Old 22-04-2024, 01:08   #31
Marine Service Provider

Join Date: Jun 2015
Location: Croatia
Boat: neptunus 56 fly
Posts: 1,400
Images: 2
Re: BMS capacity vs fuse size

Quote:
Originally Posted by GILow View Post
Yes, true.


I’ve decided to go with a 350 amp Class T for the main lithium bank and manufacturer spec rated ANLs for each of the inverters, I.e 200 and 100 amp respectively. At least if the surge capacity does blow the ANL fuses they are cheap to replace.

If my boat is subsequently replaced by a smouldering crater in the water then I’ll know I was wrong.
You are from Australia.
dont go with T-fuse this is american, australia use different fuse i think germany NH fuse is comon in Australia,easy to buy in australia .
ANL fuse i dont recommended nobody. for you better use RGS4b fuse. and far better mccb circuit breaker.
again fuse is short protection and overcurent protection for cable burn or melt.

far,far better MCCB circuit breaker with overcurent protection to safe brake overcurent to 200000 A
MCCB disadvantage is price like T-fuse but 6-10x more expensive
NH fuse,RGS4b,..

T-fuse,NH fuse,RGS4b is primitive fuse from ww2
MCCB is light year in front
https://eshop.se.com/in/blog/post/mc...%20flexibility.
more is offline   Reply With Quote
Old 22-04-2024, 03:00   #32
Marine Service Provider

Join Date: Jun 2015
Location: Croatia
Boat: neptunus 56 fly
Posts: 1,400
Images: 2
Re: BMS capacity vs fuse size

and watch this video. all this info is for all short protection and overload protection. i must go
more is offline   Reply With Quote
Old 22-04-2024, 03:55   #33
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,431
Re: BMS capacity vs fuse size

Quote:
Originally Posted by GILow View Post
Yes, true.

But my main question, which got lost in all the cable lectures, was about the fuse types as well as their current ratings.

And reasonably enough, the inverter manufacturer does not venture into the area of ANL vs Class T etc. And the inverter manufacturer doesn’t really consider how it their component interacts with other devices.

I think the scope of my original question is beyond this forum in the sense that is is bespoke to my setup. My hope was that others might have a similar setup and be able to share whether there were any pitfalls with all these variable power ratings.

I’ve decided to go with a 350 amp Class T for the main lithium bank and manufacturer spec rated ANLs for each of the inverters, I.e 200 and 100 amp respectively. At least if the surge capacity does blow the ANL fuses they are cheap to replace.

If my boat is subsequently replaced by a smouldering crater in the water then I’ll know I was wrong.
There is guidance on maximum current interrupt rating in ABYC. I have attached the relevant sections below
Attached Thumbnails
Click image for larger version

Name:	IMG_5451.jpg
Views:	31
Size:	175.5 KB
ID:	289125   Click image for larger version

Name:	IMG_5452.jpg
Views:	48
Size:	301.3 KB
ID:	289126  

__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 22-04-2024, 05:40   #34
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,356
Re: BMS capacity vs fuse size

Quote:
Originally Posted by s/v Jedi View Post
There is guidance on maximum current interrupt rating in ABYC. I have attached the relevant sections below
Not sure HOW relevant. It explicitly states it is not applicable for lithium.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 22-04-2024, 15:26   #35
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,431
Re: BMS capacity vs fuse size

Quote:
Originally Posted by GILow View Post
Not sure HOW relevant. It explicitly states it is not applicable for lithium.
Which means you need to follow the big battery guidance, i.e. 100 times the 20hr capacity rating when the short circuit current Isc is unknown.

So in your case 304 * 100 = 30kA
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Old 22-04-2024, 17:11   #36
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,356
Re: BMS capacity vs fuse size

Quote:
Originally Posted by s/v Jedi View Post
Which means you need to follow the big battery guidance, i.e. 100 times the 20hr capacity rating when the short circuit current Isc is unknown.

