With an external BMS it shuts off the field wire to the regulator.

Batteries with internal BMS have no place on a boat in my opinion.
mitiempo is offline   Reply With Quote
Old 12-06-2022, 11:28   #7592
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by mitiempo View Post
With an external BMS it shuts off the field wire to the regulator.

Batteries with internal BMS have no place on a boat in my opinion.
I actually put in a manual switch. There may bs times when I need all my hp for moving the boat . Alternators under heavy load can require as much as 4 hp for a fully loaded 100 zmp alternator. My 75 amp takes 2hp and with a total of 12 well 2 is significant.
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 12-06-2022, 11:52   #7593
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

@mitiempo #7591
Quote:
With an external BMS it shuts off the field wire to the regulator.
It is actually considered better to shut off B+ to the regulator rather than the field. Same result but gentler on the regulator.

Quote:
Batteries with internal BMS have no place on a boat in my opinion.
I absolutely agree. I made a business decision not to install internal BMS LFP batteries on boats unless they communicate their status outside of their box.

I will, and have, installed internal BMS LFP batteries in RV's. My position is if the LFP system in an RV has a problem that opens a contactor, the operator can pull over to the side of the road and sort it out. On a boat, in the middle of the Gulf Stream, not so much.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 12-06-2022, 12:59   #7594
Registered User

Join Date: Jul 2020
Location: Malmo Sweden
Boat: Regina 43
Posts: 655
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Charlie J. Many thanks for this reply. You have confirmed my suspitions against internal BMS’ for house banks aboard. Having already had a near miss with a electrical fire aboard in the middle of the North Sea due to an alternator pumping amps into a dead battery I’m a safety first kind of guy with electrical these days.
Na Mara is offline   Reply With Quote
Old 12-06-2022, 13:26   #7595
Registered User
 
sparrowhawk1's Avatar

Join Date: Jan 2014
Location: Miami Beach Fl
Boat: Colombia Cc 11.8
Posts: 1,758
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

The way I've heard most people charging with an alternator is to keep your starting battery lead and have a battery to battery charger for your lifepo4 house. By choosing a charger that has a lower output than your alternator you will also extend the life of the alternator so it doesn't run full blast the whole time.
sparrowhawk1 is offline   Reply With Quote
Old 12-06-2022, 13:48   #7596
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by sparrowhawk1 View Post
The way I've heard most people charging with an alternator is to keep your starting battery lead and have a battery to battery charger for your lifepo4 house. By choosing a charger that has a lower output than your alternator you will also extend the life of the alternator so it doesn't run full blast the whole time.
Yep seems to be general consensus. Also 20% seems to be the best derating of alternator output. For high output but also alternator longevity.
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 12-06-2022, 13:55   #7597
Registered User

Join Date: Jul 2020
Location: Malmo Sweden
Boat: Regina 43
Posts: 655
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Trouble with doing it that way is that it’s really inefficient. I’m planing 800Ah house bank charged off a 250A genmaxx alternator limited to 190A. This will make best use of my limited use of my overpowered engine. But the starter AGM is 110Ah so it can only charge at 50A continuous assuming standard acceptance rates. That would mean I could at most have one 30A DC-DC charger. It would take over a day to charge the house bank like that. I could double up on starter batteries to get 100A charging capacity on them and then I could run 3 parallel 30A DC DC chargers but then it would still take 7-8 hrs to charge from 80% discharge. Moreover those chargers run very hot meaning significant inefficiencies over and above excessive fuel burn.

It’s much more efficient to charge the LFP batteries off a high output alt and DCDC charge the engine battery off the LFPs. But to do that safely requires an external BMS that can talk to the regulator which is a more complex and expensive install.
Na Mara is offline   Reply With Quote
Old 12-06-2022, 14:04   #7598
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Na Mara View Post
Trouble with doing it that way is that it’s really inefficient. I’m planing 800Ah house bank charged off a 250A genmaxx alternator limited to 190A. This will make best use of my limited use of my overpowered engine. But the starter AGM is 110Ah so it can only charge at 50A continuous assuming standard acceptance rates. That would mean I could at most have one 30A DC-DC charger. It would take over a day to charge the house bank like that. I could double up on starter batteries to get 100A charging capacity on them and then I could run 3 parallel 30A DC DC chargers but then it would still take 7-8 hrs to charge from 80% discharge. Moreover those chargers run very hot meaning significant inefficiencies over and above excessive fuel burn.

