Re: ABYC definition of “conduit”

Quote:
Originally Posted by wyb2 View Post



I wonder what the flame rating of my plywood bulkheads is?


Thats why u dont want flaming wiring pieces tied to it. [emoji106]
team karst is offline   Reply With Quote
Old 17-03-2023, 17:56   #17
Marine Service Provider
 
boatpoker's Avatar

Join Date: Nov 2008
Location: Port Credit, Ontario or Bahamas
Boat: Benford 38 Fantail Cruiser
Posts: 7,296
Re: ABYC definition of “conduit”

Can't you use an MRBF fuse instead ?
__________________
If you're not laughing, you're not doin' it right.
boatpoker is offline   Reply With Quote
Old 17-03-2023, 20:43   #18
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: ABYC definition of “conduit”

Quote:
Originally Posted by wyb2 View Post
Sorry about your head.

Amazon is the wild west of product descriptions. Even without knowing that polyethylene would be a problem here (I hadn’t thought about it), I would have given it a 50/50 chance of getting the material correct. You basically just have to rely on the fact that no one is setting up a separate production run for something like that to sell on Amazon.

It’s not a perfect system , I definitely got copper clad aluminum wire once when it clearly stated solid copper.

Looks like the same stuff from McMaster is listed as “polyester fabric”, and you can get it as ‘standard’, VW-1 flame rated, or NFPA 262 plenum rated. My guess is the Amazon stuff is exactly the same as the ‘standard’ stuff from Mcmaster.

You do bring up a good point. In the future I’ll probably opt for the VW-1 stuff from McMaster, looks like it’s a very small extra cost. The plenum rated stuff is a 5x the price, might take my chances and pass on that.

https://www.mcmaster.com/9196K14

I wonder what the flame rating of my plywood bulkheads is?
Better rethink that… that sleeve is not split, the stuff is h@ll, I have been haunted by it, no more for me
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 17-03-2023, 22:51   #19
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: ABYC definition of “conduit”

The temperature rating of the Alex Tech split loom is -103 to 257 F.

Electrical tape has a rating from 0 to 221 F.

For melting temperature electrical tape clearly wins at 932 F versus 446 F for he split loom.

Traditional split loom has a rating of -40 to 300 F and melts at 482 F.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 18-03-2023, 06:07   #20
Registered User
 
Fishspearit's Avatar

Join Date: Jan 2006
Location: FL
Posts: 646
Re: ABYC definition of “conduit”

Quote:
Originally Posted by boatpoker View Post
Can't you use an MRBF fuse instead ?
Because of the lower internal resistance of the lithium batteries and the size of the banks people are installing they usually require an Amperage Interrupting Current (AIC) of 25,000 amps, requiring the class T fuse.

Do they make MRBF fuses that large? I've only seen them with an AIC of 10,000 amps.
__________________
www.BestMarineSurveyor.com
Fishspearit is offline   Reply With Quote
Old 18-03-2023, 06:18   #21
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: ABYC definition of “conduit”

Quote:
Originally Posted by Fishspearit View Post
Because of the lower internal resistance of the lithium batteries and the size of the banks people are installing they usually require an Amperage Interrupting Current (AIC) of 25,000 amps, requiring the class T fuse.

Do they make MRBF fuses that large? I've only seen them with an AIC of 10,000 amps.
The class-T fuse AIC is only 20kA so also below what you require.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 18-03-2023, 06:22   #22
Registered User

Join Date: Aug 2015
Location: States - Northeast
Boat: '86 MacGregor 25
Posts: 552
Re: ABYC definition of “conduit”

Quote:
Originally Posted by s/v Jedi View Post
Better rethink that… that sleeve is not split, the stuff is h@ll, I have been haunted by it, no more for me
Crud, you’re right, I forgot that not split was even an option. That’s a no go.

