 2010
Location: Turkiye
Boat: Bavaria Match35
Posts: 410
Re: 48 Volt System

To understand the cost reductions that come with rising system voltage, you should focus on the electrical power formula. In general terms, Power is physical work done per unit time or energy converted per unit time. P = work/time = U x I

To give an example: A small windlass needs an electric motor with 700-1000 watts in order to be able to pull the chain and the anchor attached to the end of a certain length to the boat without difficulty within the desired time. Continuing with this example: Electric power through a conductor: It is calculated with the formula P=UxI. You must supply the power required by the windlass with the voltage suitable for the structure of the motor on it.

If the motor works with 12 volts: you will find the upper value of the current to be transmitted over the cable for the power you need to transmit from the battery to the motor: 1000W/12V = 83.3A.

If the windlass has a motor suitable for 48 volts with the same power, it is possible to transmit the same power with 20.8A current by using 48 volt batteries. This means you can use a cable with a thinner cross section up to 1/4 compared to 12 volts.
SOLAR SUPPORT is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
24 volt panels for a 12 volt system docrn Electrical: Batteries, Generators & Solar 2 06-08-2020 07:45
Wiring a 24 volt windlass on a 12 volt boat Paul Lefebvre Electrical: Batteries, Generators & Solar 7 12-08-2018 16:34
Using a 24 volt genset in a 12 volt system flopster Electrical: Batteries, Generators & Solar 2 21-05-2012 18:50
direct-charging a six volt bank from a 12 volt charger Jonathan Reiter Electrical: Batteries, Generators & Solar 19 14-12-2011 06:24
6 volt vs 12 volt? mestrezat Electrical: Batteries, Generators & Solar 39 17-02-2009 23:33

Advertise Here


All times are GMT -7. The time now is 09:04.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.