It’s much more efficient to charge the LFP batteries off a high output alt and DCDC charge the engine battery off the LFPs. But to do that safely requires an external BMS that can talk to the regulator which is a more complex and expensive install.
Ok but your numbers don't make any sense to me a start battery will be recharged from the start of the iron wind within a few minutes But sounds what you need is an external programmable regulator to the lfp and a simple 10 or 20 amp b2b to recharge the 5 to 7 amps required to start your engine .
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 12-06-2022, 14:05   #7599
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

@Na_Mara #7597
Quote:
requires an external BMS that can talk to the regulator which is a more complex and expensive install.
Also, much, much safer. All that is needed is the BMS ATC signal to a relay in the B+ supply to the regulator. When ATC is rescinded by the BMS, the relay opens and alternator safely stops alternating. The Victron SolidSwitch 104 is purpose built for this application.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 12-06-2022, 14:11   #7600
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Regarding starting an engine. Here is a thought experiment:
Assume:
> It takes 1000A to start your engine.
> The engine must spin for 3.6 seconds before it starts

The amp-hr used to start this mythical engine is: 1,000A x 3.6 seconds = 3,600Asec/3,600sec/hr = 1Ahr.

A Group 31 is about 110Ahrs+/-; 50% rule yields 55Ahrs usable. Point of this is that, yes we want to start our engines when needed, but I submit most boats could go an entire boating season with a good starting battery and never have to charge it.
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 12-06-2022, 14:18   #7601
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Anybody that is installing an LFP bank had best check their alternator temperature carefully with an IR gun at a minimum to ensure that when it is charging a depleted bank its highest temperature is <100C. I am in the business and I use a FLIR IR camera for this purpose and to document the alternator's thermal performance under load.

Some YouTube videos that are germane:
>>
__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 12-06-2022, 14:18   #7602
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by CharlieJ View Post
Regarding starting an engine. Here is a thought experiment:
Assume:
> It takes 1000A to start your engine.
> The engine must spin for 3.6 seconds before it starts

The amp-hr used to start this mythical engine is: 1,000A x 3.6 seconds = 3,600Asec/3,600sec/hr = 1Ahr.

A Group 31 is about 110Ahrs+/-; 50% rule yields 55Ahrs usable. Point of this is that, yes we want to start our engines when needed, but I submit most boats could go an entire boating season with a good starting battery and never have to charge it.
You forgot the electric lift pump and glow plug draws
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Old 12-06-2022, 14:21   #7603
Commercial Member
 
CharlieJ's Avatar

Cruisers Forum Supporter

Join Date: Dec 2008
Location: St. Petersburg, FL
Boat: Gulfstar Long Range Trawler; 53'; BearBoat
Posts: 1,558
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

newhaul #7602

__________________
Charlie Johnson
ABYC Master Technician
JTB Marine Corporation
"The Devil is in the details and so is salvation."
CharlieJ is offline   Reply With Quote
Old 12-06-2022, 14:55   #7604
Registered User
 
Simi 60's Avatar

Join Date: Jun 2016
Location: Australia
Boat: Milkraft 60 ex trawler
Posts: 4,653
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by newhaul View Post
You forgot the electric lift pump and glow plug draws
And for some, anchor windlass
Simi 60 is offline   Reply With Quote
Old 12-06-2022, 15:05   #7605
Senior Cruiser
 
newhaul's Avatar

Cruisers Forum Supporter

Join Date: Sep 2014
Location: puget sound washington
Boat: 1968 Islander bahama 24 hull 182, 1963 columbia 29 defender. hull # 60
Posts: 12,245
Re: LiFePO4 Batteries: Discussion Thread for Those Using Them as House Banks

Quote:
Originally Posted by Simi 60 View Post
And for some, anchor windlass
Most don't run the windlass off of the starting battery. Mine is manual. Most have a dedicated battery and hoist after the engines are already running .
__________________
Non illigitamus carborundum
newhaul is offline   Reply With Quote
Reply

Tags
battery, grass, lifepo4, LiFePO4 Batteries, sailing


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Advertise Here


All times are GMT -7. The time now is 09:45.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.