Looks like the split stuff is not available with the extra fire ratings, just standard UL/CSA

https://www.mcmaster.com/1459T817

Did find this similar stuff that meets a different flame spec, ASTM E162. It’s about triple the price.

https://www.mcmaster.com/2649K531
wyb2 is offline   Reply With Quote
Old 18-03-2023, 06:28   #23
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: ABYC definition of “conduit”

Quote:
Originally Posted by wyb2 View Post
Crud, you’re right, I forgot that not split was even an option. That’s a no go.

Looks like the split stuff is not available with the extra fire ratings, just standard UL/CSA

https://www.mcmaster.com/1459T817

Did find this similar stuff that meets a different flame spec, ASTM E162. It’s about triple the price.

https://www.mcmaster.com/2649K531
But why? The first one is the same. If you want it to be better than required by ABYC (electrical tape and regular split loom will do) why would you buy more expensive plastic? Just put it in metal conduit then and use stainless steel.

I keep it to the split loom I get from Amazon (it’s sold in other places too of course) because when my wiring is melting, I don’t care about how much longer the split loom keeps holding up.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 18-03-2023, 06:48   #24
Registered User
 
Fishspearit's Avatar

Join Date: Jan 2006
Location: FL
Posts: 646
Re: ABYC definition of “conduit”

Quote:
Originally Posted by s/v Jedi View Post
The class-T fuse AIC is only 20kA so also below what you require.
You're right, 20K is the requirement.

11.10.1.2.3 For batteries or battery banks with a CCA rating greater than 2200 CCA or 500 amp hours, battery overcurrent protection shall have a minimum ampere interrupting capacity (AIC) rating as follows:
11.10.1.2.3.1 at least as great as the battery manufacturer’s short circuit rating, or
11.10.1.2.3.2 20 kA at 125 VDC or higher, if a battery manufacturer’s short circuit rating exceeds 10 kA.
__________________
www.BestMarineSurveyor.com
Fishspearit is offline   Reply With Quote
Old 18-03-2023, 07:01   #25
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: ABYC definition of “conduit”

Quote:
Originally Posted by Fishspearit View Post
You're right, 20K is the requirement.

11.10.1.2.3 For batteries or battery banks with a CCA rating greater than 2200 CCA or 500 amp hours, battery overcurrent protection shall have a minimum ampere interrupting capacity (AIC) rating as follows:
11.10.1.2.3.1 at least as great as the battery manufacturer’s short circuit rating, or
11.10.1.2.3.2 20 kA at 125 VDC or higher, if a battery manufacturer’s short circuit rating exceeds 10 kA.
Yes, so for most LFP installations that use inline BMS with ratings of a couple hundred amps, you should be able to use the MRBF fuse.

It’s clear that the ABYC guidelines are for very large traditional battery banks, not for batteries that limit current and don’t have CCA ratings.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 18-03-2023, 07:10   #26
Registered User

Join Date: Mar 2021
Location: Flagler County, FL, USA, Earth
Boat: Lagoon 380
Posts: 1,515
Re: ABYC definition of “conduit”

I use a MRBF on each house batt + terminal. This way a battery shorted cell can be mitigated in the worst case.
team karst is offline   Reply With Quote
Old 18-03-2023, 07:17   #27
Registered User

Join Date: Aug 2015
Location: States - Northeast
Boat: '86 MacGregor 25
Posts: 552
Re: ABYC definition of “conduit”

Quote:
Originally Posted by s/v Jedi View Post
But why? The first one is the same. If you want it to be better than required by ABYC (electrical tape and regular split loom will do) why would you buy more expensive plastic? Just put it in metal conduit then and use stainless steel.

I keep it to the split loom I get from Amazon (it’s sold in other places too of course) because when my wiring is melting, I don’t care about how much longer the split loom keeps holding up.
I was just providing the options I was finding that would alleviate any flame/fire concern in response to team karst's statement:

Quote:
Originally Posted by team karst View Post
🤯 Polyethylene is a poor choice for wire and any wireways. Highly flammable unless its got FR additives. PVC can be easily found with UL fire ratings.
Though I do think that the Amazon stuff is almost certainly polyester, not polyethylene, and the product description is just wrong.

