Old 16-09-2022, 02:05   #16
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by krid2000 View Post
Thanks, I hadn't thought of that!



Dirk


The nature of TVS diode protection is that it’s not that sharp a cutoff, depending on how much current is in the spike.

Typically automotive qualified electronics is designed to handle 40v spikes and recently 60v is often norm.

Hence then a 18-24V rated TVS will typically then protect that.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 16-09-2022, 06:30   #17
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,236
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by krid2000 View Post
What do you think of "Alternator Protectors" instead (such as this one) that buffer the voltage spike in case of a BMS cutoff?

Thanks
Dirk
Alternator protectors are not meant to be used instead of BMS control of charge sources but in addition to.

Think of them like fire extinguishers: to turn off the flame of a propane burner, you close the gas valve. Only when that doesn’t work you use a fire extinguisher. It is a measure to be used as a backup.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 18-09-2022, 18:49   #18
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,236
Re: LiFePO4 reference diagram, 12V version

I added a version for big alternator charging here: https://www.cruisersforum.com/forums...on-268766.html
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 21-09-2022, 09:52   #19
00X
Registered User

Join Date: Aug 2022
Posts: 31
Re: LiFePO4 reference diagram, 12V version

Would I be correct saying that a setup like this is about as close as you can get to what would be called a 'drop-in' lithium system?

Meaning that the alternator is not something that needs to be modified since its charging is sent to the start bank?

Im trying to come up to speed on lithium systems as i'd like to convert my house bank some day in the near future. I've been looking into the Lithionics batteries with internal BMS. If i directed all my charge sources to the lithium house bank 'except' the alternator, which would only charge the isolated start batteries, it seems, if im understanding things correctly, i could leave the alternator stock with no modifications?

My idea would be to use a 1,2,B switch in some manner so that i could run loads from either house or start bank temporarily in an emergency, but that there would be no connection between the battery banks initially. This would be changed in the future, the idea would be to get a basic lithium base system installed as my house bank because my current AGM house bank is getting near its end, and then deal with and modify the system in the future as time allows to allow alternator charging of the lithium bank.
00X is offline   Reply With Quote
Old 21-09-2022, 09:59   #20
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,236
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by 00X View Post
Would I be correct saying that a setup like this is about as close as you can get to what would be called a 'drop-in' lithium system?

Meaning that the alternator is not something that needs to be modified since its charging is sent to the start bank?

Im trying to come up to speed on lithium systems as i'd like to convert my house bank some day in the near future. I've been looking into the Lithionics batteries with internal BMS. If i directed all my charge sources to the lithium house bank 'except' the alternator, which would only charge the isolated start batteries, it seems, if im understanding things correctly, i could leave the alternator stock with no modifications?
Correct. In the diagram there’s also a dc-dc converter which takes power from the alternator to charge the lithium batteries. With one such converter, it takes up to 30A from the alternator, which some standard ones may have trouble with (overheating) which may require to configure the converter to reduce that amperage until you see a steady temperature that isn’t too hot. This is easy with the SmartOrion converters.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 21-09-2022, 10:20   #21
00X
Registered User

Join Date: Aug 2022
Posts: 31
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by s/v Jedi View Post
Correct. In the diagram there’s also a dc-dc converter which takes power from the alternator to charge the lithium batteries. With one such converter, it takes up to 30A from the alternator, which some standard ones may have trouble with (overheating) which may require to configure the converter to reduce that amperage until you see a steady temperature that isn’t too hot. This is easy with the SmartOrion converters.
Interesting. Thanks for taking the time to post these diagrams and feedback.
00X is offline   Reply With Quote
Old 26-09-2022, 02:03   #22
Registered User
 
krid2000's Avatar

Join Date: Sep 2020
Boat: Tartan 40
Posts: 132
Re: LiFePO4 reference diagram, 12V version

Is there any specific reason to go with the bi-stable battery switch that adds the need for additional custom logic to drive it from the REC BMS, instead of just going with the NO contactor sold by REC?

I understand that the NO contactor uses some (low, negligible?) power during normal operation, while the bi-stable ML-RBS doesn't. Anything else I'm missing?

