Old 13-09-2019, 00:40   #6946
Registered User
 
CatNewBee's Avatar

Join Date: Aug 2017
Boat: Lagoon 400S2
Posts: 3,755
Images: 3
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by john61ct View Post
That is only relevant for charge sources that are both user-adjustable, and VE.Bus compatible.

Not all such Victron devices are.

Even SPI, I2C or CAN would be fine, but I suspect no adjustment is possible with this particular unit.

I'd be very happy to be proven wrong.
You are wrong. Most controllers have only a (sometimes optional) BT interface.
__________________
Lagoon 400S2 refit for cruising: LiFeYPO4, solar and electric galley...
CatNewBee is offline   Reply With Quote
Old 13-09-2019, 01:14   #6947
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,571
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by newhaul View Post
Upon further reading of the specifications page , I would personally have to recommend that you don't use this with Lfp for long term storage .

Lfp don't like being fully charged.

Storage Mode: Less maintenance and aging when the battery is not in use The storage mode kicks in whenever the battery has not been subjected to discharge during 24 hours. In the storage mode float voltage is reduced to 2,2 V/cell (13,2 V for a 12 V battery) to minimise gassing and corrosion of the positive plates. Once a week the voltage is raised back to the absorption level to ‘equalize’ the battery. This feature prevents stratification of the electrolyte and sulphation, a major cause of early battery failure.

Because of this statement in there
Once a week the voltage is raised back to the absorption level to ‘equalize’ the battery

And then there is this part
Also charges Li-ion (LiFePO₄) batteries LiFePO₄ batteries are charged with a simple bulk – absorption – float algorithm.

And the Lfp float is 13.5v or fairly close to what is normally considered by most of us using Lfp to be considered fully charged .

And we all know Lfp hate being kept fully charged for long periods.



OK, so how do we solve this? We've discussed it a lot, but I'm not sure we've come up with anything clear cut.


* At the dock, if I'm not on board I shut down the systems and isolate the batteries and shut down the charger. Disconnect shore power.



* Anticipating not being on board, I stop charging short of a full charge, by forcing the charger into float (can be done with any Victron charger/inverter even without the Venus control)



* If I'm on board and using some systems, I stop charging short of a full charge, by forcing the charger into float.


* Anticipating leaving for a long sailing passage, I will fully charge the battery by forcing the charger into bulk.




So far so good -- right?


But what about if I am using Power Boost? I think that's the big fly in the ointment. I don't see how I could hold the battery at partial SOC and be using Power Boost, because after heavy loads from the inverter, the whole normal charge routine will start, and I would have to manually force to float every time at the desired state of charge.


Unless perhaps I could get an automatic "force to float" command into the charger/inverter from the BMS. Based on selecting a target SOC.


That would be pretty simple to implement, but Batrium doesn't have any such function that I was able to find. I can imagine a toggle switch on the instrument panel for selecting 50% vs 90% or whatever target SOC, based on which the BMS would command the Multiplus to go over to float at the selected target.



Ideas?
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is online now   Reply With Quote
Old 13-09-2019, 06:29   #6948
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Dockhead View Post
OK, so how do we solve this? We've discussed it a lot, but I'm not sure we've come up with anything clear cut.


* At the dock, if I'm not on board I shut down the systems and isolate the batteries and shut down the charger. Disconnect shore power.



* Anticipating not being on board, I stop charging short of a full charge, by forcing the charger into float (can be done with any Victron charger/inverter even without the Venus control)



* If I'm on board and using some systems, I stop charging short of a full charge, by forcing the charger into float.


* Anticipating leaving for a long sailing passage, I will fully charge the battery by forcing the charger into bulk.




So far so good -- right?


But what about if I am using Power Boost? I think that's the big fly in the ointment. I don't see how I could hold the battery at partial SOC and be using Power Boost, because after heavy loads from the inverter, the whole normal charge routine will start, and I would have to manually force to float every time at the desired state of charge.


Unless perhaps I could get an automatic "force to float" command into the charger/inverter from the BMS. Based on selecting a target SOC.


That would be pretty simple to implement, but Batrium doesn't have any such function that I was able to find. I can imagine a toggle switch on the instrument panel for selecting 50% vs 90% or whatever target SOC, based on which the BMS would command the Multiplus to go over to float at the selected target.



Ideas?
no ideas as far as using a mains charger in those scenarios .

The only time I use a mains charger is the day I am leaving to top up with during my preps to get underway.

I have 2 settings normally used on my solar . ( considering all of the various discissions on the forum about Lfp )

new regime will be me on boat using systems charge to 13.8v ( one day a month to 14.45v top balancing) forstaling memory issues )

not onboard set controller to 12.8v ( I'm onboard 75% of the time so rarely set here ) .

Seems like it would work good . We shall see in a year or so .
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 13-09-2019, 07:23   #6949
Registered User
 
CatNewBee's Avatar

Join Date: Aug 2017
Boat: Lagoon 400S2
Posts: 3,755
Images: 3
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Dockhead View Post
OK, so how do we solve this? We've discussed it a lot, but I'm not sure we've come up with anything clear cut.


