Isotherm problem

Have a isotherm compact classic. The problem is it will turn on and run the compressor for 2 or 3 seconds then cut out. Replaced the electrics box, nothing changed. Shorted out the thermostat, still no change.. checked the voltage at the control box when the fridge turned on and seems fine, even ran new wires directly from the bus bars. Any ideas?
Kestrahl is offline   Reply With Quote
Old 06-06-2018, 03:25   #2
cruiser

Join Date: Dec 2006
Posts: 405
Re: Isotherm problem

Try disconnecting the fan. If the unit then runs, replace the fan.
Next, remove the Motor Driver Module (electrics box) and check the resistance between each two pins... should be all the same at approx 2 ohms. Also check from these pins to the compressor case to see if there is any continuity. (Motor winding shorting to frame)
What is the history of the system because the compressor itself is usually bullet proof and you have changed the driver, so the only thing left is an induced seized compressor!

Cheers OzePete
OzePete is offline   Reply With Quote
Old 09-06-2018, 08:25   #3
Marine Service Provider
 
Kestrahl's Avatar

Join Date: Jun 2012
Location: Sri Lanka
Boat: Laurie Davidson 35
Posts: 394
Re: Isotherm problem

Thanks for that. Turns out one of the fans had died. As soon as that was disconnected it works fine.

I added an extra fan here in the tropics to try and improve efficiency, if it only had one fan then I would have noticed that there was no fan sound!
Kestrahl is offline   Reply With Quote
Old 09-06-2018, 16:31   #4
cruiser

Join Date: Dec 2006
Posts: 405
Re: Isotherm problem

Quote:
Originally Posted by Kestrahl View Post
Thanks for that. Turns out one of the fans had died. As soon as that was disconnected it works fine.

I added an extra fan here in the tropics to try and improve efficiency, if it only had one fan then I would have noticed that there was no fan sound!
That is good news.
These little fans have a tiny built in processor which, if it fails, can corrupt the processor that drives the compressors Motor Driver Module on rare occasions.

I would be more concerned at your running two fans as this may exceed the Motor Drivers fan circuit limit.
We use a relay powered by the Motor Drivers fan circuit and supplying the fan (fans) direct from the 12VDC supply. This eliminates any chance of a faulty fan corrupting the Driver or overloading it.

Cheers OzePete Ozefridge | 12 Volt Refrigeration Systems
OzePete is offline   Reply With Quote
Reply

Tags
isotherm


Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are Off
Pingbacks are Off
Refbacks are Off


Similar Threads
Thread Thread Starter Forum Replies Last Post
Isotherm Refrigerators schoonerdog Plumbing Systems and Fixtures 40 14-11-2017 12:11
Isotherm Fridge Problem Jim Hood Plumbing Systems and Fixtures 9 13-08-2013 14:07
Isotherm 5801 Cycling?? Anyone have an Isotherm? ssullivan Plumbing Systems and Fixtures 8 16-02-2013 07:10
Problem with Isotherm 3700 ASU Fridge richardhula Plumbing Systems and Fixtures 3 27-04-2010 12:33
Isotherm Fridge and water heater kcrompton Cooking and Provisioning: Food & Drink 5 25-12-2004 11:44

Advertise Here


All times are GMT -7. The time now is 03:23.


Google+
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.
Social Knowledge Networks
Powered by vBulletin® Version 3.8.8 Beta 1
Copyright ©2000 - 2024, vBulletin Solutions, Inc.

ShowCase vBulletin Plugins by Drive Thru Online, Inc.