Re: LFP Available Short Circuit Current

Quote:
Originally Posted by tanglewood View Post
No, I think this is PRECISELY what the AIC rating is. It's the maximum current at which the fuse can open, and STAY open. I think the discussion has been going in circles for nearly a month because you are working to an incorrect definition of what AIC means/is.
Please show me where it stands that AIC means disconnect AND STAY disconnected at AIC and for how for how long?

Then please explain also how can you have an AIC of 20kA rating staying disonnected with 7mm gap between the 2 metal parts (thats what a 400A Class T has) when physically around 8-10kA is already enough to arc up to 3cm when this 8-10kA is present for more then 3sec ionizing the air. Thats pure physics, nothing else .That this is the case you can see at the Winston test how the current of a shortened cell is builing up.
CaptainRivet is offline   Reply With Quote
Old 21-05-2023, 17:44   #62
Registered User

Join Date: Feb 2015
Posts: 1,241
Images: 1
Re: LFP Available Short Circuit Current

Quote:
Originally Posted by CaptainRivet View Post
Please show me where it stands that AIC means disconnect AND STAY disconnected at AIC and for how for how long?

Then please explain also how can you have an AIC of 20kA rating staying disonnected with 7mm gap between the 2 metal parts (thats what a 400A Class T has) when physically around 8-10kA is already enough to arc up to 3cm when this 8-10kA is present for more then 3sec ionizing the air. Thats pure physics, nothing else .That this is the case you can see at the Winston test how the current of a shortened cell is builing up.

This is from Eaton, but Schneider and others say the same thing:


AIC (kAIC) applies to protective interrupting devices such as circuit breakers and fuses. The unit of measure for AIC is Amps RMS Symmetrical. This figure, which is typically in range of 5000 to 200,000 amps, describes the maximum fault current that the protective device can clear safely, without welding closed or causing damage to equipment or personnel.


If current continues to flow, then I think it's pretty clear that it hasn't cleared the fault.


As for arcing, air gaps, and other construction properties that allow these to work, I don't know. But if there is some other standardized parameter that you are talking about, what is it?
__________________
www.MVTanglewood.com
tanglewood is offline   Reply With Quote
Old 21-05-2023, 23:20   #63
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,235
Re: LFP Available Short Circuit Current

Quote:
Originally Posted by CaptainRivet View Post
Please show me where it stands that AIC means disconnect AND STAY disconnected at AIC and for how for how long?

Then please explain also how can you have an AIC of 20kA rating staying disonnected with 7mm gap between the 2 metal parts (thats what a 400A Class T has) when physically around 8-10kA is already enough to arc up to 3cm when this 8-10kA is present for more then 3sec ionizing the air. Thats pure physics, nothing else .That this is the case you can see at the Winston test how the current of a shortened cell is builing up.
It is physically impossible to have a “8-10kA current present” when there is no circuit it flows through. A current is there or not there; it can not build up to make a jump.

You only have a current when a circuit is completed. To jump a gap, you need voltage.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is offline   Reply With Quote
Reply

Tags
current


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electrical current when circuit is off crayiii Electrical: Batteries, Generators & Solar 48 17-03-2022 14:48
LFP house to LFP starter charging Drennan Lithium Power Systems 0 27-09-2021 09:59
Alternator with LFP: How to calculate current? Ulstue Lithium Power Systems 26 30-04-2021 07:09
Double pole circuit breakers for each circuit ayates Electrical: Batteries, Generators & Solar 9 04-01-2021 10:34
solar, 100w, open circuit ok, short circuit ok, no power to battery NotreVoyage Electrical: Batteries, Generators & Solar 3 26-04-2016 22:41

Advertise Here


All times are GMT -7. The time now is 04:12.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.