Old 03-02-2023, 06:54   #16
Registered User

Join Date: Jun 2019
Location: Rochester, NY
Boat: Chris Craft 381 Catalina
Posts: 6,561
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by noelex 77 View Post
There is an important factor that has not been mentioned in this thread. If you are using solar as your primary means of electrical generation the amount of day to day variation in solar insolation is of great importance in determing the required battery bank size.

In places like the Caribbean and the Mediterranean (in summer) the solar insolation is very consistent so consequently you can manage comfortably with a very small battery bank. If you want to cruise some other parts of the world, a larger battery bank is needed to average out the days and sometimes even weeks of poor conditions, with the better times.

A “solar” boat cruising Scotland in summer will need a much larger bank than an otherwise identical boat, with the same electrical needs cruising the Caribbean in winter. The average solar insolation is similar, but Scotland has a much higher variability.

On the same note, the boat in Scotland will want a larger solar installation for the same daily power usage (assuming they aren't already running as much solar as they can fit).
rslifkin is online now   Reply With Quote
Old 03-02-2023, 12:26   #17
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,325
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by noelex 77 View Post


Australia is a large country, but many areas have a reasonably high variation in solar insolation from day to day. I think 200Ahrs of lithium is insufficient to contemplate all electric cooking with a boat that is primarily dependent on solar power.

Having wintered in the southern end of Tasmania and spent numerous summers in Adelaide, I can confidently say I’ve seen the extremes of variation in solar input on offer in Australia.

The battery bank I am contemplating is not adequate for solar-only in winter in Tasmania, but I figured that’s easily fixed. Don’t do winter in Tasmania again.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 03-02-2023, 15:28   #18
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,801
Re: Battery bank sizing with Lithium

The average solar insolation primarily affects the size of the required solar panel array while the variation in solar insolation from day to day primarily affects the required battery bank size (assuming the vast majority is power is generated from solar).

Tasmania has a significantly lower solar insolation than South Australia so requires a larger solar panel array, especially in winter. The variation is also slightly greater than South Australia so the battery bank size also needs to be greater, but only slightly.

The solar panels make the energy. The batteries only store the energy made by the solar panels. The most the battery bank can do is average out the production over a limited time frame.
noelex 77 is offline   Reply With Quote
Old 03-02-2023, 16:59   #19
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,325
Re: Battery bank sizing with Lithium

Click image for larger version

Name:	IMG_0040.jpg
Views:	75
Size:	446.4 KB
ID:	271088

Actually, the main issue in Tasmania was that the sun is rather lazy down there and doesn’t bother to get out bed properly. During winter it barely makes five fingers above the horizon all day. This problem was addressed by tilting the panels. Took some monitoring, where possible I used the kedge to hold the boat steady at anchor. Tilting the panels doubled the output of the tilted panel.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 03-02-2023, 17:14   #20
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,801
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by GILow View Post
Attachment 271088
Actually, the main issue in Tasmania was that the sun is rather lazy down there and doesn’t bother to get out bed properly. During winter it barely makes five fingers above the horizon all day.
Scotland in winter is more of a challenge .

15° further from the equator hurts.

It does show how far modern solar, battery, and electrical systems have come when you can still cruise in these environments without a generator, but closer to the equator is recommended in winter for sensible people .
Attached Thumbnails
Click image for larger version

Name:	F0E21F28-9445-4007-91F8-2F4539D80F46.jpg
Views:	67
Size:	401.0 KB
ID:	271090  
noelex 77 is offline   Reply With Quote
Old 03-02-2023, 18:01   #21
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,325
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by noelex 77 View Post
Scotland in winter is more of a challenge .
.

As we say in Australia… “yeah, nah”.

I’m eyeing off the Tropic of Capricorn as a suitable cruising latitude.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 03-02-2023, 18:38   #22
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,801
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by GILow View Post

I’m eyeing off the Tropic of Capricorn as a suitable cruising latitude.
This is a great winter cruising ground.

The Whitsundays is a good starting point, but it has been many years since I have cruised these waters. The days of being able to anchor freely and in solitude at Butterfly bay or Bait Reef are sadly long gone. Compulsory moorings have filled these and many other areas.

To stay on topic, the solar conditions are quite variable in Australia even at these latitudes. Many consecutive days of heavily overcast conditions are not uncommon. If you are planning on depending on electric cooking primarily via solar, you will need a battery bank larger than 200 Ahrs.
noelex 77 is offline   Reply With Quote
Old 03-02-2023, 19:09   #23
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,325
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by noelex 77 View Post
This is a great winter cruising ground.