* At the dock, if I'm not on board I shut down the systems and isolate the batteries and shut down the charger. Disconnect shore power.



* Anticipating not being on board, I stop charging short of a full charge, by forcing the charger into float (can be done with any Victron charger/inverter even without the Venus control)



* If I'm on board and using some systems, I stop charging short of a full charge, by forcing the charger into float.


* Anticipating leaving for a long sailing passage, I will fully charge the battery by forcing the charger into bulk.




So far so good -- right?


But what about if I am using Power Boost? I think that's the big fly in the ointment. I don't see how I could hold the battery at partial SOC and be using Power Boost, because after heavy loads from the inverter, the whole normal charge routine will start, and I would have to manually force to float every time at the desired state of charge.


Unless perhaps I could get an automatic "force to float" command into the charger/inverter from the BMS. Based on selecting a target SOC.


That would be pretty simple to implement, but Batrium doesn't have any such function that I was able to find. I can imagine a toggle switch on the instrument panel for selecting 50% vs 90% or whatever target SOC, based on which the BMS would command the Multiplus to go over to float at the selected target.



Ideas?
Use the programmable inputs of the multiplus along with a macro. You can do it by a switch, connected one side to the input of the multiplus, the other to a BMV, that delivers the SOC. Switching off, the Multiplus will run the normal settings and receive no cut signal, switched on, the bmv will trigger float or stop charge above the set value.

I would use a BMV that oversees all charging sources and loads instead of the multiplus internal SOC calcullation
__________________
Lagoon 400S2 refit for cruising: LiFeYPO4, solar and electric galley...
CatNewBee is offline   Reply With Quote
Old 13-09-2019, 07:29   #6950
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,571
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by CatNewBee View Post
Use the programmable inputs of the multiplus along with a macro. You can do it by a switch, connected one side to the input of the multiplus, the other to a BMV, that delivers the SOC, switching off, the the multiplus will run the normal settings, switched on, the bmv will trigger float or stop charge above the set value.

OK, so the programmable input on the Multiplus can be programmed to "force float"?


If so, then I see how this could work. Either the BMS OR the battery monitor could then be programmed to give a signal at a set SOC level, and this could be used to force the Multiplus into float.


If you want it to run the normal program, just interrupt that signal with a toggle switch.


Did I understand that correctly? If so, that sounds like the solution! That would work even when using Power Boost! Thanks!
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is online now   Reply With Quote
Old 13-09-2019, 07:49   #6951
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by CatNewBee View Post
You are wrong. Most controllers have only a (sometimes optional) BT interface.
Sorry? don't catch your intent here.

Are you still thinking this charger does allow user-custom settings?
john61ct is offline   Reply With Quote
Old 13-09-2019, 07:57   #6952
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Dockhead View Post
But what about if I am using Power Boost? I think that's the big fly in the ointment
Yes, combi inverter/chargers interfere with the usual LFP design modes, cannot separate loads buss from charge buss.

Keeping both Absorb and Float settings turned down to Storage voltage levels is one possibility.

A lead Reserve bank lets you completely isolate the LFP Main house, even if it is very small. Or Starter(s) can serve that function.

Or just let the LFP bank sit at Full and take the longevity hit, could well allow you to get a decade or more and KISS.
john61ct is offline   Reply With Quote
Old 13-09-2019, 08:19   #6953
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,571
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by john61ct View Post
Yes, combi inverter/chargers interfere with the usual LFP design modes, cannot separate loads buss from charge buss.

Keeping both Absorb and Float settings turned down to Storage voltage levels is one possibility.

A lead Reserve bank lets you completely isolate the LFP Main house, even if it is very small. Or Starter(s) can serve that function.

Or just let the LFP bank sit at Full and take the longevity hit, could well allow you to get a decade or more and KISS.

A parallel lead bank wouldn't solve this problem at all.



You want your inverter connected to the lithium, not the lead bank.


Power Boost, by the way, murders lead batteries. It's how I ruined my latest set of lead batteries . Every time you draw power from the batts for power boost, a whole new charging cycle is initiated. Lead batteries don't like to see absorption voltages over and over again when they are more or less fully charged -- it corrodes the positive plates.


No, I think CatNewBee's solution is perfect. The Victron battery monitors have a programmable relay for SOC (intended for automatic starting of generators, but easily adaptable for this). So I can get a signal to force float at any given programmed SOC, from a 700-series battery monitor. Now to figure out how to program the Multiplus.
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is online now   Reply With Quote
Old 13-09-2019, 08:32   #6954
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Dockhead View Post
A parallel lead bank wouldn't solve this problem at all.
I was only talking about when you want to keep the LFP in "storage mode", their energy not required for cycling purposes, the shore power being sufficient to carry the loads.

Of course never mind, if using the (very versatile) programmable relay feature of the BMV-712 works better for you, many ways to skin the various cats to suit different use cases.
john61ct is offline   Reply With Quote
Old 13-09-2019, 08:45   #6955
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,571
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by john61ct View Post
I was only talking about when you want to keep the LFP in "storage mode", their energy not required for cycling purposes, the shore power being sufficient to carry the loads.