So in your case 304 * 100 = 30kA
Gotcha.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 22-04-2024, 20:02   #37
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,548
Re: BMS capacity vs fuse size

Quote:
Originally Posted by GILow View Post
Oh my goodness. For someon lecturing me on needing to read his posts, with lots and lots of exclamation points too, you clearly didn’t read my posts.
I read your post
CaptainRivet is offline   Reply With Quote
Old 22-04-2024, 20:11   #38
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,356
Re: BMS capacity vs fuse size

Quote:
Originally Posted by CaptainRivet View Post
I read your post
Not very well. You missed this bit...

"However, the intention is not to run them both at once but instead to choose the inverter most suited to the needs at the time."

So the maximum load would be 4kW, not 6kW.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 22-04-2024, 20:42   #39
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,548
Re: BMS capacity vs fuse size

Quote:
Originally Posted by GILow View Post
Not very well. You missed this bit...

"However, the intention is not to run them both at once but instead to choose the inverter most suited to the needs at the time."

So the maximum load would be 4kW, not 6kW.
The intension is but how you makes sure that doesn't happen...intension is not enough when eg the admiral still can put both on...we had exactly that in another thread and suddenly 400A hit the system...

And the answers are all in my first post:
Single 200A JK BMS with 150A class T with min 30kA or NH fuse which has 80kA anyhow.
You decided for the wrong 350A class T....poor JK BMS will be dead soon...the 150A class T would have saved it.
Your solution is a 2nd battery with a 2nd BMS parallel. Then you can run your 4kw alone ot as well as 2kw.

Inverters use ANL Fuse speced for the cable used to connect the inverter, if giandel specs 100 and 200A that is ok for the cable they suggest too. For cable and therfor fuse the surge is irrelevant.
The Giandel have thier own internal fuses that protect the inverters, the fuse is for the cable.
CaptainRivet is offline   Reply With Quote
Old 22-04-2024, 21:19   #40
Registered User
 
GILow's Avatar

Join Date: Sep 2008
Location: On the boat, somewhere in Australia.
Boat: Swanson 42 & Kelly Peterson 44
Posts: 9,356
Re: BMS capacity vs fuse size

Quote:
Originally Posted by CaptainRivet View Post
The intension is but how you makes sure that doesn't happen...intension is not enough when eg the admiral still can put both on...we had exactly that in another thread and suddenly 400A hit the system...

And the answers are all in my first post:
Single 200A JK BMS with 150A class T with min 30kA or NH fuse which has 80kA anyhow.
You decided for the wrong 350A class T....poor JK BMS will be dead soon...the 150A class T would have saved it.
Your solution is a 2nd battery with a 2nd BMS parallel. Then you can run your 4kw alone ot as well as 2kw.

Inverters use ANL Fuse speced for the cable used to connect the inverter, if giandel specs 100 and 200A that is ok for the cable they suggest too. For cable and therfor fuse the surge is irrelevant.
The Giandel have thier own internal fuses that protect the inverters, the fuse is for the cable.
Mate, we know how to manage power. I'm happy with our setup.
__________________
Refitting… again.
GILow is offline   Reply With Quote
Old 23-04-2024, 03:35   #41
Registered User

Join Date: Oct 2021
Location: On my boat
Posts: 170
Re: BMS capacity vs fuse size

Quote:
Originally Posted by CaptainRivet View Post
The intension is but how you makes sure that doesn't happen...intension is not enough when eg the admiral still can put both on...we had exactly that in another thread and suddenly 400A hit the system...

And the answers are all in my first post:
Single 200A JK BMS with 150A class T with min 30kA or NH fuse which has 80kA anyhow.
You decided for the wrong 350A class T....poor JK BMS will be dead soon...the 150A class T would have saved it.
Your solution is a 2nd battery with a 2nd BMS parallel. Then you can run your 4kw alone ot as well as 2kw.

