Old 05-01-2023, 09:28   #1
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,287
Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Hi all,
Supporting a buddy boat as shore support during Atlantic crossing and he is facing a strange behavior from the Victron DC to dc 12 30/30 and cannot charge his Lithium via it.
He has 420AH of Gel as starter/backup house where the Victron DC2DC is connected charging 560AH lithium. 90A mastervolt alternator on a Volvo d2-55 with regulator for gel, charging gel.
When he switches on the Orion, the Orion starts and then over course from 2 min the input voltage drops from 14,78V to 10V.
If he puts a 30A load (not the dc2dc) on the gel the gel stays stable.
When he puts the 30A from the input voltage on DC2DC dropes to 10v over 2 min and dc to dc switches off. But measuring at the gel it’s stable.
What can that be?
CaptainRivet is offline   Reply With Quote
Old 05-01-2023, 09:34   #2
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,235
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Quote:
Originally Posted by CaptainRivet View Post
Hi all,
Supporting a buddy boat as shore support during Atlantic crossing and he is facing a strange behavior from the Victron DC to dc 12 30/30 and cannot charge his Lithium via it.
He has 420AH of Gel as starter/backup house where the Victron DC2DC is connected charging 560AH lithium. 90A mastervolt alternator on a Volvo d2-55 with regulator for gel, charging gel.
When he switches on the Orion, the Orion starts and then over course from 2 min the input voltage drops from 14,78V to 10V.
If he puts a 30A load (not the dc2dc) on the gel the gel stays stable.
When he puts the 30A from the DC2DC the voltages dropes to 10v over 2 min and dc to dc switches off.
What can that be?
Which model Orion? Is it a Smart model? 12 30/30 doesn’t exist.

Are the voltages and currents measured or confirmed with a multimeter? Where were the meter probes connected during the measurements?
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 05-01-2023, 09:36   #3
Registered User

Join Date: Mar 2007
Location: Santa Cruz
Boat: SAnta Cruz 27
Posts: 6,887
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Just use jumper cables to charge the lithium.
donradcliffe is offline   Reply With Quote
Old 05-01-2023, 09:40   #4
Registered User
 
Scubaseas's Avatar

Join Date: Apr 2005
Location: Seabroook Texas or Southern Maine
Boat: Pearson 323, Tayana V42CC
Posts: 1,512
Images: 1
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Do the lithium batteries have a low voltage cut out? Sounds like the BMS on the LiFePo4 battery is not letting voltage in? Or is there a fuse between the Orion and the LiFePo4 bank? I'd call Victron and see what they think.
Scubaseas is offline   Reply With Quote
Old 05-01-2023, 09:47   #5
Registered User

Join Date: Nov 2013
Location: US East Coast Probably?
Boat: Privilege 435
Posts: 399
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Assuming that all this info is correct, and the gel bank indeed is stable over that same two minutes, the problem really can only be the cables or the dc/dc itself.

If he has extra cables, he can swap them out (the ones to the dc/dc) to eliminate that problem at least. Or he can try to swap the cables the run to the dc/dc to a different battery in the bank. It could be connected to the one bad battery that the others can’t compensate for but that seems like a reach with that size bank.

I don’t use a dc/dc on my setup so I shouldn’t try to comment on the problems that could arise with the victron itself.
__________________
Occasionally attempting to document our favorite boat upgrades on clevermariner.com
SV Confianza is offline   Reply With Quote
Old 05-01-2023, 09:59   #6
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,287
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Quote:
Originally Posted by s/v Jedi View Post
Which model Orion? Is it a Smart model? 12 30/30 doesn’t exist.

Are the voltages and currents measured or confirmed with a multimeter? Where were the meter probes connected during the measurements?
Yes orion TR Smart 12V/12V 30A
Gel is directly connected to a mastervolt shunt and battery manager, confirmed with measuring at the poles of the battery and poles of the argofet, who is splitting bowtruster and gel starter/backup house.
Then on input of the Orion shows the Same then the app.
Well the only thing in between is 50cm cable and a fuse.
Told him now to just use a new piece of cable without a fuse to the DC2DC and just reconnect all new to the battery.
Installation is a month old, I helped him to do and we did 3 days together all the use cases that could happen, all was fine and DC2DC was working correct.
It’s the Orion itself that’s cutting out, gel is at 14V and 100% full and LFP is at 13,4V. Taking the 30A.
CaptainRivet is offline   Reply With Quote
Old 05-01-2023, 10:03   #7
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,235
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Quote:
Originally Posted by CaptainRivet View Post
Yes orion TR Smart 12V/12V 30A
Gel is directly connected to a mastervolt shunt and battery manager, confirmed with measuring at the poles of the battery and poles of the argofet, who is splitting bowtruster and gel starter/backup house.
Then on input of the Orion shows the Same then the app.
Well the only thing in between is 50cm cable and a fuse.
Told him now to just use a new piece of cable without a fuse the DC2DC.
Installation is a month old, I helped him to do and we did 3 days together all the use cases that could happen, all was fine.
It sounds like maybe the BMS is disconnecting the house battery?