Thanks!
Dirk
krid2000 is offline   Reply With Quote
Old 26-09-2022, 02:31   #23
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by krid2000 View Post
Is there any specific reason to go with the bi-stable battery switch that adds the need for additional custom logic to drive it from the REC BMS, instead of just going with the NO contactor sold by REC?



I understand that the NO contactor uses some (low, negligible?) power during normal operation, while the bi-stable ML-RBS doesn't. Anything else I'm missing?



Thanks!

Dirk


In fact bistable relays are not fail safe and shouldn’t be used for bms cuttout in my opinion. Use the TE connectivity relay with the economiser option ( sold by many ) this consumes 130mA holding current only. It will open if the bms dies
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Old 26-09-2022, 04:14   #24
Moderator
 
noelex 77's Avatar

Cruisers Forum Supporter

Join Date: Jul 2007
Boat: Bestevaer.
Posts: 14,801
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by krid2000 View Post
I understand that the NO contactor uses some (low, negligible?) power during normal operation, while the bi-stable ML-RBS doesn't. Anything else I'm missing?

Thanks!
Dirk
These economiser relays/solenoids are excellent. They have a smaller form factor than the Blueseas latching solenoids and they seem very reliable. I have been using two as a remote switch for the inverter. This is a tough application involving multiple switch cycles with high currents and they have been totally reliable.

Their consumption is small but not negligible. As Goboatingnow points out, expect about 130ma or 3 Ahrs (@12v) per relay if the coil is permanently energised.
noelex 77 is online now   Reply With Quote
Old 26-09-2022, 06:06   #25
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,236
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by krid2000 View Post
Is there any specific reason to go with the bi-stable battery switch that adds the need for additional custom logic to drive it from the REC BMS, instead of just going with the NO contactor sold by REC?

I understand that the NO contactor uses some (low, negligible?) power during normal operation, while the bi-stable ML-RBS doesn't. Anything else I'm missing?

Thanks!
Dirk
You don’t need to buy additional logic from REC when you buy the compatible model RBS. For 12V it is the 7713: https://www.bluesea.com/products/771...-Release_-_12V

These are normally open like any solenoid but because they are latching, they only need 10% of the power to keep open.
They still function as a manual battery switch as well.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 26-09-2022, 06:11   #26
Registered User
 
krid2000's Avatar

Join Date: Sep 2020
Boat: Tartan 40
Posts: 132
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by s/v Jedi View Post
You don’t need to buy additional logic from REC when you buy the compatible model RBS. For 12V it is the 7713: https://www.bluesea.com/products/771...-Release_-_12V

These are normally open like any solenoid but because they are latching, they only need 10% of the power to keep open.
They still function as a manual battery switch as well.
Thanks, this looks interesting! These use 13mA when ON as opposed to the 130mA of the TE contactors. I just realized that's your referenced 10% :-)

I like that it has a manual LOCKED OFF switch.
krid2000 is offline   Reply With Quote
Old 26-09-2022, 07:00   #27
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,236
Re: LiFePO4 reference diagram, 12V version

Keep in mind that any component can fail. I see the argument that when the BMS fails, the non-latching solenoid will open, protecting the battery. This argument is brought like if it is an advantage. Now imagine a battery that is 100% okay and the BMS fails, taking this good battery offline preventing you from hauling anchor during a violent squall that threatens to throw you on the rocks. The supposedly safety mechanism has turned into a disaster.

With the RBS, you can manually switch it off.

Likewise, instead of the BMS failing, the solenoid can fail. Imagine a massive power draw from the inverter and the BMS detects low voltage in cells and triggers LVC, but the solenoid contacts fuse together as they try to interrupt the large current.

For MOSFET based BMS’s it’s the same because MOSFETs normally fail in a shorted state.