But I agree with you, unless someone points to where flame rated sheath/loom is required or recommended by some standard, I'm completely fine with using the regular stuff.
wyb2 is offline   Reply With Quote
Old 18-03-2023, 08:03   #28
Registered User
 
Fishspearit's Avatar

Join Date: Jan 2006
Location: FL
Posts: 646
Re: ABYC definition of “conduit”

Quote:
Originally Posted by s/v Jedi View Post
Yes, so for most LFP installations that use inline BMS with ratings of a couple hundred amps, you should be able to use the MRBF fuse.

It’s clear that the ABYC guidelines are for very large traditional battery banks, not for batteries that limit current and don’t have CCA ratings.
They do address it in one place in the new E-13 standard:

13.7.3A BMS shall have a voltage rating not less than the system voltage and a current rating not less than the total of the ampacities of the main overcurrent protection devices immediately downstream of the battery or battery bank.

But then they also refer to the E-11 standard for overcurrent protection of all types of batteries that I posted above.

It begs the question, and I don't know the answer, do all LFP battery BMS current limiting devices have the appropriate AIC in the case of a short circuit?

I suspect the ABYC isn't quite ready to let the BMS substitute for appropriate AIC ratings for the battery bank overcurrent protection, knowing there are some pretty poor LFP batteries being sold out there.
__________________
www.BestMarineSurveyor.com
Fishspearit is offline   Reply With Quote
Old 18-03-2023, 12:19   #29
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,323
Re: ABYC definition of “conduit”

Quote:
Originally Posted by Fishspearit View Post
They do address it in one place in the new E-13 standard:

13.7.3A BMS shall have a voltage rating not less than the system voltage and a current rating not less than the total of the ampacities of the main overcurrent protection devices immediately downstream of the battery or battery bank.

But then they also refer to the E-11 standard for overcurrent protection of all types of batteries that I posted above.

It begs the question, and I don't know the answer, do all LFP battery BMS current limiting devices have the appropriate AIC in the case of a short circuit?

I suspect the ABYC isn't quite ready to let the BMS substitute for appropriate AIC ratings for the battery bank overcurrent protection, knowing there are some pretty poor LFP batteries being sold out there.
Well, yes, the BMS will interrupt a short successfully because they test this. It will be permanently damaged of course.

So the fuse… some leave it out but that’s not right either because the wiring must still be protected like for every circuit.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 18-03-2023, 12:44   #30
Writing Full-Time Since 2014
 
thinwater's Avatar

Join Date: Nov 2008
Location: Deale, MD
Boat: PDQ Altair, 32/34
Posts: 9,852
Re: ABYC definition of “conduit”

Quote:
Originally Posted by Drennan View Post
Owing to space constraints, I must place a Class-T fuse 25”-30” from my LFP house battery. ABYC code permits up to 40” through “conduit”.

Am I limited to flexible/rigid PVC & metal conduit, or might some other, and more flexible types of cable enclosure be acceptable? If not, I’ll need a much different plan B.

Thank you

Bending PVC pipe or conduit is piss easy, and I'm surprised we don't see this more often. Common practice for electricians.



Search "bending springs" on Amazon and Google how-to. Heat helps (easier and less stress on the pipe), but a few minutes with a heat gun is enough for smaller pipe. I've also used hot water, hot sand, and just placing it in a warm (not hot) oven. hard to beat if going box-to-box. Less mounting effort and support than other methods.
__________________
Gear Testing--Engineering--Sailing
https://sail-delmarva.blogspot.com/
thinwater is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Definition of a 'Boat Unit' sneuman Flotsam & Sailing Miscellany 16 15-08-2021 22:11
What does “ABYC” or “Meets ABYC Standards” on a product mean Joe Abbott Construction, Maintenance & Refit 2 11-09-2017 22:16
Definition of Coastal Crusing Sailboat? karlhead General Sailing Forum 16 01-02-2010 15:31
What is the definition of piracy? sneuman Health, Safety & Related Gear 24 23-12-2006 18:21

Advertise Here


All times are GMT -7. The time now is 01:10.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.