Of course never mind, if using the (very versatile) programmable relay feature of the BMV-712 works better for you, many ways to skin the various cats to suit different use cases.

I don't think you understood the issue then -- it's being dockside with shorepower but using Power Boost.


This is a VERY COMMON situation in Northern Europe where shorepower may be as little as 6 amps (i've even seen 4 amps).


If you're hooked up for a long time, you won't want to hold the battery at 100% SOC, but you will be drawing from the battery to supplement shore power as often as every few minutes. An auxiliary lead bank will not solve this.



It would be really useful to be able to limit the charging to some set % SOC. I can get an output from a 7-series Victron battery mon, but still don't see how to use that signal in the Multiplus -- maybe CatNewBee has some ideas.
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is online now   Reply With Quote
Old 13-09-2019, 08:58   #6956
Marine Service Provider

Join Date: May 2011
Location: Cruising Mexico Currently
Boat: Gulfstar 50
Posts: 1,980
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

I've been looking at the (non victron) lithium assistant. No experience with it yet. It appears to set the multiplus to accept charge on / charge off signals from a BMS or another source for that matter.

IT is called the Two signal BMS support assistant...

https://www.victronenergy.com/upload...uattros-EN.pdf
evm1024 is offline   Reply With Quote
Old 13-09-2019, 09:06   #6957
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by john61ct View Post
Yes, combi inverter/chargers interfere with the usual LFP design modes, cannot separate loads buss from charge buss.

Keeping both Absorb and Float settings turned down to Storage voltage levels is one possibility.

A lead Reserve bank lets you completely isolate the LFP Main house, even if it is very small. Or Starter(s) can serve that function.

Or just let the LFP bank sit at Full and take the longevity hit, could well allow you to get a decade or more and KISS.
So now your advocating for a lead reserve / starter
What had changed since
http://www.cruisersforum.com/forums/...ml#post2972968
About 4 pages back when you were not wanting lead based in the system at all is this new charger the reason for the change in theoretical battery setups ?
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 13-09-2019, 09:08   #6958
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,571
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by evm1024 View Post
I've been looking at the (non victron) lithium assistant. No experience with it yet. It appears to set the multiplus to accept charge on / charge off signals from a BMS or another source for that matter.

IT is called the Two signal BMS support assistant...

https://www.victronenergy.com/upload...uattros-EN.pdf



Bingo!


That's it exactly, and must be what CatNewBee was talking about.


It's not in my Multiplus manual -- guess it's a feature of newer ones, than mine:



Click image for larger version

Name:	Capture.PNG
Views:	125
Size:	96.6 KB
ID:	199806
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is online now   Reply With Quote
Old 13-09-2019, 09:15   #6959
cruiser

Join Date: Jan 2017
Boat: Retired from CF
Posts: 13,317
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Yes I did not infer that Power Boost, or even any particular vendor's gear were essential elements to the current discussion.

Quote:
Originally Posted by Dockhead View Post
It would be really useful to be able to limit the charging to some set % SOC.
It may seem crude, but just setting Absorb and Float voltages to between 13.1 - 13.2V, 3.27 - 3.31Vpc should accomplish that.

By default start testing at the low end. If the Ah draw required from the bank is high, then stick to the higher end.
john61ct is offline   Reply With Quote
Old 13-09-2019, 09:21   #6960
Moderator
 
Dockhead's Avatar

Cruisers Forum Supporter

Join Date: Mar 2009
Location: Denmark (Winter), Cruising North Sea and Baltic (Summer)
Boat: Cutter-Rigged Moody 54
Posts: 34,571
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by john61ct View Post
Yes I did not infer that Power Boost, or even any particular vendor's gear were essential elements to the current discussion.

Well, I mentioned Power Boost in every post. It's a fundamental function on my boat, and probably any other boat with any gear which will do this (Victron, Magnum, Mastervolt, etc.). This is an exceptionally useful function.



Quote:
Originally Posted by john61ct View Post
It may seem crude, but just setting Absorb and Float voltages to between 13.1 - 13.2V, 3.27 - 3.31Vpc should accomplish that.

By default start testing at the low end. If the Ah draw required from the bank is high, then stick to the higher end.

It does seem crude, and this does not achieve the described target functionality.


First of all, I am skeptical whether with lithium you can hit some partial SOC, whether it's 50% or whatever, or anything close, with voltage setting alone, although I will defer to those with experience (I have none).


But secondly, I am after a SWITCH to allow me to select target SOC with on flip. I don't want to go into a programming menu and reprogram charging voltages every time I change regime.
__________________
"You sea! I resign myself to you also . . . . I guess what you mean,
I behold from the beach your crooked inviting fingers,
I believe you refuse to go back without feeling of me;
We must have a turn together . . . . I undress . . . . hurry me out of sight of the land,
Cushion me soft . . . . rock me in billowy drowse,
Dash me with amorous wet . . . . I can repay you."
Walt Whitman
Dockhead is online now   Reply With Quote
Reply

Tags
battery, grass, lifepo4, LiFePO4 Batteries, sailing


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 05:43.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.