Inverters use ANL Fuse speced for the cable used to connect the inverter, if giandel specs 100 and 200A that is ok for the cable they suggest too. For cable and therfor fuse the surge is irrelevant.
The Giandel have thier own internal fuses that protect the inverters, the fuse is for the cable.
Not hard if you install a rotary changeover switch
Wandering1 is offline   Reply With Quote
Old 23-04-2024, 04:15   #42
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,548
Re: BMS capacity vs fuse size

Quote:
Originally Posted by Wandering1 View Post
Not hard if you install a rotary changeover switch
Perfect to kill BMS...
Seperate switches with pre charge resistor as i also posted in my first answer, to keep inrush current low to protect BMS. 4kw inverter has some beefy capacitors that are waiting to kill mosfets...same reason victron states not to use battery protects, which are smart SSR containing mosfets as disconnect switch for inverters.
Well with a 350A class T i expect the BMS dead soon, we can start posting bets when...
@GILow do you have a gauge 4/0 or 150mm2 battery cable or how did you spec for 350A fuse rating????
CaptainRivet is offline   Reply With Quote
Old 23-04-2024, 04:43   #43
Registered User

Join Date: Oct 2021
Location: On my boat
Posts: 170
Re: BMS capacity vs fuse size

Quote:
Originally Posted by CaptainRivet View Post
Perfect to kill BMS...
Seperate switches with pre charge resistor as i also posted in my first answer, to keep inrush current low to protect BMS. 4kw inverter has some beefy capacitors that are waiting to kill mosfets...same reason victron states not to use battery protects, which are smart SSR containing mosfets as disconnect switch for inverters.
Well with a 350A class T i expect the BMS dead soon, we can start posting bets when...
@GILow do you have a gauge 4/0 or 150mm2 battery cable or how did you spec for 350A fuse rating????
Are you assuming that somebody would use the rotary switch under load?
Wandering1 is offline   Reply With Quote
Old 23-04-2024, 06:42   #44
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,548
Re: BMS capacity vs fuse size

Quote:
Originally Posted by Wandering1 View Post
Are you assuming that somebody would use the rotary switch under load?
sure if 1000% wanna kill BMS, do it under load from 2kw to 4kw inverter…and please switch directly one to two, so you blow min 1 inverter too.
And by the way how do you sync both inverter to run it parallel…only Victron, Mastervolt (maybe Xantex?) and Studer can work parallel or use power assist staging them syncs the inverters, Giandel not. You can only run completly seperate circuits in AC and switchboards.

Just do it from off…best first 4kw inverter then 2kw inverter and you wanna switch to 2nd inverter. please do a video showing the 200A JK BMS while you doing it, so everyone can watch what’s happening then… and book the resulting cost under lessons learned..some just need to learn it the hard way….

I suggest for his own sake and his ship OP should post circuit diagram containing AC and DC so we can see how all is set up incl fuses etc. also to avoid misunderstanding.
We just wanna help here…
CaptainRivet is offline   Reply With Quote
Old 23-04-2024, 06:46   #45
Registered User

Join Date: Oct 2021
Location: On my boat
Posts: 170
Re: BMS capacity vs fuse size

Quote:
Originally Posted by CaptainRivet View Post
Just do it in standby…best first 4kw inverter then 2kw inverter and please do a video showing the 200A JK BMS while you doing it…
I asked you a reasonable question and you respond with that!
Wandering1 is offline   Reply With Quote
Reply

Tags
size


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
LFP+BMS+Ultracapacitors? or (2)(LFP+BMS)? rgleason Lithium Power Systems 128 03-01-2024 02:55
Why do we need a fuse when we have a BMS to break in a catastrophic event. Fuss Lithium Power Systems 69 05-05-2023 21:03
Fuse Panel and stuck fuse holder Tmacmi Electrical: Batteries, Generators & Solar 0 14-04-2020 09:14
Fuse Panel and stuck fuse holder Tmacmi Construction, Maintenance & Refit 0 13-04-2020 06:35
LiFe(Y)PO4 BMS Dessign - good reading for DIY BMS developers CatNewBee Lithium Power Systems 10 20-09-2018 00:15

Advertise Here


All times are GMT -7. The time now is 19:02.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.