Old 29-10-2017, 16:06   #5941
Registered User

Join Date: Sep 2017
Posts: 33
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

SoC readings taken from BEP battery monitor. It's not perfect, but it's repeatable. My test methodology can be thought of as pretty reasonable for an 'absolute' test, but perfectly acceptable as a 'relative' test. I could have used the DataTaker to also measure voltage drop across the main boat shunt resistor and used it to calculate amps drawn and Ah used, but just decided to keep it simple as time was limited and I had other things to do (like get wind controller set correctly).

Why did I use about double the typical Amp draw? Time constraints, that's why. In any case, it's still a fractional draw on a battery type that has minimal Puekerts effect, so not hugely relevant. A C20 rate would be more relevant if performing this test on a LA battery, sure.

Test took 7:54. I'm aware this is a little less than my estimated 8:15 based on current draw.
200MPH is offline   Reply With Quote
Old 29-10-2017, 17:49   #5942
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

And in fact at 12.1V you still had significantly more AH capacity left at the end, your actual capacity may be a lot higher than rated.

Or the BEP meter is off?
john61ct is offline   Reply With Quote
Old 31-10-2017, 14:03   #5943
Registered User

Join Date: Sep 2015
Posts: 445
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by 200MPH View Post
It also verifies the 12.8V low voltage buzzer alarm I've setup so that everyone who uses the yacht gets a notification at around 80% discharged.
One of the challenges with a single low voltage buzzer is that, if your system has typical wiring and internal cell resistance, you'll find that the voltage drop due to load can really throw off the effective SOC at the threshold.

For example, on my LFP pack with a 500W load, 51.2V also means I have somewhere around 20% SOC. But with a 10kW load, a reading of 51.2V means there is more than twice the capacity left.

Since the SOC gauge is really there for convenience and (the rest of the) non-technical users, it would be nice if there were an implementation that would adapt based on the load, a defined Ri, and perhaps a defined hysteresis interval.

And as long as we're dreaming... it would also be nice if the inverter would allow its LV cutouts and warnings to shift based upon load, too. Unless I want to set a low cutout that would damage the cells under low loads, I end up with one that is breached too easily at 10 or 15% SOC under very high loads. And of course a bunch of spurious LV warnings and emails before that.
nebster is offline   Reply With Quote
Old 01-11-2017, 06:43   #5944
Registered User

Join Date: Sep 2017
Posts: 33
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Nebster - correct about wanting/needing a low voltage alarm/cutoff that varies with load. Would be easy to achieve with a simple logic lookup table. Wonder if any existing battery monitors incorporate such functionality? If not then I guess you could make your own with a little effort.

For instance, my low voltage alarm briefly sounds when starting the diesel engines. Yet the Lead starter battery is 100% OK. It's all a compromise I guess! Ultimately I'm happy knowing what's going on with the yacht systems and can deal with alarm systems that are not 'inteligent' or 'learning'. Not sure the other partners in the yacht are, so I've set the sytems to be conservative for that reason.
200MPH is offline   Reply With Quote
Old 01-11-2017, 06:57   #5945
Registered User
 
OceanPlanet's Avatar

Join Date: May 2009
Location: Woolwich, Maine
Boat: Mull 42-cold molded NZ 1970
Posts: 512
Send a message via Skype™ to OceanPlanet
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by 200MPH View Post
So, I did a full discharge test on the new battery pack last night so I would have a baseline test I can consistently repeat every year to see how much the battery is degrading.

Battery: 300Ah Winston 4 cells to make 12.8V.

Charged to 13.8V setting on Victron charger, using dedicated voltage sensing function it has. Bulk charge 90A, then absorbtion for 1 hr (it can't terminate on trailing amps), let battery settle for a few minutes while I fooled around getting the wind controller set correctly, then start a constant discharge overnight. Load was a radiant heater run through the Victron AC inverter. 465W or thereabouts (35A at 13.2 V). No other loads during discharge test.
Victron low voltage inverter cut set to 12.0V. Capacity during discharge monitored using the yacht BEP battery monitor, Pukerts set to 1.03 as an estimate.
Battery voltage logged from the pack terminals (pack level, not individual cells) using a DataTaker DT85, logged every 15 seconds. Before you ask, it is a professional quality precision logger, that is way, way overkill for this application. So I'd trust the results of it pretty much over every other reading. We calibrate our fleet of these instruments regularly against national standards.

The short version of the results are:

Volts (mV) SoC % Capacity (Ah)
13473 100 300
13197 90 270
13159 80 240
13078 70 210
13029 60 180
13000 50 150
12958 40 120
12874 30 90
12774 20 60
12640 10 30
12131 0 0

Interestingly the Victron cut the AC inverter a bit above 12V (12.131V) within a minute of the BEP SoC reading reaching 0 Ah. Coincidence of course, couldn't have planned it that way.

I don't know how to post a picture of the graph otherwise I would.

The above values are very, very similar to those published by MaineSail from a test done last year on a 400Ah Winston battery discharged at 30A, although that test went down to 11.6V and hence showed more than 100% nominal capacity.