If he measures 10V on the terminals of a gel start battery then either the battery is defective, or there is a very large load, like a near dead short.
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 05-01-2023, 10:05   #8
Registered User

Join Date: Mar 2016
Location: San Francisco
Boat: Morgan 382
Posts: 3,123
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

You state that the voltage at the AGM is stable, but at the input to the DCDC it slowly drops to 10V. Assuming that is confirmed by a voltmeter, there is a bad connection, that is heating up, and as it heats, gets worse. It is probably a crimp connector somewhere between the AGM and the DCDC. But it could be something else, and could even be a bad connection (cold solder joint) inside the DCDC.

But 90%, it's a bad crimp connection between the AGM and DCDC. It could be either the positive or ground, so check both.
__________________
-Warren
wholybee is offline   Reply With Quote
Old 05-01-2023, 10:07   #9
Registered User
 
Scubaseas's Avatar

Join Date: Apr 2005
Location: Seabroook Texas or Southern Maine
Boat: Pearson 323, Tayana V42CC
Posts: 1,512
Images: 1
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Quote:
Originally Posted by CaptainRivet View Post
Yes orion TR Smart 12V/12V 30A
Gel is directly connected to a mastervolt shunt and battery manager, confirmed with measuring at the poles of the battery and poles of the argofet, who is splitting bowtruster and gel starter/backup house.
Then on input of the Orion shows the Same then the app.
Well the only thing in between is 50cm cable and a fuse.
Told him now to just use a new piece of cable without a fuse to the DC2DC.
Installation is a month old, I helped him to do and we did 3 days together all the use cases that could happen, all was fine and DC2DC was working correct.
There may be a special restart situation with the battery if the house bank went below a certain voltage. Try checking wiring and fuses. If they're OK try making sure ALL the house loads are off then try turning on the Orion and see if the House will start to accept a charge. If you have a 10.2V or lower house and a lot of stuff on you need to remove the load by turning stuff off and let it charge up some first. To put it another way you are drawing more off the house than the DC2DC can put back in.

I have Renogy LiFePo4s which if run below 10.2V need a special power supply to turn the BMS back on. Not sure what that means and I've never let the bank go that low but there may be special voltage considerations if you ran the house down below what the BMS allows.
Scubaseas is offline   Reply With Quote
Old 05-01-2023, 10:39   #10
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,287
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

So one issue is found, it was the breaker in the input line to the DC2DC.
Input breaker 13.3V, output breaker fluctuate between 13 and 5V, the longer on more 5V.
Replaced and now at least voltage is stable.
But output alternator is 14,78V=input gel but the input voltage on the DC2DC is 12,78V.
It looks like DC2DC is taking the 30A out of the gel as the gel is very slowly dropping in voltage but should actually show the 14,78V from the alternator.

BMS is not involved at all and not shutting off the Orion. All ok on LFP side.
CaptainRivet is offline   Reply With Quote
Old 05-01-2023, 10:41   #11
Registered User
 
Captain Bill's Avatar

Join Date: Apr 2008
Location: Punta Gorda, Fl
Boat: Endeavourcat Sailcat 44
Posts: 3,188
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