The Whitsundays is a good starting point, but it has been many years since I have cruised these waters. The days of being able to anchor freely and in solitude at Butterfly bay or Bait Reef are sadly long gone. Compulsory moorings have filled these and many other areas.

To stay on topic, the solar conditions are quite variable in Australia even at these latitudes. Many consecutive days of heavily overcast conditions are not uncommon. If you are planning on depending on electric cooking primarily via solar, you will need a battery bank larger than 200 Ahrs.


Yes, I’m eyeing a 280 AH kit. Eve cells and a good quality smart BMS.

But much of what we “cook” is raw and we often go days without using the stove.

As long as I have power for the coffee machine, that bit is non negotiable.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 06-02-2023, 07:11   #24
Registered User

Join Date: Oct 2020
Location: West Palm Beach
Boat: Hunter 37C
Posts: 178
Re: Battery bank sizing with Lithium

You’ve failed to mention/calculate your daily total anticipated watt draw which is the most crucial piece of information when sizing a bank.
As someone who builds battery banks for homes,boats and buses Id say thats a really small bank especially for having such high loads. Especially if you are living aboard. Most lithium installations I do are in the 15-20KW range for power hungry users which replaces 5-6 traditional lead acid batteries (size wise)
Quality lithium banks can easily handle 1C discharge but it really all depends on the BMS.
Any voltage drop will be comparatively minimal until the bank gets down to 20-30%charge. Remember lithium starts at a higher voltage and always has a linear voltage drop. Peukerts law doesn’t apply here. But you still want a large bank to hold plenty in reserve and decrease you load percentage of capacity.

It’s all about watts. The issue is you expect to run a 4 or 3 KW load on a 4.8KW battery. How often are these loads running? Is this once a day multiple times a day? Are they running when the no source of charge can happen? Have you factored in the power used by the inverter?
Anyways, I still maintain This is to undersized for such things especially in the long term unless you plan on charging it with a generator consistently. If on renewable you have to have a few days backup energy in case the sun/wind isn’t providing power. Get more batteries and don’t live life on the edge.
Sailing Ohm is offline   Reply With Quote
Old 06-02-2023, 10:25   #25
Registered User

Join Date: Nov 2017
Posts: 459
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by GILow View Post
So, on another thread I asked for ideas about running a dual 12/24 volt system for the boat. Long story short, it seems to be the way to go.

However, I am making some assumptions about the capabilities of lithium batteries that are based purely on what I've read, so I'd like to test those assumptions by running them past peoplei who are using lithium batteries on their boats.

The assumption that is most critical is about voltage drop (or sag) under load.

My anticipated peak load would be 4kW, and that would be for maybe one or two minutes at a time. Sustained loads of up to 3kW for maybe twenty minutes at most.

This would be provided at 240 v AC by a decent quality pure sine wave inverter, probably rated at 5 kW continuous and running from 24 volts.

I would expect to use a battery bank of four 12 volt 100 AH(nominal) lithium batteries, each with a 100 amp BMS. So, two parallel pairs of two batteries in series. (At this stage I am assuming I will buy a decent set of commercially made 12 volt drop ins, but I have not ruled out making my own batteries)

So, that's asking up to 80 amps per series string for short bursts and 60 amps per string for longer periods of time.

In the experience of people using lithium batteries, how well are they likely to cope with this sort of use and is voltage sag likely to be an issue, given inverters tend to be a bit fussy about this sort of thing?
Lithium batteries are both advantageous and often mishandled.
Research the negatives. Start with another car carrier caught fire over weekend in Asia tim due to lithium car batteries.
They can not be mistreated, must be properly design installed, and when age approaches replaced.
Don’t worry about all the technology’s advances- that is anticipated. Worry about overheating, thermal
Runaway, and the fact that they cook at 2500+F .
That is a great accelerator for fiberglass.
boat driver is offline   Reply With Quote
Old 06-02-2023, 10:48   #26
Registered User

Join Date: Mar 2016
Location: San Francisco
Boat: Morgan 382
Posts: 3,123
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by boat driver View Post
Lithium batteries are both advantageous and often mishandled.
Research the negatives. Start with another car carrier caught fire over weekend in Asia tim due to lithium car batteries.
They can not be mistreated, must be properly design installed, and when age approaches replaced.
Don’t worry about all the technology’s advances- that is anticipated. Worry about overheating, thermal
Runaway, and the fact that they cook at 2500+F .
That is a great accelerator for fiberglass.
You have fallen into the same trap and MANY others. Lithium Iron Phosphate, the Lithium batteries used on boats, are a totally different battery than what is used in automobiles, cell phones, hoverboards, etc. They are very difficult to get into thermal runaway. You can abuse them all you want, and it just isn't going to happen. You can even set the boat on fire, and the LFP batteries will not go into thermal runaway, or even contribute to the fire. Subject them to a direct short, and they will burn, but at a lower temp than what is required to set wood on fire, and remove the short and they self extinguish. In pretty much every way, LFP are safer than lead-acid (which can explode) and some have made the comparison that they are safer than a 2x4.