What does all this prove? Not much, but a good baseline for me and just thought I'd share it. It also verifies the 12.8V low voltage buzzer alarm I've setup so that everyone who uses the yacht gets a notification at around 80% discharged. The actual DC and AC voltage cut levels are set lower than this of course, but I figure we don't need to discharge it to less than 20% SoC in normal use.
Excellent test, well done!
__________________
Twice around was enough for me...
Now I just help others prep for ocean trips...
www.oceanplanetenergy.com
[SIGPIC][/SIGPIC]
OceanPlanet is offline   Reply With Quote
Old 13-12-2017, 08:03   #5946
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Balmar asking for VR ideas

http://www.cruisersforum.com/forums/...d.php?t=194917
john61ct is offline   Reply With Quote
Old 19-12-2017, 11:56   #5947
Registered User
 
Recy's Avatar

Join Date: Apr 2015
Location: Stockholm, Sweden
Boat: Sun Odyssey 45.2
Posts: 155
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

I have a 360 Ah 12v LFP bank and a Victron Multi Plus 12/1600/70 charger.
When charging there is only max 47A even if I start charge below 12V.
I had expected the charge to be close to 70A under these conditions.
What can be reason?
Recy is offline   Reply With Quote
Old 19-12-2017, 11:58   #5948
Registered User

Join Date: Jun 2007
Location: SW Florida
Boat: FP Belize, 43' - Dot Dun
Posts: 3,823
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Recy View Post
I have a 360 Ah 12v LFP bank and a Victron Multi Plus 12/1600/70 charger.

When charging there is only max 47A even if I start charge below 12V.

I had expected the charge to be close to 70A under these conditions.

What can be reason?


House is using 23A ??
DotDun is offline   Reply With Quote
Old 19-12-2017, 12:21   #5949
Registered User
 
Recy's Avatar

Join Date: Apr 2015
Location: Stockholm, Sweden
Boat: Sun Odyssey 45.2
Posts: 155
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

No there is no load on the batteries they are only being charged.
Recy is offline   Reply With Quote
Old 19-12-2017, 12:31   #5950
Registered User

Join Date: Jun 2008
Posts: 316
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Recy View Post
I have a 360 Ah 12v LFP bank and a Victron Multi Plus 12/1600/70 charger.
When charging there is only max 47A even if I start charge below 12V.
I had expected the charge to be close to 70A under these conditions.
What can be reason?
The charge current of the MultiPlus is limited to 75% of the max by default. You may need a computer and their USB adapter to change it. I don't see it mentioned in the 12/1600/70 manual as configurable by DIP switches.

https://www.victronenergy.com/upload...L-FR-DE-ES.pdf
JayH is offline   Reply With Quote
Old 19-12-2017, 13:01   #5951
Registered User
 
Recy's Avatar

Join Date: Apr 2015
Location: Stockholm, Sweden
Boat: Sun Odyssey 45.2
Posts: 155
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

I have the usb adapter so I was able to change it to 70.
Do you know the reason for setting it to 75% by default?
Recy is offline   Reply With Quote
Old 19-12-2017, 14:00   #5952
Registered User

Join Date: Jun 2008
Posts: 316
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Recy View Post
I have the usb adapter so I was able to change it to 70.
Do you know the reason for setting it to 75% by default?
The manual for the 24/3000/70 says this:

Quote:
5.5.1.3 Battery charge current limitation (default setting 75%) For maximum battery life, a charge current of 10% to 20% of the capacity in Ah should be applied. Example: optimal charge current of a 24V/500Ah battery bank: 50A to 100A. The temperature sensor supplied automatically adjusts the charge voltage to the battery temperature. If faster charging – and a subsequent higher current – is required: - The temperature sensor supplied should always be fitted, since fast charging can lead to a considerable temperature rise of the battery bank. The charge voltage will be adapted to the higher temperature (i.e. lowered) by means of the temperature sensor. - The bulk charge time will sometimes be so short that a fixed absorption time would be more satisfactory (‘fixed’ absorption time, see ds5, step 2).
JayH is offline   Reply With Quote
Old 19-12-2017, 16:12   #5953
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Recy View Post
I have a 360 Ah 12v LFP bank and a Victron Multi Plus 12/1600/70 charger.
When charging there is only max 47A even if I start charge below 12V.
I had expected the charge to be close to 70A under these conditions.
What can be reason?
What are you using to measure amps, and at what point(s) are you measuring?
Have you checked on the Victron's charge profile programming? Any derating options set there?

Link to your cells?

Is there a BMS or other devices between the bare cells and the charger outputs?

Link to those too please.

Have you checked for resistance in the wiring, make sure properly crimped terminations, no loose connections etc ?

What do you mean by "start charge below 12V"? Is that the resting voltage of the cells when isolated in a depleted state?

Have you ever allowed the cells to go dead flat?
john61ct is offline   Reply With Quote
Old 19-12-2017, 18:09   #5954
Marine Service Provider

Join Date: May 2011
Location: Cruising Mexico Currently
Boat: Gulfstar 50
Posts: 1,980
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Measure the voltage under charge at the battery terminals and then again at the output of the charger.

I am assuming that the chargers voltage sense is internal. Thus, if you have too small of gauge wire from the charger to the bank the voltage drop across the charge cables will not give the charger proper feedback.

I use 2/0 charge cables to my LiFePO4 bank and even then I see this happening with my Xantrex inverter/charger.
evm1024 is offline   Reply With Quote
Old 20-12-2017, 02:48   #5955
Registered User
 
Recy's Avatar

Join Date: Apr 2015
Location: Stockholm, Sweden
Boat: Sun Odyssey 45.2
Posts: 155
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

The problem is solved.
Victronic sets the charge level by default to 75%.
I have now reset it to 70A so now there is full charge.
Thanks for all your advices.
Recy is offline   Reply With Quote
Reply

Tags
battery, grass, lifepo4, LiFePO4 Batteries, sailing


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 13:31.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.