Dealing with failing technology is a thing to consider. I like the RBS because it allows manual operation, even a lockout function, as well as remote switch and remote control by microcontroller. I also like the switch indicator signal that allows the microcontroller to learn the switch state. You can write a software routine that closes or opens the switch intelligently, instead of just sending a signal and pray it works.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 27-09-2022, 17:41   #28
Registered User
 
rgleason's Avatar

Join Date: Mar 2012
Location: Boston, MA
Boat: 1981 Bristol 32 Sloop
Posts: 17,711
Images: 2
Re: LiFePO4 reference diagram, 12V version

Nick, I believe your list of advantages for the RBS manual switch when dealing with failures, also apply for the single 1-Off-2 Switch in diagram I recently posted , check out the descriptions on the second page SK-2.



Quote:
Originally Posted by s/v Jedi View Post
Keep in mind that any component can fail. I see the argument that when the BMS fails, the non-latching solenoid will open, protecting the battery. This argument is brought like if it is an advantage. Now imagine a battery that is 100% okay and the BMS fails, taking this good battery offline preventing you from hauling anchor during a violent squall that threatens to throw you on the rocks. The supposedly safety mechanism has turned into a disaster.

With the RBS, you can manually switch it off.

Likewise, instead of the BMS failing, the solenoid can fail. Imagine a massive power draw from the inverter and the BMS detects low voltage in cells and triggers LVC, but the solenoid contacts fuse together as they try to interrupt the large current.

For MOSFET based BMS’s it’s the same because MOSFETs normally fail in a shorted state.

Dealing with failing technology is a thing to consider. I like the RBS because it allows manual operation, even a lockout function, as well as remote switch and remote control by microcontroller. I also like the switch indicator signal that allows the microcontroller to learn the switch state. You can write a software routine that closes or opens the switch intelligently, instead of just sending a signal and pray it works.
rgleason is offline   Reply With Quote
Old 29-09-2022, 00:22   #29
Registered User
 
fxykty's Avatar

Join Date: Apr 2016
Location: Indonesia
Boat: Outremer 55L
Posts: 3,936
Re: LiFePO4 reference diagram, 12V version

Here is our system design for our upcoming conversion from one 12V 700Ah LFYP battery to two parallel 12V 700Ah LFYP batteries. This was done in Visio and I haven’t bothered with pretty pictures.
Click image for larger version

Name:	IMG_1664436020.498478.jpg
Views:	154
Size:	452.3 KB
ID:	265107

Here is the BMS relay wiring for the new system. Current wiring is very similar, except of course not two BMS and no battery disconnect currently (only the two HVC and LVC disconnects, which when combined completely disconnect the battery).
Click image for larger version

Name:	IMG_1664436034.589505.jpg
Views:	106
Size:	434.2 KB
ID:	265108
fxykty is offline   Reply With Quote
Old 29-09-2022, 07:12   #30
Nearly an old salt
 
goboatingnow's Avatar

Join Date: Jun 2009
Location: Lefkas Marina ,Greece
Boat: Bavaria 36
Posts: 22,801
Images: 3
Re: LiFePO4 reference diagram, 12V version

Quote:
Originally Posted by krid2000 View Post
Thanks, this looks interesting! These use 13mA when ON as opposed to the 130mA of the TE contactors. I just realized that's your referenced 10% :-)



I like that it has a manual LOCKED OFF switch.


Te $50 and 130mA is hard to beat simple one wire coil circuit. Completely fail safe.

The ML series is a manual battery disconnect it’s not a safety device imho.
__________________
Interested in smart boat technology, networking and all things tech
goboatingnow is offline   Reply With Quote
Reply

Tags
enc, lifepo4


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
LiFePO4 reference diagram s/v Jedi Lithium Power Systems 121 24-09-2022 10:05
Jedi AC power diagram: updated version 3 s/v Jedi Electrical: Batteries, Generators & Solar 40 29-08-2022 17:31
Review Lifepo4 installation diagram please CaptainRivet Lithium Power Systems 4 09-03-2022 12:36
Is there a LiFePO4 Reference Guide out there yet? jimp1234 Lithium Power Systems 0 14-06-2020 17:10
wiring diagram for autohelm3000... NOT the ST version! centerline General Sailing Forum 3 07-01-2015 09:16

Advertise Here


All times are GMT -7. The time now is 06:59.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.