Unfortunately, people hear "Lithium" and that is all they hear.
__________________
-Warren
wholybee is offline   Reply With Quote
Old 06-02-2023, 11:33   #27
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,325
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by Sailing Ohm View Post
You’ve failed to mention/calculate your daily total anticipated watt draw which is the most crucial piece of information when sizing a bank.
As someone who builds battery banks for homes,boats and buses Id say thats a really small bank especially for having such high loads. Especially if you are living aboard. Most lithium installations I do are in the 15-20KW range for power hungry users which replaces 5-6 traditional lead acid batteries (size wise)
Quality lithium banks can easily handle 1C discharge but it really all depends on the BMS.
Any voltage drop will be comparatively minimal until the bank gets down to 20-30%charge. Remember lithium starts at a higher voltage and always has a linear voltage drop. Peukerts law doesn’t apply here. But you still want a large bank to hold plenty in reserve and decrease you load percentage of capacity.

It’s all about watts. The issue is you expect to run a 4 or 3 KW load on a 4.8KW battery. How often are these loads running? Is this once a day multiple times a day? Are they running when the no source of charge can happen? Have you factored in the power used by the inverter?
Anyways, I still maintain This is to undersized for such things especially in the long term unless you plan on charging it with a generator consistently. If on renewable you have to have a few days backup energy in case the sun/wind isn’t providing power. Get more batteries and don’t live life on the edge.


No, I’ve done my numbers. After five years on board I know a lot more about my power needs than you. The bank size is more than adequate.

My question was about sizing for peak load, not storage capacity. But thanks for the patronising lecture on wattage, it made me laugh.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 06-02-2023, 11:35   #28
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,325
Battery bank sizing with Lithium

Quote:
Originally Posted by boat driver View Post
Lithium batteries are both advantageous and often mishandled.

Research the negatives. Start with another car carrier caught fire over weekend in Asia tim due to lithium car batteries.

They can not be mistreated, must be properly design installed, and when age approaches replaced.

Don’t worry about all the technology’s advances- that is anticipated. Worry about overheating, thermal

Runaway, and the fact that they cook at 2500+F .

That is a great accelerator for fiberglass.


Save it for another thread, my question was about voltage sag under peak load.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 06-02-2023, 13:56   #29
Registered User

Join Date: May 2021
Posts: 223
Re: Battery bank sizing with Lithium

Quote:
Originally Posted by rslifkin View Post
On the same note, the boat in Scotland will want a larger solar installation for the same daily power usage (assuming they aren't already running as much solar as they can fit).

On another note, I've been told that no true Scotsman would turn on his water heater, as showering in warm water only makes you soft and weak and an easy pushover for lean, hungry barbarian invaders.
Cwens is offline   Reply With Quote
Old 11-02-2023, 04:37   #30
Registered User

Join Date: Mar 2011
Location: Puerto Escondido/Loreto, Mexico
Boat: Ocean Alexander tri cabin 52'
Posts: 307
Re: Battery bank sizing with Lithium

Where is Oz?
MVDarlin is offline   Reply With Quote
Reply

Tags
battery, lithium


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
DC negative connections when adding a new lithium bank to an existing LA bank andrzej0nl1ne Electrical: Batteries, Generators & Solar 5 29-08-2022 18:18
Lithium battery bank as auxiliary starter battery Deividas Electrical: Batteries, Generators & Solar 36 24-07-2022 15:46
Lithium Portable Lithium Battery Pack Charging zboss Electrical: Batteries, Generators & Solar 2 01-05-2020 10:33
AC battery charger for AGM start battery and Lithium bank exMaggieDrum Electrical: Batteries, Generators & Solar 75 19-06-2018 14:35
Battery Bank Interconnect Cable Sizing? Catamount Electrical: Batteries, Generators & Solar 7 10-04-2010 08:03

Advertise Here


All times are GMT -7. The time now is 05:27.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.