What Wholybee said. 30 amps through a bad crimp or solder joint will do exactly what you describe. I could also be a damaged wire but not as likely. If he has a laser temperature sensor, a quick scan of the wires will show a definite hot spot.
Captain Bill is online now   Reply With Quote
Old 05-01-2023, 11:34   #12
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,287
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Thank you everyone, problems solved:
Issue 1 was a faulty 60A breaker in the input to the DC2DC
Issue 2 was a cable break in the field wire to the alternator.
After issue 1 was found the voltage was high from alternator because it was not delivering any amps as field wire just got contact from time to time means the DC2DC took the 30A partly from the starter/backup 420AH gel when field wire didn’t have contact. We couldn’t see that before due to faulty breaker. And when we tested the alternator delivered 30A to the gel and breaker was ok…assume partly because that happened now after longer time motoring.
Replaced the field wire and all working as it should, 57A from alternator, 32A for DC2DC, Rest for bowtruster battery, normal house loads and autopilot.
That’s the advantage if you DIY your system, you know it and can troubleshoot it.
CaptainRivet is offline   Reply With Quote
Old 06-01-2023, 00:32   #13
always in motion is the future
 
s/v Jedi's Avatar

Cruisers Forum Supporter

Join Date: Feb 2009
Location: in paradise
Boat: Sundeer 64
Posts: 19,235
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Quote:
Originally Posted by CaptainRivet View Post
Thank you everyone, problems solved:
Issue 1 was a faulty 60A breaker in the input to the DC2DC
Issue 2 was a cable break in the field wire to the alternator.
After issue 1 was found the voltage was high from alternator because it was not delivering any amps as field wire just got contact from time to time means the DC2DC took the 30A partly from the starter/backup 420AH gel when field wire didn’t have contact. We couldn’t see that before due to faulty breaker. And when we tested the alternator delivered 30A to the gel and breaker was ok…assume partly because that happened now after longer time motoring.
Replaced the field wire and all working as it should, 57A from alternator, 32A for DC2DC, Rest for bowtruster battery, normal house loads and autopilot.
That’s the advantage if you DIY your system, you know it and can troubleshoot it.
You mean the blue wire between the regulator and the alternator field terminal? Yes, if that is intermittent then that will throw everything off.

I was fearing there were faulty diode or FET isolators hidden somewhere
__________________
“It’s a trap!” - Admiral Ackbar.

s/v Jedi is online now   Reply With Quote
Old 06-01-2023, 21:27   #14
Registered User

Join Date: Jun 2013
Location: canada
Posts: 4,705
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

if input battery is 14v and orion input is 10v. there is only 2 options. cables / conectinos from battery to orion is bad. or orion is bad internally and it it really has 14v at the posts but only sees 10 inside.

both can be confirmd with a volt meter by measuring battery and orion posts.
smac999 is offline   Reply With Quote
Old 10-01-2023, 07:57   #15
Registered User

Join Date: Sep 2019
Location: Lifeaboard
Boat: FP Lavezzi 40
Posts: 3,287
Re: Urgent: Victron DC2DC cut off input voltage is low but isn‘t

Quote:
Originally Posted by smac999 View Post
if input battery is 14v and orion input is 10v. there is only 2 options. cables / conectinos from battery to orion is bad. or orion is bad internally and it it really has 14v at the posts but only sees 10 inside.

both can be confirmd with a volt meter by measuring battery and orion posts.
Correct Jedi..The cable break in the field wire was kinda randomly connecting and not. Most likely that cable break is old and was even present when we tested the new installed LFP system 6 weeks ago. There breaker worked and DC2DC too.
But it needed the breaker to get faulty additionally that this could discovered…Murphy is calling…it’s mostly several things that need to go wrong till you realize something is wrong.
If that breaker wouldn’t have been faulty that issue with the field cable wouldn’t have been detected that easy.
And doing that via iridium communication on a new install when in the middle of ocean is quite challenging.
What helped is the fact that all switching of BMS is done via optocopler so with one quick view you can see if the BMS was involved and switched or not. Each source has its own optocopler, so what is on shines red…
Means I put I acrylic sheet as cover on my BMS Box so I See this optocopler too.

Thanks again for prompt help.
CaptainRivet is offline   Reply With Quote
Reply


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
LFP alternator charge, LA-dc2dc in which order SOLAR SUPPORT Lithium Power Systems 88 24-12-2022 19:13
DC2DC charger: Before/After Argo FET CaptainRivet Lithium Power Systems 5 06-12-2022 03:54
Easily swapping input/output of dc2dc charger LifesBetterWhenYoureBeating Electrical: Batteries, Generators & Solar 3 02-12-2022 07:59
Victron Orion DC2DC with banks in parallel LifesBetterWhenYoureBeating Electrical: Batteries, Generators & Solar 6 26-09-2022 10:49
Low Voltage alarm whilst Victron BMV showing 90%+ jamesconnell Marine Electronics 13 03-07-2019 15:46

Advertise Here


All times are GMT -7. The time now is 06:24.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.